<feed xml:lang="en" xmlns="http://www.w3.org/2005/Atom"><title>Recent posts to Warm Reset</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/af7702ea1b/" rel="alternate"/><link href="https://forge.codesys.com/forge/talk/Engineering/thread/af7702ea1b/feed.atom" rel="self"/><id>https://forge.codesys.com/forge/talk/Engineering/thread/af7702ea1b/</id><updated>2021-04-27T15:08:29.773000Z</updated><subtitle>Recent posts to Warm Reset</subtitle><entry><title>Warm Reset</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/af7702ea1b/?limit=25#abb4" rel="alternate"/><published>2021-04-27T15:08:29.773000Z</published><updated>2021-04-27T15:08:29.773000Z</updated><author><name>awal</name><uri>https://forge.codesys.com/u/awal/</uri></author><id>https://forge.codesys.comd2ae3ff497307a89ad0e8d42ad41a64234b7479e</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Yes. The controller works ok after the user requests a reset but the run led is red.  Not sure how reliable the controller would be when the run led isn't green.&lt;br/&gt;
Or is it red because the pointer selects the debug app instead of the boot app. Is there some way to point the restart to the boot application ? &lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>Warm Reset</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/af7702ea1b/?limit=25#a908/5ba9" rel="alternate"/><published>2021-04-27T13:26:04.488000Z</published><updated>2021-04-27T13:26:04.488000Z</updated><author><name>mkhogali</name><uri>https://forge.codesys.com/u/mkhogali/</uri></author><id>https://forge.codesys.com68cb9afd8583b8b1aff533f053b0928bfdab5b96</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;U mean the  controller work OK the only issue is the red led?? &lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>Warm Reset</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/af7702ea1b/?limit=25#a908" rel="alternate"/><published>2021-04-27T02:11:48.553000Z</published><updated>2021-04-27T02:11:48.553000Z</updated><author><name>awal</name><uri>https://forge.codesys.com/u/awal/</uri></author><id>https://forge.codesys.comf6a0c8682b665f5f632cda4d9947c23be34ed2ad</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;This works kind of...    When the user resets or restarts the plc from the hmi the run led on the plc will turn red and stay red until it is power cycled. The plc is full functional but the run led remains red.    I would use with caution until someone comes up with a solution. &lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>Warm Reset</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/af7702ea1b/?limit=25#153d" rel="alternate"/><published>2021-04-19T07:45:42.285000Z</published><updated>2021-04-19T07:45:42.285000Z</updated><author><name>Ton</name><uri>https://forge.codesys.com/u/ton/</uri></author><id>https://forge.codesys.com361886b3c97eb5a178cf8d1f0b552569e0942197</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Hi,&lt;/p&gt;
&lt;p&gt;My solution:&lt;/p&gt;
&lt;p&gt;Create program:&lt;br/&gt;
PROGRAM Ethercat_INode&lt;br/&gt;
VAR&lt;br/&gt;
    pApp: POINTER TO CmpApp.APPLICATION;&lt;br/&gt;
    result: RTS_IEC_RESULT;&lt;br/&gt;
    xInit: BOOL:= TRUE;&lt;br/&gt;
    xRestartApp: BOOL; //Visu&lt;br/&gt;
END_VAR&lt;br/&gt;
VAR RETAIN&lt;br/&gt;
    xAutoRestart: BOOL;&lt;br/&gt;
END_VAR&lt;br/&gt;
IF xInit THEN&lt;br/&gt;
    pApp:= AppGetCurrent(pResult:= result);&lt;br/&gt;
    xInit:= FALSE;&lt;br/&gt;
    xAutoRestart:= FALSE;&lt;br/&gt;
END_IF&lt;/p&gt;
&lt;p&gt;IF xRestartApp THEN&lt;br/&gt;
    xRestartApp:= FALSE;&lt;br/&gt;
    CmpApp.AppReset(pApp:= pApp, usResetOption:= CmpApp.RTS_RESET);&lt;br/&gt;
    xAutoRestart:= TRUE;&lt;br/&gt;
END_IF&lt;/p&gt;
&lt;p&gt;Create function:&lt;br/&gt;
FUNCTION SysEvent_StopDone : DWORD&lt;br/&gt;
VAR_INPUT&lt;br/&gt;
    EventPrm: CmpApp.EVTPARAM_CmpAppStop;&lt;br/&gt;
END_VAR&lt;br/&gt;
IF Ethercat_INode.xAutoRestart THEN&lt;br/&gt;
    CmpApp.AppStartApplication(Ethercat_INode.pApp);&lt;br/&gt;
END_IF&lt;/p&gt;
&lt;p&gt;In Task Configuration/System Events add event Handler StopDone and fuction call to SysEvent_StopDone.&lt;/p&gt;
&lt;p&gt;Hopefully this helps.&lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>Warm Reset</title><link href="https://forge.codesys.com/forge/talk/Engineering/thread/af7702ea1b/?limit=25#66bf" rel="alternate"/><published>2021-04-19T04:57:35.607000Z</published><updated>2021-04-19T04:57:35.607000Z</updated><author><name>mkhogali</name><uri>https://forge.codesys.com/u/mkhogali/</uri></author><id>https://forge.codesys.comb0e90c5e85e4668938ce9055194f81a2ec4b485b</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Hi there,&lt;br/&gt;
I'm working in a project of wago controller which is programmed by codesys 3.5, and I'm looking for way to let the operator to reset the controller from the HMI, so if there any ready function that can make this directly from the software without physical touching the controller.&lt;/p&gt;&lt;/div&gt;</summary></entry></feed>