<feed xml:lang="en" xmlns="http://www.w3.org/2005/Atom"><title>Recent posts to Gateway and Target same device for testing</title><link href="https://forge.codesys.com/forge/talk/CODESYS-V2/thread/e5ca724220/" rel="alternate"/><link href="https://forge.codesys.com/forge/talk/CODESYS-V2/thread/e5ca724220/feed.atom" rel="self"/><id>https://forge.codesys.com/forge/talk/CODESYS-V2/thread/e5ca724220/</id><updated>2020-12-09T18:36:07.557000Z</updated><subtitle>Recent posts to Gateway and Target same device for testing</subtitle><entry><title>Gateway and Target same device for testing</title><link href="https://forge.codesys.com/forge/talk/CODESYS-V2/thread/e5ca724220/?limit=25#370c" rel="alternate"/><published>2020-12-09T18:36:07.557000Z</published><updated>2020-12-09T18:36:07.557000Z</updated><author><name>eschwellinger</name><uri>https://forge.codesys.com/u/eschwellinger/</uri></author><id>https://forge.codesys.comd770b05f5b56dcef6a30500dc3f9d4722d112d39</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Hi,&lt;br/&gt;
you are almost there,&lt;br/&gt;
the only thing is.. in your project is a COntrol Win plc(32Bit) and on your PC&lt;br/&gt;
I asume you have installed CODESYS 64Bit.&lt;br/&gt;
So the missing part is you need to change your project to Control Win 64Bit - &amp;gt; Update device by rightclick on the plc device in the device tree.&lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>Gateway and Target same device for testing</title><link href="https://forge.codesys.com/forge/talk/CODESYS-V2/thread/e5ca724220/?limit=25#21a3" rel="alternate"/><published>2020-12-09T14:14:16.198000Z</published><updated>2020-12-09T14:14:16.198000Z</updated><author><name>codesysnoob</name><uri>https://forge.codesys.com/u/codesysnoob/</uri></author><id>https://forge.codesys.com94575f2bbb2bc369a71951a09536ac64737e2247</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Hi,&lt;/p&gt;
&lt;p&gt;I am using Codesys 3.5.16.30, I might be posting in the wrong forum but I do not see a newer version here.&lt;br/&gt;
I am using this software for the first time and trying to see if we can replace our allen bradley plcs with these ones. I would like to know for testing purposes how can i use my Windows 10 computer to act as both the gateway and plc. In the communications tab I see that the the Gateway has green light which I suppose is my own PC and the Device has grey light. But if I want to use my PC as the PLC as well what do I do? I have installed Codesys Control Win V3 - x64 Version 3.5.16.30 and also click on start PLC from the system tray but I can't seem to understand how to use the same PC for both programming/Gateway and the Target device.&lt;/p&gt;
&lt;p&gt;Please help as I want to start this journey with Codesys and I am really excited about it.&lt;/p&gt;
&lt;p&gt;Regards&lt;br/&gt;
SB&lt;/p&gt;&lt;/div&gt;</summary></entry></feed>