Hi,
after adding Ethernet device, i push the Interface Browsing Button.
The pop-up is displayed "Gateway not configued property"
all the phenomenon is the same in Test Enviorment:
Codesys 3.5.15.0 , 3.5.14.2 ,
windows 7 64bit, 32bit
Windows 10 64bit
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
The button is trying to find this path:
CODESYS Development System
CODESYS Gateway
CODESYS Control Win V3
You have to make sure your gateway and Control Win V3 PLC are running, then configure the communication by double clicking the Control Win V3 at the top of your devices tree.
Hi,
after adding Ethernet device, i push the Interface Browsing Button.
The pop-up is displayed "Gateway not configued property"
all the phenomenon is the same in Test Enviorment:
Codesys 3.5.15.0 , 3.5.14.2 ,
windows 7 64bit, 32bit
Windows 10 64bit
Hi,
The button is trying to find this path:
CODESYS Development System
CODESYS Gateway
CODESYS Control Win V3
You have to make sure your gateway and Control Win V3 PLC are running, then configure the communication by double clicking the Control Win V3 at the top of your devices tree.
More detail can be found here:
https://help.codesys.com/webapp/_cds_tu ... g-sections m