I am using codesys v2.3, i have a project that has worked on a PC, now i had must change the PC.
Now the same project gine the error "The selected PLC profile does not match the profile of the target!"
when i try to do the login. I have checked the configuration and seem correct.
What can be the problem?
The PLC is a ttcontrol
Thanks
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Are you sure you installed the right target with codesys?
Besides installing codesys you will also need to install the right target with InstallTarget.exe. This allows codesys to communicate with your PLC.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi
I am using codesys v2.3, i have a project that has worked on a PC, now i had must change the PC.
Now the same project gine the error "The selected PLC profile does not match the profile of the target!"
when i try to do the login. I have checked the configuration and seem correct.
What can be the problem?
The PLC is a ttcontrol
Thanks
use export and import easy and safe way.
Are you sure you installed the right target with codesys?
Besides installing codesys you will also need to install the right target with InstallTarget.exe. This allows codesys to communicate with your PLC.