Hi Takeshi, not sure what you are trying to do.Can you post the EDS file for the adapter? And also if possible the two projects only with EtherNet/IP IO configuration. I do not need the logic.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I was trying to get the value of other Ethernet/IP devices while exposing the value of I/O connected to itself as an Ethernet/IP adapter.
I was able to communicate correctly after updating to CODESYS V3.5 SP19.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
When the Ethernet/IP Scanner and Adapter are connected together, OβT data is only sent correctly up to 600 bytes.
REAL type 300 data has been added to both TβO and OβT.
Deleting Scanner will send OβT correctly.
Anyone have a solution?
Hi Takeshi, not sure what you are trying to do.Can you post the EDS file for the adapter? And also if possible the two projects only with EtherNet/IP IO configuration. I do not need the logic.
I was trying to get the value of other Ethernet/IP devices while exposing the value of I/O connected to itself as an Ethernet/IP adapter.
I was able to communicate correctly after updating to CODESYS V3.5 SP19.
Well, great.