I have a problem with the CODESYS IO-Link SL software. When I insert a IO link master AL1332 and plug a discrete digital input to a channel it reads only 1 of the 2 available inputs on that channel. Is there anyone who sorted out if the second input is also usable?
When we configure the module without the CODESYS IO-Link SL software then the second input on the channel can be used. At the moment we use some channels on a module as IO-link port, and some as discrete IO. It would be very nice if we can use both inputs on a channel with the use of CODESYS IO-Link SL.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Try changing the port mode to digital input for each port you want to have 2 inputs in the connection settings for the device. I've successfully used ports for inputs on an AL1920 this way, I think the procedure should be the same for an AL1332.
I have a problem with the CODESYS IO-Link SL software. When I insert a IO link master AL1332 and plug a discrete digital input to a channel it reads only 1 of the 2 available inputs on that channel. Is there anyone who sorted out if the second input is also usable?
When we configure the module without the CODESYS IO-Link SL software then the second input on the channel can be used. At the moment we use some channels on a module as IO-link port, and some as discrete IO. It would be very nice if we can use both inputs on a channel with the use of CODESYS IO-Link SL.