<feed xml:lang="en" xmlns="http://www.w3.org/2005/Atom"><title>Recent posts to OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/11cde80f33/" rel="alternate"/><link href="https://forge.codesys.com/forge/talk/Engineering/thread/11cde80f33/feed.atom" rel="self"/><id>https://forge.codesys.com/forge/talk/Engineering/thread/11cde80f33/</id><updated>2024-09-11T12:08:33.611000Z</updated><subtitle>Recent posts to OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins</subtitle><entry><title>OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/11cde80f33/?limit=25#edf1" rel="alternate"/><published>2024-09-11T12:08:33.611000Z</published><updated>2024-09-11T12:08:33.611000Z</updated><author><name>thysonfury</name><uri>https://forge.codesys.com/u/thysonfury/</uri></author><id>https://forge.codesys.comc77d4467fbf80a1545db74d5cc9eff17cb7c0424</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;OPTO22 Codesys Activation license not active. &lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/11cde80f33/?limit=25#7fd9" rel="alternate"/><published>2024-09-10T20:39:30.934000Z</published><updated>2024-09-10T20:39:30.934000Z</updated><author><name>esmith</name><uri>https://forge.codesys.com/u/esmith/</uri></author><id>https://forge.codesys.com222bf15c5016bf0d0664cb3145b2f367513b0edc</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;I think I am having a similar issue. Have you found out what was causing this problem?&lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/11cde80f33/?limit=25#5db8" rel="alternate"/><published>2024-04-15T07:58:59.556000Z</published><updated>2024-04-15T07:58:59.556000Z</updated><author><name>thysonfury</name><uri>https://forge.codesys.com/u/thysonfury/</uri></author><id>https://forge.codesys.come6f95c53b02d05c73197f9a3006d2f45de2b2ecf</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Hi after some assistance with an error on a Groov PR2 PLC.&lt;/p&gt;
&lt;p&gt;We have a few different communications set up as shown below:&lt;/p&gt;
&lt;p&gt;One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC )&lt;br/&gt;
Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph)&lt;br/&gt;
One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel)&lt;br/&gt;
One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit)&lt;br/&gt;
All Licenses have been installed as per OPTO22 suggestions of the order below:&lt;/p&gt;
&lt;p&gt;Modbus TCP Master&lt;br/&gt;
Modbus TCP Slave&lt;br/&gt;
Modbus RTU Master&lt;br/&gt;
Modbus RTU Slave&lt;br/&gt;
When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly.&lt;/p&gt;
&lt;p&gt;Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter.&lt;/p&gt;
&lt;p&gt;Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?&lt;/p&gt;&lt;/div&gt;</summary></entry></feed>