We found a way to solve that problem. On the PFC200 both Ethernet port are bridged by default so you aren't able to use Ethercat in this configuration.
To remove this bridge you need to connect to the WBM of your PFC200 or you can do it with the linux command: cbm.
I hope that can be helpful.
Hugo.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,
I am working on SP17.1 with a PFC200 from WAGO and I am trying to add an Ethercat Master but as you can see below it doesn't work.
I have already tried with others version (SP16.3 and SP16.4) and I have checked all my hardware connections without success.
Also, I have already worked with Ethercat Master without any problem.
Do you have a solution to solve that problem ?
Thank you in advance,
Hugo.
We found a way to solve that problem. On the PFC200 both Ethernet port are bridged by default so you aren't able to use Ethercat in this configuration.
To remove this bridge you need to connect to the WBM of your PFC200 or you can do it with the linux command: cbm.
I hope that can be helpful.
Hugo.