This is maybe more ethercat-related, but I am sure someone here knows how to deal.
I have a Beckhoff EL3403 -energymeter unit, working smoothly.
Just now I am having hard times, because I should work with the process data.
For example:
The unit is counting energyconsumption by itself whenever running and saving result to its own persistent data bank.
Monitoring the value is easy, since it is one of the default variables in mapping list.
But I want to reset the value from command and this should be done by "entering 0004hex to index 0xFB00:01.
What does this actually mean and how to proceed?
Do I need to add this index to process data inputs to be able to map it and then set the value?
I already tried, but I was not succesful. (After download the bus is not going up)
-Juha
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
So, after reading manuals all over, I found what I need, but still not getting it to work...
So, in this case the dataflow between Master and Slave is CanOpen over EtherCAT ( CoE ).
Only way to change the value is to either set Startup value or Write the process data.
So, with codesys-package there comes this IODrvEtherCAT -library.
There is a function block "ETC_CO_SdoWRITE4" with which you can write values to process data.
So,
to delete the energy values of all channels manually enter 0004hex in index 0xFB00:01
I enter following values to my CoE-writer:
xExecute = TRUE
xAbort = empty
usiCom = 1 (Number of Ethercat master)
uiDevice = 1005 (Number of the slave device)
usiChannel = empty
wIndex = 64256 (FB00 -> decimal because datatype WORD)(should it be like this???)
bySubindex = 1
udiTimeOut = 500 (ms)
abyData = 4 *HOW TO WRITE THAT 0004hex here?? datatype should be ARRAY [1,,4] OF BYTE
usiDataLength = 2 ?* datatype should be USINT
Do I need to do something else to get this work, like take some global variable from that IODrvEtherCAT -library or something else.
//EDIT:wrong picture
-Juha
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
juhataipale hat geschrieben:
So, after reading manuals all over, I found what I need, but still not getting it to work...
So, in this case the dataflow between Master and Slave is CanOpen over EtherCAT ( CoE ).
Only way to change the value is to either set Startup value or Write the process data.
So, with codesys-package there comes this IODrvEtherCAT -library.
There is a function block "ETC_CO_SdoWRITE4" with which you can write values to process data.
ADS_kommu_block.JPG
So,
to delete the energy values of all channels manually enter 0004hex in index 0xFB00:01
I enter following values to my CoE-writer:
xExecute = TRUE
xAbort = empty
usiCom = 1 (Number of Ethercat master)
uiDevice = 1005 (Number of the slave device)
usiChannel = empty
wIndex = 64256 (FB00 -> decimal because datatype WORD)(should it be like this???)
bySubindex = 1
udiTimeOut = 500 (ms)
abyData = 4 *HOW TO WRITE THAT 0004hex here?? datatype should be ARRAY [1,,4] OF BYTE
usiDataLength = 2 ?* datatype should be USINT
Do I need to do something else to get this work, like take some global variable from that IODrvEtherCAT -library or something else.
//EDIT:wrong picture
-Juha
Got it work, so maybe this can help someone...
Remember to use trigger in execute input!
See photo below, how to proceed the rest.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
juhataipale hat geschrieben:
So, after reading manuals all over, I found what I need, but still not getting it to work...
So, in this case the dataflow between Master and Slave is CanOpen over EtherCAT ( CoE ).
Only way to change the value is to either set Startup value or Write the process data.
So, with codesys-package there comes this IODrvEtherCAT -library.
There is a function block "ETC_CO_SdoWRITE4" with which you can write values to process data.
ADS_kommu_block.JPG
So,
to delete the energy values of all channels manually enter 0004hex in index 0xFB00:01
I enter following values to my CoE-writer:
xExecute = TRUE
xAbort = empty
usiCom = 1 (Number of Ethercat master)
uiDevice = 1005 (Number of the slave device)
usiChannel = empty
wIndex = 64256 (FB00 -> decimal because datatype WORD)(should it be like this???)
bySubindex = 1
udiTimeOut = 500 (ms)
abyData = 4 *HOW TO WRITE THAT 0004hex here?? datatype should be ARRAY [1,,4] OF BYTE
usiDataLength = 2 ?* datatype should be USINT
Do I need to do something else to get this work, like take some global variable from that IODrvEtherCAT -library or something else.
//EDIT:wrong picture
-Juha
Hello Juha,
I am new to CoDeSys. Can you please tell me how to access IODrvEtherCAT library through CoDeSys Engineering so that I can access the FB you mentioned.
Thanks and Kind Regards
Zahoor
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello all,
This is maybe more ethercat-related, but I am sure someone here knows how to deal.
I have a Beckhoff EL3403 -energymeter unit, working smoothly.
Just now I am having hard times, because I should work with the process data.
For example:
The unit is counting energyconsumption by itself whenever running and saving result to its own persistent data bank.
Monitoring the value is easy, since it is one of the default variables in mapping list.
But I want to reset the value from command and this should be done by "entering 0004hex to index 0xFB00:01.
What does this actually mean and how to proceed?
Do I need to add this index to process data inputs to be able to map it and then set the value?
I already tried, but I was not succesful. (After download the bus is not going up)
-Juha
So, after reading manuals all over, I found what I need, but still not getting it to work...
So, in this case the dataflow between Master and Slave is CanOpen over EtherCAT ( CoE ).
Only way to change the value is to either set Startup value or Write the process data.
So, with codesys-package there comes this IODrvEtherCAT -library.
There is a function block "ETC_CO_SdoWRITE4" with which you can write values to process data.
So,
to delete the energy values of all channels manually enter 0004hex in index 0xFB00:01
I enter following values to my CoE-writer:
xExecute = TRUE
xAbort = empty
usiCom = 1 (Number of Ethercat master)
uiDevice = 1005 (Number of the slave device)
usiChannel = empty
wIndex = 64256 (FB00 -> decimal because datatype WORD)(should it be like this???)
bySubindex = 1
udiTimeOut = 500 (ms)
abyData = 4 *HOW TO WRITE THAT 0004hex here?? datatype should be ARRAY [1,,4] OF BYTE
usiDataLength = 2 ?* datatype should be USINT
Do I need to do something else to get this work, like take some global variable from that IODrvEtherCAT -library or something else.
//EDIT:wrong picture
-Juha
Got it work, so maybe this can help someone...
Remember to use trigger in execute input!
See photo below, how to proceed the rest.