Hello, I have a Exor HMI with 2 seperatred ETH interface's.
It is Configured as PN Master on ETH interface 1 and the IO's are working, as long as the development PC is connected to the ETH 0 interface.
When the PC is disconnected, the PN communication drops and a reconnection is started.
I installed the newest device description for Codesys and Firmware for the Panel.
The IO Gateway is from Weidmueller
did you try setup two eth ?
on ethO you set ip to communicate with pc, example 192.168.0.1
on eth1 ip to communicate with weidmuler I/O, example 192.168.100.1
note : ip need the same of ip setup under system setting of hmi.
Hello, I have a Exor HMI with 2 seperatred ETH interface's.
It is Configured as PN Master on ETH interface 1 and the IO's are working, as long as the development PC is connected to the ETH 0 interface.
When the PC is disconnected, the PN communication drops and a reconnection is started.
I installed the newest device description for Codesys and Firmware for the Panel.
The IO Gateway is from Weidmueller
What could cause the Problem?
did you try setup two eth ?
on ethO you set ip to communicate with pc, example 192.168.0.1
on eth1 ip to communicate with weidmuler I/O, example 192.168.100.1
note : ip need the same of ip setup under system setting of hmi.