Problem with downloading OPC UA tags by Data Source Manager

damian177
2024-09-03
2024-09-08
  • damian177 - 2024-09-03

    Hi,
    In Codesys V3.5 SP20, using Data Source Manager I am trying to connect to the OPC UA server and receive tags from it.
    The connection is ok, but the Codesys have a problem with downloading Tags group. The window (downloadingTags.jpg in attachement) never stop.
    After waiting for a while, I disconnect the connection and only the Server group remains downloaded, with OPC UA server diagnostic data (and this is read in Codesys).

    Of course, I tried connected via another OPC UA client : UaExpert , and everything works as it should, all tags are downloaded (Uaexpert.jpg screen).

    Has anyone on the forum encountered the OPC UA client configuration in Codesys?
    Is it possible to manually request the appropriate tags from the OPC server for reading in Codesys?

     
  • damian177 - 2024-09-04

    In my OPC UA Server is about 12 thousands tags. Can by possible that downloading tags from OPC UA Server lasts a long time , and when expires about 2 hours (demo license time) that downloading freezes ?

     
  • damian177 - 2024-09-04

    After 3 hours is some progress - please find in attachment - progress1.jpg

     
  • damian177 - 2024-09-08

    Unfortunately , Data Source Manager from Codesys has any problem with OPC UA Server delivered with ifix SCADA.
    Someone can help me add manually any tag from UaExpert to codesys ? How should be was a structure for an example of one tag ?

    I try like in attachement, but question is , if it a good idea ?

     

    Last edit: damian177 2024-09-08