I have a EDS from Pneumax valve manufacturer. When i import in an other PLC software my output valve are available in PDO but when i import in Codesys ( no PDO are display ). When i remove the last part of the EDS ( optionnal input ) the PDO for the output appear. I supect that the optional input have something that Codesys didn't like ! See in the EDS file if you see what can be the problem with Codesys V3....
I don't know the details of the contents of .eds files, but I do know that CoDeSys V3 checks it better than CoDeSys V2.3.
With other .eds files CoDeSys V3 works OK. Therefore it must be related to an incorrect or incomplete .eds file.
I think you should contact your valve supplier for a file which conforms to the standard better.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I have a EDS from Pneumax valve manufacturer. When i import in an other PLC software my output valve are available in PDO but when i import in Codesys ( no PDO are display ). When i remove the last part of the EDS ( optionnal input ) the PDO for the output appear. I supect that the optional input have something that Codesys didn't like ! See in the EDS file if you see what can be the problem with Codesys V3....
Thank you .
Optyma_1_10.zip [1.77 KiB]
I don't know the details of the contents of .eds files, but I do know that CoDeSys V3 checks it better than CoDeSys V2.3.
With other .eds files CoDeSys V3 works OK. Therefore it must be related to an incorrect or incomplete .eds file.
I think you should contact your valve supplier for a file which conforms to the standard better.
You could run the EDS checker program from this site to see what may be the issue:
http://www.can-cia.org/index.php?id=841 m