Looking at the last few lines, it looks like you try to access a drive with number "0". That's not a real drive adress, please check your program for correct drive adresses when calling the SDORead function.
Good luck!
Alfred
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
alwoso hat geschrieben:
Hi nozomiv!
Looking at the last few lines, it looks like you try to access a drive with number "0". That's not a real drive adress, please check your program for correct drive adresses when calling the SDORead function.
Good luck!
Alfred
hi!
I changed Numuber of the slave from 0 to1.
"number of slaves has changed or is different to the configuration" error happend:
01534311747630: Cmp=IoDrvEtherCAT, Class=2, Error=0, Info=0, pszInfo=!!!! AL Status read from slave address 1001 status 16#00 : No error
01534311757233: Cmp=SoftMotion, Class=4, Error=0, Info=0, pszInfo=* FBError Drive=1: 1 general communication error
01534311757233: Cmp=SoftMotion, Class=1, Error=0, Info=0, pszInfo= ErrorInstance = Unknown
01534311771079: Cmp=IoDrvEtherCAT, Class=2, Error=0, Info=0, pszInfo=!!!! AL Status read from slave address 1001 status 16#34 : Invalid DC Timeout Error
01534311773133: Cmp=IoDrvEtherCAT, Class=4, Error=0, Info=0, pszInfo=* Warning: number of slaves has changed or is different to the configuration!
01534311775150: Cmp=IoDrvEtherCAT, Class=2, Error=0, Info=0, pszInfo=!!!! AL Status read from slave address 1001 status 16#34 : Invalid DC Timeout Error
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
When I start SoftMotion Win V3, it displays error like this:
how to solve it?
Hi nozomiv!
Looking at the last few lines, it looks like you try to access a drive with number "0". That's not a real drive adress, please check your program for correct drive adresses when calling the SDORead function.
Good luck!
Alfred
hi!
I changed Numuber of the slave from 0 to1.
"number of slaves has changed or is different to the configuration" error happend:
01534311747630: Cmp=IoDrvEtherCAT, Class=2, Error=0, Info=0, pszInfo=!!!! AL Status read from slave address 1001 status 16#00 : No error
01534311757233: Cmp=SoftMotion, Class=4, Error=0, Info=0, pszInfo=* FBError Drive=1: 1 general communication error
01534311757233: Cmp=SoftMotion, Class=1, Error=0, Info=0, pszInfo= ErrorInstance = Unknown
01534311771079: Cmp=IoDrvEtherCAT, Class=2, Error=0, Info=0, pszInfo=!!!! AL Status read from slave address 1001 status 16#34 : Invalid DC Timeout Error
01534311773133: Cmp=IoDrvEtherCAT, Class=4, Error=0, Info=0, pszInfo=* Warning: number of slaves has changed or is different to the configuration!
01534311775150: Cmp=IoDrvEtherCAT, Class=2, Error=0, Info=0, pszInfo=!!!! AL Status read from slave address 1001 status 16#34 : Invalid DC Timeout Error