Hello Everyone,
750-8204 was installed on a machine and it becomes faulty. We have arrange a new PLC from local market
we don't have PLC program but thanks to our other machine which has the same PLC running
I want to upload the program from that running PLC and download it to new PLC
can anyone tell me the procedure please?
π
2
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
You use the WAGOUpload tool.
You can download it on the download center of WAGO.
Make a backup and restore it on the new device. (if can check the remanent data to copy the persistent variables if necessary)
You can also use a SD card, go to the WBM copy it the image to the SD card and restart the other controller on the SD card. In the WBM, copy it back to the internal flash.
If you contact your local Wago office, they will more than probably help you.
There is also a WAGO forum.
RP,
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello Everyone,
750-8204 was installed on a machine and it becomes faulty. We have arrange a new PLC from local market
we don't have PLC program but thanks to our other machine which has the same PLC running
I want to upload the program from that running PLC and download it to new PLC
can anyone tell me the procedure please?
more posts ...
Hello,
You use the WAGOUpload tool.
You can download it on the download center of WAGO.
Make a backup and restore it on the new device. (if can check the remanent data to copy the persistent variables if necessary)
You can also use a SD card, go to the WBM copy it the image to the SD card and restart the other controller on the SD card. In the WBM, copy it back to the internal flash.
If you contact your local Wago office, they will more than probably help you.
There is also a WAGO forum.
RP,