    Does anyone have a list of possible values and their meanings for the OPC tag CommState? I had found a list before in an old manual, but I can no longer find it.
    Thanks!
  • TimvH
    TimvH - 2016-01-20
    See the .pdf in your installation folder, e.g. c:\program files (x86)\codesys\codesys opc server 3\
    This will tell you the following (PS, it describes the name with single underscore, but if I remember correctly it is a double underscore...):
    For each configured PLC the OPC Server V3 generates the status variables _CommState and _CommStateOK. _CommState can be interpreted from an OPC Client and the following states can
    be requested:
    STATE_TERMINATE = -1
    STATE_PLC_NOT_CONNECTED = 0
    STATE_PLC_CONNECTED = 1
    STATE_NO_SYMBOLS = 2
    STATE_SYMBOLS_LOADED = 3
    STATE_RUNNING = 4
    STATE_DISCONNECT = 5
    STATE_NO_CONFIGURATION = 6
    _CommStateOK is a Boolean variable indicating in state TRUE a communication with the OPC server.
    The name of the plc can be taken from the prefix of the Boolean variable. If the variable is FALSE,