IFM-Sensor ADC READ

taqamert
2024-08-23
2024-08-24
  • taqamert - 2024-08-23

    I have a pressure sensor that measures 0-600 bar and outputs a 0-5V signal, but my PLC reads analog inputs in the 0-10V range and displays a value of 1024 when 10V is applied. In this case, when the sensor outputs 5V at 600 bar, the PLC shows a value of 512. My working range is 0-350 bar, which means the PLC only uses 298 bits in this range, significantly reducing the resolution. What can I do to achieve better resolution within the 0-350 bar range?

     
  • IonCoder - 2024-08-24

    Get a different sensor that is 0-10V and 0-350 Bar. There is nothing you can reasonably do to boost the range of the sensor, and the PLC will only ever be 0-10V. Take away is to always be careful to match the sensor and PLC input ranges in the future.

     