Two WAGO Ethernet controllers 750-841 configuration

FIRAS
2010-04-26
2010-04-27
  • FIRAS - 2010-04-26

    Hello all ,

    I am using CodeSYS V2.3 with WAGO Ethenet controller 750-841 & I have a problem that I have three WAGO Ethernet controllers 750-841 , and I need to connect them in a network using switch , but I don’t know how to add more than one controller in K-BUS tree in PLC configuration menu ,how to give IP addresses for each PLC , how to write a ladder program for each PLC , and how to make visualization for each PLC components . Knowing that I programmed , visualized and operated one controller alone ( not PLCs network ).

    Hope to find a solution for this topic as soon as possible.

    Best regards..

    Firas

     
  • Nitrozin - 2010-04-27

    Hi,

    1.

    for setting the IP-Adress you can use the BootP-Server or the ethernet setting tool from WAGO.

    DL from here.

    http://www.wago.com/cps/rde/xchg/SID-24844007-4D6D049B/wago/style.xsl/deu-23342.htm

    2.

    you never see all Controllers in the KBus tree, only the actually programmed.

    3.

    all programs & visu's are controller-local, but you can exchange variables between the controllers using network-variables

    Nitro

     
  • FIRAS - 2010-04-27

    Thanks a lot Nitro... I'll try it myself

     