With over ~100 adapters i got new issues:
- if scanner have more then ~20 adapters, connected devices over ~20 gone failed with error about buffer size, so now I have 5 scanners with 20 adapters each;
- with such number of adapters, time by time got connection timed out. The only way for now is to change timeout value on each adapter, so I want to assign a single parameter somewhere.
- with changing IP addresses of adapters they are hunging-up with error 100 (Duplicate Forward Open), but it happens only if connection was established on this adapter before, so restart of runtime helps.
I was looking for some parameters to be changed, and I found some properties:
"RemoteAdapter.EncapsulationKeepAliveInterval"
"RemoteAdapter.MaxConnectionSize"
- but nothing about what are they affecting on.
So here the question: anybody know the better way to fix this issues?
hello!
With over ~100 adapters i got new issues:
- if scanner have more then ~20 adapters, connected devices over ~20 gone failed with error about buffer size, so now I have 5 scanners with 20 adapters each;
- with such number of adapters, time by time got connection timed out. The only way for now is to change timeout value on each adapter, so I want to assign a single parameter somewhere.
- with changing IP addresses of adapters they are hunging-up with error 100 (Duplicate Forward Open), but it happens only if connection was established on this adapter before, so restart of runtime helps.
I was looking for some parameters to be changed, and I found some properties:
"RemoteAdapter.EncapsulationKeepAliveInterval"
"RemoteAdapter.MaxConnectionSize"
- but nothing about what are they affecting on.
So here the question: anybody know the better way to fix this issues?
P.S. found very useful paper (EthernetIP Connection Status Messages), check it if you need to https://www.unitronicsplc.com/Download/SoftwareHelp/UniLogic_Knowledgebase/Communications/EthernetIP_Connection_Status_Messages.htm