If I want to open some directory by the following way:
PROGRAM PLC_PRG
VAR
xDirOpen:BOOL;
DirOpen:FILE.DirOpen;
END_VAR
===================
IF xDirOpen THEN
REPEAT
DirOpen(xExecute:=xDirOpen,sDirName:='D:\myTestDir';
IF DirOpen.xDone OR DirOpen.xError THEN
xDirOpen:=FALSE;
DirOpen(xExecute:=FALSE);
END_IF
UNTIL NOT xDirOpen
END_REPEAT
END_IF
When the program is running,I change the value of xDirOpen from FALSE to TURE,but the result is endless loop!
Can someone give some explaination?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Remove the repeat / untill loop
It could take some scans before the OS returns a result.
Wait for the done/error and then set a condition to handle the next step.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
TimvH hat geschrieben:
Remove the repeat / untill loop
It could take some scans before the OS returns a result.
Wait for the done/error and then set a condition to handle the next step.
====================================================
Do you mean that the scan cannot be excute during a PLC cycle even if the PLC cycle takes a long time? but must be execute during the intervals between two PLC cycles?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Yes, that is my experience.
It is made like this to make sure it is non-blocking.
With the SysFile library the PLC execution halted untill the OS returned a result, but this was not good for time critical applications.
I don't know the exact reason behind it (internal operation) why it takes at least 2 scans.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
If I want to open some directory by the following way:
PROGRAM PLC_PRG
VAR
xDirOpen:BOOL;
DirOpen:FILE.DirOpen;
END_VAR
===================
IF xDirOpen THEN
REPEAT
DirOpen(xExecute:=xDirOpen,sDirName:='D:\myTestDir';
IF DirOpen.xDone OR DirOpen.xError THEN
xDirOpen:=FALSE;
DirOpen(xExecute:=FALSE);
END_IF
UNTIL NOT xDirOpen
END_REPEATEND_IF
When the program is running,I change the value of xDirOpen from FALSE to TURE,but the result is endless loop!
Can someone give some explaination?
Remove the repeat / untill loop
It could take some scans before the OS returns a result.
Wait for the done/error and then set a condition to handle the next step.
====================================================
Do you mean that the scan cannot be excute during a PLC cycle even if the PLC cycle takes a long time? but must be execute during the intervals between two PLC cycles?
Yes, that is my experience.
It is made like this to make sure it is non-blocking.
With the SysFile library the PLC execution halted untill the OS returned a result, but this was not good for time critical applications.
I don't know the exact reason behind it (internal operation) why it takes at least 2 scans.