OPC-server

bryn
2005-10-26
2005-11-04
  • bryn - 2005-10-26

    I'm configuring OPC-server and "talk" to this from Intouch via OPCLink (Wonderware). The log-file at the OPC-server looks to be fine, I can browse all items from OPCLink, but get no values. Any out there have any ideas? Bryn. OPC-logfile looks like this:

    Filter=0xffffffff

    (26.10.2005, 09:44:43.484) Server 2.3.9.1 started

    (26.10.2005, 09:44:43.484) UpdateRate[ms]=500, PublicGroups=1, SyncInit=1, LogEvents=1

    (26.10.2005, 09:44:43.484) 1. Reconnect to <plc1></plc1>

    (26.10.2005, 09:44:43.500) [PLC1]: ::ConnectGateway(): m_ulGatewayChannels=1

    (26.10.2005, 09:44:43.500) Gateway Version: 2.3.5.1

    (26.10.2005, 09:44:45.343) <plc1> Reconnect successful, ProjectName='BSY1.pro'</plc1>

    (26.10.2005, 09:44:45.343) Timeout[ms]=10000, BufferSize[B]=0, Waitime[s]=10, Reconnecttime[s]=15

    (26.10.2005, 09:44:45.343) Motorola=0, NoLogin=0

    (26.10.2005, 09:44:47.531) <plc1> ProjectID matched, Project <bsy1.pro>: PLC=519306, SYM=519306</bsy1.pro></plc1>

    (26.10.2005, 09:44:47.531) <plc1> 7 symbols loaded</plc1>

    (26.10.2005, 09:44:47.546) Client attached to server

     
  • Armin Hornung - 2005-11-03

    The logfile looks good, but there are no active items requested by the client.

    Do you have added the items into a group in OPCLink? Then you should see number of active items > 0 in the opc-server logfile and you should see the item values.

    Regards,

    Armin

     
  • Anonymous - 2005-11-04

    Originally created by: Brynjar

    Here are some stuff from the WWLogger

    1550 04.11.2005 08:07:44 1504 1556 Info VIEW Wonderware I/O Server Toolkit for Windows NT - Version 7,2,0,0

    1551 04.11.2005 08:07:45 1620 1492 Info OPClink TRACE: add OPC group (hClientGroup=0x00000002, hServerGroup=0x00000001) to: test.pro on CoDeSys.OPC.02

    1552 04.11.2005 08:07:45 1620 1492 Info OPClink TRACE: attaching group to: test.pro

    1553 04.11.2005 08:07:45 1620 1492 Info OPClink ERROR: cannot add OPC item: PLC_PRG.VERDI1 (type=0x0003, hr=0xc0040008, hCli=0x01000000, hSrv=0x00000000) to group on topic: test.pro

    1554 04.11.2005 08:07:45 1620 1492 Info OPClink The item ID doesn't conform to the server's syntax.

    1555 04.11.2005 08:07:45 1620 1492 Info OPClink ERROR: cannot add OPC item: VERDI0 (type=0x0004, hr=0xc0040008, hCli=0x01000001, hSrv=0x00000000) to group on topic: test.pro

    1556 04.11.2005 08:07:45 1620 1492 Info OPClink The item ID doesn't conform to the server's syntax.

    1557 04.11.2005 08:07:49 1620 1492 Info OPClink Build Information for Server "CoDeSys.OPC.02": Build Number=9. Version Number: Major=2; Minor=3.

    1558 04.11.2005 08:07:54 1620 1492 Info OPClink GetStatus for server "CoDeSys.OPC.02": state: 1

    As you can see there are some problems with the item-syntax written in Intouch. Corresponding to thes error messages I use the following item-syntax:

    VERDI0 use rVERDI0

    VERDI1 use iPLC_PRG.VERDI1

    STATUS use STATUS

    I've used Intouch a lot of times with OPSLink against other OPC-servers and prefix the items with i - r - d - m according to the OPCLink-rules of addressing items.

     