After much trail and error I think I found the root cause to my OPC UA problem.
The problem is that I cannot manage to build and download a program with a a custom OPC UA Information model. We use a Weidmueller WL2000 PLS, but the problem also exsist on the Win V3 PLC.
Our custom information model is based on the latest versions of the OPC UA Core Nodeset v 1.05.03 (2023-09-20) and UA/DI nodeset 1.04.0 (2022-11-03)
Those nodesets are installed in the Codesys Information Model Repository (3.5.19.6)
However, when trying to build I get the following error.
[ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://bos.org/ with a minimal publication date from 15.12.2023 but the device has only a model from 15.09.2021 installed. Probably the information model from 15.09.2021 is missing in the information model repository. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/DI/ is required by http://bos.org/ with a minimal publication date from 03.11.2022 but the device has only a model from 09.03.2021 installed. Probably the information model from 09.03.2021 is missing in the information model repository.
Build complete -- 2 errors, 1 warnings : No download possible
I think the problem is that the UA Core nodeset is implemented in the PLC firmware (at least that in Siemens S7), and that only includes the "old" nodeset from 2021-09-21 etc.
So the question is, how (or if?) can I transfer the new nodeset to the PLS? I have created separate Information models under Communication manager with the newer code nodesets (UA and DI).
But it seems that the compiler does not recognize them being excising, neither in the Codesys IDE or on the PLC.
Would have guessed that this is a common issue, sine many manufacturers use the latest versions of the OPC UA standard, and that it would be a solution to the problem.
Hi
After much trail and error I think I found the root cause to my OPC UA problem.
The problem is that I cannot manage to build and download a program with a a custom OPC UA Information model. We use a Weidmueller WL2000 PLS, but the problem also exsist on the Win V3 PLC.
Our custom information model is based on the latest versions of the OPC UA Core Nodeset v 1.05.03 (2023-09-20) and UA/DI nodeset 1.04.0 (2022-11-03)
Those nodesets are installed in the Codesys Information Model Repository (3.5.19.6)
However, when trying to build I get the following error.
[ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://bos.org/ with a minimal publication date from 15.12.2023 but the device has only a model from 15.09.2021 installed. Probably the information model from 15.09.2021 is missing in the information model repository.
[ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/DI/ is required by http://bos.org/ with a minimal publication date from 03.11.2022 but the device has only a model from 09.03.2021 installed. Probably the information model from 09.03.2021 is missing in the information model repository.
Build complete -- 2 errors, 1 warnings : No download possible
I think the problem is that the UA Core nodeset is implemented in the PLC firmware (at least that in Siemens S7), and that only includes the "old" nodeset from 2021-09-21 etc.
So the question is, how (or if?) can I transfer the new nodeset to the PLS? I have created separate Information models under Communication manager with the newer code nodesets (UA and DI).
But it seems that the compiler does not recognize them being excising, neither in the Codesys IDE or on the PLC.
Would have guessed that this is a common issue, sine many manufacturers use the latest versions of the OPC UA standard, and that it would be a solution to the problem.