newbie question, how to reuse a pulse timer?

pnn
2010-11-04
2010-11-07
  • pnn - 2010-11-04

    Hi,

    using Codesys 2.3
    I can't get how to reuse a pulse timer.
    Attached is a simple project with one SFC program, which tries to use a TP timer declared as TP1 global.

    It works only once after a PLC reset.

    If I set TP1.IN from an action(TransA -> Step1A), the first time it works.
    TP is started, .ET increases etc.
    The next time I set .IN, nothing happens as .ET is already equal to .PT
    I can't reset .ET to 0, it doesn't reset automatically, so how am I supposed to reuse the timer?

    If I set TP1.IN from an ENTRY action(TransB -> Step1B), TP1.Q becomes true forever and TP1.ET stays at 0.

    It should be obvious already that I'm a complete newbie.
    How all this works and how to reuse a timer?

    Thanks.

    tp2.pro [28.9 KiB]

     
  • pnn - 2010-11-04

    please ignore, I've found what's wrong.
    Instead of TP1.IN:=FALSE; I should have used TP1(IN :=FALSE);
    Not so obvious at first sight

     
  • spfeif - 2010-11-07

    Sorry I hope you don't mind if I explain the difference between the two calls for people who might be wondering.

    TP1.IN:=FALSE; this sets the variable but never jumps to the instance of the timer TP1 in memory to reload the algorithm.

    TP1(IN:=FALSE); this sets the variable and jumps to the instance of the timer TP1 in memory and calls/runs the algorithm.

    EXAMPLE:

    PROGRAM PLC_PRG
    var
    Β Timer :TON;
    end_var
    Timer(IN := TRUE, PT:= T#5s);
    Timer.PT := T#10s;
    end_Program
    

    The outcome of the timer will be Timer.Q := TRUE after 5 sec not 10 sec.

     