Hello,
I'm trying to login with WAGO IPC C10E from the CoDeSys IDE to download test project.
Always pop up message "Communication error (#0)".
Project is some dummy - PLC_PRG with few rows of code and simple visu with one button - for test only.
Ethernet cable connected to X8, 192.168.1.20 ( default setting ). Ping ok, ftp ok, telnet ok.
Communication parameters IP adr 192.168.1.20 port 1200.
Computer in same network with IP 192.168.1.99. Two devices only in network.
On K-bus only one DI module 750-430.
Any ideas to improve situation?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
are ethernet settings in controller oke. start ethernet settings separate program from wago, free available on website.
on 750 series there is a small hatchcover and a switch below. see manual for position of this switch.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Wago devices need the k-Bus termination module.
Without it codesys comm do not work.
The minimum configuration to have online communication via codesys is: CPU + 1module (DI,DO,AI,AO, Serial,...) + k-bus termination
Regards
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,
I'm trying to login with WAGO IPC C10E from the CoDeSys IDE to download test project.
Always pop up message "Communication error (#0)".
Project is some dummy - PLC_PRG with few rows of code and simple visu with one button - for test only.
Ethernet cable connected to X8, 192.168.1.20 ( default setting ). Ping ok, ftp ok, telnet ok.
Communication parameters IP adr 192.168.1.20 port 1200.
Computer in same network with IP 192.168.1.99. Two devices only in network.
On K-bus only one DI module 750-430.
Any ideas to improve situation?
are ethernet settings in controller oke. start ethernet settings separate program from wago, free available on website.
on 750 series there is a small hatchcover and a switch below. see manual for position of this switch.
Wago devices need the k-Bus termination module.
Without it codesys comm do not work.
The minimum configuration to have online communication via codesys is: CPU + 1module (DI,DO,AI,AO, Serial,...) + k-bus termination