wago 750 84.. <-> proface ST 403

Anonymous
2007-02-26
2007-02-28
  • Anonymous - 2007-02-26

    Originally created by: kees kraaijeveld

    I have a wago controller programmed with CodeSys and a Proface screen ST403 and I have communication with Ethernet between these components

    I have problems with the addresses

    Codesys uses for instance addres 256 two times, for sending (word out) and receiving ( word in ).

    The The sent information from Word out 256 returns to Word In 256

    Does anyone have same experience, or a solution?

     
  • Uwe - 2007-02-27

    Hello kees,

    at the follow link you can find a documentation about the plc-addresses

    and the modbusfunctions for WAGO contollers and couplers

    http://www.wago.com/wagoweb/documentati ... 00003e.pdf

    If you use a 750-841 or a 750-842 normaly it is a better way to use the FB

    "ETHERNET_TERMINAL_MODBUSSLAVE".

    Inside the wago-specific library "ModbusEthernet_04.lib" (provided by WAGO)

    you can find this FB.

    This FB is an modbus-server and this server maps the modbusaddresses to

    a wordarray inside the plc.

    You can run this server at a free port (like 2500) in the plc.

    At proface you have to adjust the communication to this port.

    For more information please contact the wago support.

    Note :

    This informations are wago specific. Systems of other manufacturers can work by an other way.

    Uwe

     
  • Oberchefe - 2007-02-27

    Zitat:
    ETHERNET_TERMINAL_MODBUSSLAVE

    is for Modbus on serial Port.

    For Modbus Ethernet there's no library needed.

     
  • Uwe - 2007-02-28

    Hello Oberchefe,

    i am sure ETHERNET_TERMINAL_MODBUSSLAVE is a modbus-TCP-server

    for Ethernet not for serial ports.

    For modbus at serial port you can use the library "TerminalSlave_04.lib" .

    Both lib's have the same userinterface inside the plc so it is very easy

    to switch from Modbus-TCP to Modbus-Serial.

    Inside the firmware of the Wago-Controllers there is a Modbus-TCP-Server implemented on port 502.

    You are right, for use this server you don't need a library.

    But this server allows a direct access to the physical inputs / outputs and have an own

    userinterface.

    I think it's better to use ETHERNET_TERMINAL_MODBUSSLAVE as a second TCP-Server

    on an other port.

    So you can controll all outputs by the plc, you have a simple interface and it is easy

    to switch to a serial communication

    ( you have only to replace ETHERNET_TERMINAL_MODBUSSLAVE by TERMINAL_MODBUSSLAVE_RTU_EN ).

    This information is valid only for WAGO-Systems 841 / 842.

    Uwe

     
  • Oberchefe - 2007-02-28

    Zitat:
    i am sure ETHERNET_TERMINAL_MODBUSSLAVE is a modbus-TCP-server

    You're right, for sure. I didn't realize "ETHERNET" in the name.

     