For my first project with codesys and with modbus RTU.
This is a real hell.
i managed to send and receive using coils.
But i want to go further, i want ro readout the analog inputs from this drive over Modbus RTU.
This i can find in the holding register. The system from Danfos : " Register = (parameter x10)-1"
So i want to readout parameter 1620 so i nead to readout register 16119.
Okay, So i configured everything. but still got this error:" the value to be written is not valid"
Hi,
For my first project with codesys and with modbus RTU.
This is a real hell.
i managed to send and receive using coils.
But i want to go further, i want ro readout the analog inputs from this drive over Modbus RTU.
This i can find in the holding register. The system from Danfos : " Register = (parameter x10)-1"
So i want to readout parameter 1620 so i nead to readout register 16119.
Okay, So i configured everything. but still got this error:" the value to be written is not valid"
Anyone who can help me?
[
1620 * 10 - 1 = 16199 (not 16119)
oh god this is so stupid of me.
Thank you!