Hi, Iβm currently testing the Codesys Redundancy application with 2 Raspberry Pi, with the idea is of using in my project 2 Wago PFC200 and 1 Ethercat Master with 2 Remote IO.
After I configure the redundancy, and one Pi is Active and the other is Passive, if I disconnect the Ethernet cable of the Active, the Passive become Standalone, which is good, but the problem is the following:
-When I recover the Ethernet connection, both stay Standalone. They will NOT Sync until I do it manually in the Codesys environment. How to make the synchronization automatically?
-If both Pi/PLC stays Standalone, who is managing the IO? (Ethercat and Serial) I have done a test with an Modbus Slave, where I am sending a counter that increase every second. And I see that when both PLC are standalone, they both keep an active connection with the Slave, and both write values.
This does not seem good, since according to this in my project both PLC would try to control the IO at the same time.
Note: The Codesys have an option (greyed out, not possible to select) which says βAuto Syncβ. What is the purpose, and why Iβm not able to select it?
I'm using Codesys Control for Rapsberry Pi 64SL Runtime in my test environment (2xRaspberry Pi 4), with the idea of using Codesys Control PFC 200 Runtime in my project (2xWago PFC200 and 1 Ethercat Master with 2x Wago 750-354 Ethercat Fieldbus Coupler). Using the last Codesys 3.5 version (SP19 PAtch 5).
I'd appreciate a lot any help on this questions!
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,
Has anyone figured out the Standalone issue after a network break? I have the similar behavior with two 750-8212 WAGO controllers. Using firmware 27 and CODESYS 3.5.19.70.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi, Iβm currently testing the Codesys Redundancy application with 2 Raspberry Pi, with the idea is of using in my project 2 Wago PFC200 and 1 Ethercat Master with 2 Remote IO.
After I configure the redundancy, and one Pi is Active and the other is Passive, if I disconnect the Ethernet cable of the Active, the Passive become Standalone, which is good, but the problem is the following:
-When I recover the Ethernet connection, both stay Standalone. They will NOT Sync until I do it manually in the Codesys environment. How to make the synchronization automatically?
-If both Pi/PLC stays Standalone, who is managing the IO? (Ethercat and Serial) I have done a test with an Modbus Slave, where I am sending a counter that increase every second. And I see that when both PLC are standalone, they both keep an active connection with the Slave, and both write values.
This does not seem good, since according to this in my project both PLC would try to control the IO at the same time.
Note: The Codesys have an option (greyed out, not possible to select) which says βAuto Syncβ. What is the purpose, and why Iβm not able to select it?
I'm using Codesys Control for Rapsberry Pi 64SL Runtime in my test environment (2xRaspberry Pi 4), with the idea of using Codesys Control PFC 200 Runtime in my project (2xWago PFC200 and 1 Ethercat Master with 2x Wago 750-354 Ethercat Fieldbus Coupler). Using the last Codesys 3.5 version (SP19 PAtch 5).
I'd appreciate a lot any help on this questions!
Hello,
Has anyone figured out the Standalone issue after a network break? I have the similar behavior with two 750-8212 WAGO controllers. Using firmware 27 and CODESYS 3.5.19.70.