Bool turning on in case stament in wrong state?
Dave_T
2023-12-15
2023-12-16
  • Dave_T - 2023-12-15
    I have a case statement running a process.
    during one of the steps it has started calling a bool var that is 2 steps further on in the case?
    i have even tried //commenting it out but it still turns on at the same point in the case.
    i have also run a trace but cant see anything that would trigger it.
    Any Ideas?
    Cheers
  • lostcontrol - 2023-12-16
    are you sure it is not used anywhere else.?
    does it have an address that could be duplicated perhaps?
    nothing external writing to it?
    • Dave_T - 2023-12-16
      pretty sure its not. ive done a cross reference and only have one write that sets it to true.
      Only way i can stop it is to remove the function block call from the main pou that is running said case.
      its got me stumped:/
    i would be looking at what the case variable is doing then..
    sounds like there might be a logic race going on
      I had the FB called via a for loop to call a few instances of my FB
      I have removed it the for loop and just called them 1 by 1. Seems to have sorted the problem.
      tho, i have other FB's and for loops doing the same thing but they are all fine.
      below is basically what was happening.
      var:
      mVibrator : ARRAY[1..GVL_Settings.Number_Of_Products] OF Main_Vibrator;
      end_var
      Controller(PRG) call:
      FOR v := 1 TO GVL_Settings.Number_Of_Products BY 1 DO;
      mVibrator[v] ();
      END_FOR
      So at state 30: the mVibrator[1].start was turning on
      30:
      Main_Mixer.Start := TRUE;
      Process_State := 2;
      IF Main_mixer.Done THEN
      Main_Mixer.Start := FALSE;
      Control_State := 40;
      but its not till state 50: that it is actual in the code.
      50:
      Main_Suction_valve.Open_Input := TRUE;
      mVibrator[1].Start := TRUE;
      Process_State := 4;
      IF GVL_Weigh_hopper.LoadCell_Weight = 0 THEN
      Main_Suction_valve.Open_Input := FALSE;
      mVibrator1.Start := FALSE;
      Control_State := 60;
      Thanks for your input.