Reading speed is from adress 4 ( or 5) with the command 3. 20000 = 100%. Writing control word is from adress 0. The basic commands are : 1150 = stop, 1151 = start. Writing speed referance is from adress 2. 20000 = 100%.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
hello
com_mod_mast blog about the programs I want to create communication between the PLC-ACS550 DRIVES
help
Hello,
Reading speed is from adress 4 ( or 5) with the command 3. 20000 = 100%. Writing control word is from adress 0. The basic commands are : 1150 = stop, 1151 = start. Writing speed referance is from adress 2. 20000 = 100%.