On the school iΒ΄m going to there is a couple of Festo MPS station.
The PLCΒ΄s are (in general) festo cpx-cec-c1 567347 b807.
On the Festo homepage it says that it works with codesys 2.3, but will it work with Codesys 3.5?
As i don't know if the technical specifications are updated since 3.5 was released i don't know if i need to go back to 2.3 or if i can make it work.
Does anyone have any answers/ideas?
Best,
Martin
Hi!
I solved the question so if there is anyone else who has the same question the answer is no.
You need to update the PLC to a CPX-CEC-C1-V3 (3473128).
This is according to email correspondence with the Festo support.
Best,