I'm trying to use Codesys 3.5.16 with Wago PFC200 750-8202.
the problem is that the "Scan for Device" utility doesn't work 'cause the PFC200bus is not running.
License for runtime is activated , th plc is in running mode and the led SYS RUN and IO are green.
Am i doing something wrong?
BR
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
of course it is, but it doesn't work
i'm using a 750-8202 with last firmware revision : 03.04.10(16)
and the last CodeSys Runtime version V3.5.16.0 regularly licensed
i'have added manually the bus, but the results are the same!
BR
smarmiroli
Last edit: smarmiroli 2020-06-05
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello, support!
I'm trying to use Codesys 3.5.16 with Wago PFC200 750-8202.
the problem is that the "Scan for Device" utility doesn't work 'cause the PFC200bus is not running.
License for runtime is activated , th plc is in running mode and the led SYS RUN and IO are green.
Am i doing something wrong?
BR
Hi,
is the end module connected on Kbus?
To have this is mandatory on Kbus.
BR
Edwin
Last edit: eschwellinger 2020-06-04
of course it is, but it doesn't work
i'm using a 750-8202 with last firmware revision : 03.04.10(16)
and the last CodeSys Runtime version V3.5.16.0 regularly licensed
i'have added manually the bus, but the results are the same!
BR
smarmiroli
Last edit: smarmiroli 2020-06-05
I think that is a firmware problem, with the Wago firmware 03.03.10(15) it works perfectly
.. but now can't restore the license for the device..
can't believe it.. bad day..
can someone help me?