<feed xml:lang="en" xmlns="http://www.w3.org/2005/Atom"><title>Recent posts to Unable to Connect to Modbus RTU Device</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/857897b307/" rel="alternate"/><link href="https://forge.codesys.com/forge/talk/Engineering/thread/857897b307/feed.atom" rel="self"/><id>https://forge.codesys.com/forge/talk/Engineering/thread/857897b307/</id><updated>2024-09-03T13:38:53.103000Z</updated><subtitle>Recent posts to Unable to Connect to Modbus RTU Device</subtitle><entry><title>Unable to Connect to Modbus RTU Device</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/857897b307/?limit=25#0ae6" rel="alternate"/><published>2024-09-03T13:38:53.103000Z</published><updated>2024-09-03T13:38:53.103000Z</updated><author><name>TimvH</name><uri>https://forge.codesys.com/u/timvh/</uri></author><id>https://forge.codesys.comb66e59bdab519b940dc66fe2b4f7b05065a1eaa9</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;If your Control Win is the Modbus "Master" then your configuration should be something like:&lt;br/&gt;
Modbus_COM (Serial port)&lt;br/&gt;
- Modbus Master (this is the Control Win SoftPLC actively setting up the communication)&lt;br/&gt;
    - Modbus Slave (this is then your WAGO 750-315)&lt;br/&gt;
You need to add channels to the Modbus Slave configuration to inform the master which variables to read/write from the Wago module.&lt;/p&gt;
&lt;p&gt;The way you configured it now, the Control Win is also a slave.&lt;br/&gt;
PS, don't forget to put the PLC (Control Win) in Run.&lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>Unable to Connect to Modbus RTU Device</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/857897b307/?limit=25#8740" rel="alternate"/><published>2024-08-26T18:27:42.570000Z</published><updated>2024-08-26T18:27:42.570000Z</updated><author><name>jp23</name><uri>https://forge.codesys.com/u/jp23/</uri></author><id>https://forge.codesys.come060709aa3420ee8d43ab9fc59f18056d741aa8d</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Hi all,&lt;/p&gt;
&lt;p&gt;I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial:&lt;br/&gt;
&lt;a href="https://www.youtube.com/watch?v=YlRfkESaNds" rel="nofollow"&gt;https://www.youtube.com/watch?v=YlRfkESaNds&lt;/a&gt;&lt;/p&gt;
&lt;p&gt;I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1).&lt;/p&gt;
&lt;p&gt;Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."&lt;/p&gt;&lt;/div&gt;</summary></entry></feed>