<feed xml:lang="en" xmlns="http://www.w3.org/2005/Atom"><title>Recent posts to PFC200 STATUS REGISTERS</title><link href="https://forge.codesys.com/forge/talk/Runtime/thread/4633f6d7bb/" rel="alternate"/><link href="https://forge.codesys.com/forge/talk/Runtime/thread/4633f6d7bb/feed.atom" rel="self"/><id>https://forge.codesys.com/forge/talk/Runtime/thread/4633f6d7bb/</id><updated>2020-02-27T15:11:32.709000Z</updated><subtitle>Recent posts to PFC200 STATUS REGISTERS</subtitle><entry><title>PFC200 STATUS REGISTERS</title><link href="https://forge.codesys.com/forge/talk/Runtime/thread/4633f6d7bb/?limit=25#f5d7" rel="alternate"/><published>2020-02-27T15:11:32.709000Z</published><updated>2020-02-27T15:11:32.709000Z</updated><author><name>eschwellinger</name><uri>https://forge.codesys.com/u/eschwellinger/</uri></author><id>https://forge.codesys.com25c36bf3014700800e091226030c283c000097c4</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Hi,&lt;/p&gt;
&lt;p&gt;hm... let me check, think this is possible but how is your SCADA connected by which fieldbus / modbus or is OPC UA an option too for your SCADA?&lt;br/&gt;
BR&lt;br/&gt;
Edwin&lt;/p&gt;&lt;/div&gt;</summary></entry><entry><title>PFC200 STATUS REGISTERS</title><link href="https://forge.codesys.com/forge/talk/Runtime/thread/4633f6d7bb/?limit=25#45da" rel="alternate"/><published>2020-02-27T15:11:30.950000Z</published><updated>2020-02-27T15:11:30.950000Z</updated><author><name>somlioy</name><uri>https://forge.codesys.com/u/somlioy/</uri></author><id>https://forge.codesys.com45c39f5dcfa598dd5d69e5f6fa126da4292e95df</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;Did you read the manual for 8202?&lt;/p&gt;
&lt;blockquote&gt;
&lt;p&gt;&lt;strong&gt;Zitat:&lt;/strong&gt;&lt;br/&gt;
9.5.3 PLC Status Register&lt;br/&gt;
Register 0x1040 provides the status (state) that the controller is currently in.&lt;br/&gt;
Possible values:&lt;br/&gt;
1 = PLC running − PLC status is RUNNING.&lt;br/&gt;
2 = PLC stopped − PLC status is STOPPED.&lt;/p&gt;
&lt;p&gt;&lt;strong&gt;Zitat:&lt;/strong&gt;&lt;br/&gt;
9.6 Diagnostics&lt;br/&gt;
9.6.1 Diagnostics for the MODBUS Master&lt;br/&gt;
The status of the PLC, or of the control system, can be queried by the MODBUS&lt;br/&gt;
master by reading the WAGO-specific register 0x1040 – “PLC Status” using&lt;br/&gt;
MODBUS services FC3 (Read Holding Registers) or FC4 (Read Input Registers).&lt;br/&gt;
The WAGO-specific register 0x1040 – “PLC Status” is explained in the Section&lt;br/&gt;
“PLC Status Registers”.&lt;/p&gt;
&lt;/blockquote&gt;&lt;/div&gt;</summary></entry><entry><title>PFC200 STATUS REGISTERS</title><link href="https://forge.codesys.com/forge/talk/Runtime/thread/4633f6d7bb/?limit=25#6a88" rel="alternate"/><published>2020-02-27T15:11:30.340000Z</published><updated>2020-02-27T15:11:30.340000Z</updated><author><name>Eric282000</name><uri>https://forge.codesys.com/u/eric282000/</uri></author><id>https://forge.codesys.com9b84e448c6c0f2c768f010164f0bbaddcd163d41</id><summary type="html">&lt;div class="markdown_content"&gt;&lt;p&gt;i am trying to read the status register from a wago 750-8202 with control fro pfc200 installed.&lt;br/&gt;
in the wago manual for e-runtime this is modbus registers 64010 - 64013. i need to be able to tell if the plc has stopped from the remote scada system.&lt;br/&gt;