CODESYS OPC UA - RPI AND CONTROL WIN V3

2021-06-25
2021-06-30
  • darrenredford - 2021-06-25

    I am Looking for some help with codesys runtime with OPC running on both the RPI and PC (Control Win V3).

    I dont seem to be able to set the OPC UA certificates, on both devises when I try top do this via the security view it says there is no OPC UA service running, which is strange as i am able to connect to both devices using UA expert, and change variables. screenshot below:

    FYI, I am trying top add the sevcsurity certficate as I am trying to connect ABB robot studio OPC client, but i think ot needs a trusted security secrtdciate to pull through the data.

    Any help is greatly appreciated. Thank you in advance. Darren.

     

    Last edit: darrenredford 2021-06-25
  • i-campbell

    i-campbell - 2021-06-25

    I believe.. "(not available)" means there is no certificate available because you haven't created one yet.
    select the row in the table and press the create certificate button.

     
    • darrenredford - 2021-06-30

      Good monring Campbell.

      Big thank you for your speedy help and assistance. I did what you suggested and that worked fine.

      Thank you so much, Very kind of you. Darren.

       