Hello - I was wondering if I can run a webvisu in Codesys V3.5 SP 18 when using the Control Win V3 soft PLC. I don't see anything saying I can't do this, but I haven't been able to access the webvisu using conventional methods.
Thanks.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Yes, you can use the CODESYS ControlWin V3 Soft PLC. However, if simulation is enabled on the device this will disable all communication, so you need to turn off simulation to view the visualization in a web browser. In simulation mode, all IO and communication is disabled for standalone testing. In addition, make sure to set the start visualization in the WebVisu object in the application tree. I hope this helps!
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello - I was wondering if I can run a webvisu in Codesys V3.5 SP 18 when using the Control Win V3 soft PLC. I don't see anything saying I can't do this, but I haven't been able to access the webvisu using conventional methods.
Thanks.
Yes, you can use the CODESYS ControlWin V3 Soft PLC. However, if simulation is enabled on the device this will disable all communication, so you need to turn off simulation to view the visualization in a web browser. In simulation mode, all IO and communication is disabled for standalone testing. In addition, make sure to set the start visualization in the WebVisu object in the application tree. I hope this helps!