Hi all,
I am using Codesys 3.5 SP18 with:
- CODESYS Control for Raspberry Pi SL (license in USB KEY)
- CODESYS KNX SL (license in USB KEY
I have configured both Codesys and ETS but it is not communicating.
On the KNX side I am using the "IP Interface SCN-IP000.03" (MDT) and I think this is the problem (in other topic Edwin recommend an IP ROUTER).
So I should replace the interface with "IP Router SCN-IP100.03" (MDT).
Do you think this could be the solution?
In the windows KNX I/O Mapping the variable Program LED Status and Program Button are BOOL but the variable are %IB0 and %QB0. Shouldn't it be% IX0.0 and & QX0.0?
I am attaching some screenshots.
Thank you
Hi everyone,
since I haven't received information from anyone, if it can be useful to someone else, after some tests I discovered that the system can only work using an IP-ROUTER (I used an "IP Router SCN-IP100.03" from MDT).
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi all,
I am using Codesys 3.5 SP18 with:
- CODESYS Control for Raspberry Pi SL (license in USB KEY)
- CODESYS KNX SL (license in USB KEY
I have configured both Codesys and ETS but it is not communicating.
On the KNX side I am using the "IP Interface SCN-IP000.03" (MDT) and I think this is the problem (in other topic Edwin recommend an IP ROUTER).
So I should replace the interface with "IP Router SCN-IP100.03" (MDT).
Do you think this could be the solution?
In the windows KNX I/O Mapping the variable Program LED Status and Program Button are BOOL but the variable are %IB0 and %QB0. Shouldn't it be% IX0.0 and & QX0.0?
I am attaching some screenshots.
Thank you
Can anyone answer me?
Thank you
Hi everyone,
since I haven't received information from anyone, if it can be useful to someone else, after some tests I discovered that the system can only work using an IP-ROUTER (I used an "IP Router SCN-IP100.03" from MDT).