Hi guys, i have some problem with X2 control (beijer). The pictures below is the errors appeared when I was log in. I can use profinet LAN to communicate with siemens.
Thanks for your help.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi guys, i have some problem with X2 control (beijer). The pictures below is the errors appeared when I was log in. I can use profinet LAN to communicate with siemens.
Thanks for your help.
Hi Apakrat!
In Codesys, Profinet needs a license in the runtime system. Did you install it?
If so, did you connect the correct Ethernet-adapter of your runtime system to the Ethernet device in your project? (see picture)
In the end, you have to call some program in the task "Profinet_IOTask" which will copy the IO-data into your program.
Good luck!
Alfred
Hi alwoso, I forget about the license. Thanks for your help.