With the information provided here, I will assume that the issue comes from the eds file.
For me, the connection path is incorrect. It seems that the last segment is not complete. The ODVA provide a tool called EZ-EDS that can read and interpret the eds file. You can register here to download the tool https://secure.odva.org/forms/ez-eds.htm m
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Dear sir:
i used CODESYS EthernetIP SCAN (Master) connection with omron PLC based on the EthernetIP protoocl,
When i Configuration omron PLC CJ2 EDS file in my projetc , but i see the "connection path " is invalid,
Could you please help me? it is EDS file problem or master /slave problem ,i have no clue.
Thanks a lot !
br,
Peter
Hello
With the information provided here, I will assume that the issue comes from the eds file.
For me, the connection path is incorrect. It seems that the last segment is not complete. The ODVA provide a tool called EZ-EDS that can read and interpret the eds file. You can register here to download the tool
https://secure.odva.org/forms/ez-eds.htm m
Dear ikisshandball:
thanks , i will re check the omron CJ PLC EDS file issue .
other one quesition ,
Does the CODEYS Ethernet IP Driver Scanner (master ) driver have support
CIP service -Explicit Messaging function or function block ?
Maybe I can change to use CIP service -Explicit Messaging like with omron CJ2 ethernet/IP PLC(omron support).
br,
Peter
Dear Sir :
Sorry for go back the topic ,
May i know if the codesys IDE can not use 3rd EDS file for Ethernet/IP tag mapping table,
How can i can connection with 3rd PLC ?
Can i use which function block for CIP service -Explicit Messaging to connection 3rd Ethernet PLC?
Thanks a lot !
BR,
Peter