CR2513 Module : DANFOSS Valves : checking

manasa
2011-07-12
2011-07-15
  • manasa - 2011-07-12

    Hi All,

    We have a problem with IFM analog Output module CR2513. We are using this module in one of our project for DANFOSS valve 'PVES' type of valves.

    I made a sample program to test this CR2513 Analog Outputs along with CR0032 controller.
    My basic problem is how to force these outputs? IFM manual is saying that
    -1000% = 0.2 Ub
    0 = 0.5Ub
    +1000% = 0.8Ub,

    But I could able to force directly from 0 to 1000% to the channel "%QW130". I could not able to force -1000% as the outputs are "UINT" (Unsigned Integer)data type. Also i am not sure whether i am doing right or not.
    What is the raw counts i need to force to achive the voltage levels between 0.2Ub to 0.8 Ub?

    I could not able to found the rawcoutns of the AI/AO Modules on IFM R360 system manuals.

    Can any one help?

     
  • shooter - 2011-07-15

    If this is double sorry for that.
    the output of -100 % (same as -1000 permille like in manual ) is 20% of output voltage (so 2 Volts)
    +100 % is 8 volts.
    i do not know the raw count as the setting is not in the manual.
    just try it put a voltmeter on the output and run your setting.

    you will need to set a lot of settings on the ifm to have correct output.

    the output is an integer so you will need some conversion
    all real var
    minoutput :=7
    maxoutput:= 65528
    mininput :=-1000
    maxinput:=1000

    a calc is always in real so conversion must be done

    a:= (maxoutput-minoutput)/(maxinput-mininput)
    b:= minoutput
    in:= (???_TO_REAL(input)-mininput)

    out := (REAL_TO_INT ( a*in + b))

    example input =0
    in = 1000
    in most cases this all is done inside these functionblocks.

     