Modbus: dis- / re-connect cable: modbus does not re-start

chab
2013-09-27
2013-09-28
  • chab - 2013-09-27

    Hi all,
    Recently I used the Modbus master library (CoDeSys V3.5.3.0).
    And I noticed that dis-connecting and re-connecting the serial cable does NOT restart the Modbus protocol.
    Do you have any experience with (re-) starting the Modbus protocol?
    Is there a way to:
    - detect that the Modbus protocol is not running.
    - (re-) start the Modbus protocol manually (by the application).
    Any help is appreciated.
    Regards,
    Edwin.

     
  • TimvH

    TimvH - 2013-09-27

    Yes, this is known.

    In the device tree you can set the name of your slaves (right click => properties).
    This name is the instance of your Modbus Slave.

    To detect the error and reset the communication you can use e.g. (mbSlave1 is the name of my Modbus slave device):
    IF mbSlave1.xError THEN
    mbSlave1.xReset := TRUE;
    ELSE
    mbSlave1.xReset := FALSE;
    END_IF


    To get the error message you can use
    VAR
    bySlave1Error: IODRVMODBUS.MB_ErrorCodes;
    END_VAR

    bySlave1Error := mbSlave1.byModbusError;

     
  • chab - 2013-09-27

    Tim,
    Thank you for your quick answer.
    I'll apply it immediately.
    Do you know where I can find a list of known issues?
    (I do not have access to the CoDeSys jira database.)
    Regards,
    Edwin.

     
  • TimvH

    TimvH - 2013-09-28

    Please contact your supplier for this.
    Jira is only accessable for direct customers (OEMs) of 3S-Smart Software Solutions and Distributors.

     