profinet communication

gatto
2021-01-14
2021-01-15
  • gatto

    gatto - 2021-01-14

    Hi, codesys users.
    I am doing some tests here in the office to connect a siemens plc and a device codesys.
    I am using an exor hmi with softplc codesys 3.5.14 patch4.
    I entered a codesys profinet device.
    I exported the device and imported correctly in Tia-portal v15.
    In the siemens hardware configuration I inserted the same 2 input and output cards that I inserted in codesys (see images)
    I'm doing some tests and I haven't entered the license but I use it in demo for 2 hours.
    Codesys side seems to work in diagnosis.
    Siemens side when i scan the network i see the plc and the profinet codesys device correctly with ip and exact name.
    But going online with Tia-portal I see that the profinet device is in error (unreachable).
    Attached are some images and logs.
    Can you help me ?

     

    Last edit: gatto 2021-01-14
  • lorbed - 2021-01-14

    Hi gatto,

    I don't know if it's your case, but I think that Exor HMI can only be used like PROFINET MASTER and not as PROFINET Slave.

     
  • gatto

    gatto - 2021-01-15

    ok, you are right.
    Just PN controller.
    My regards.

     

Log in to post a comment.