I would like to share some information on this site for the Codesys team as well for the future members using Codesys Control for PLCnext if it is allowed. I hope that i Post it in the correct spot.
Subject:
Codesys, Codesys Control for PLCnext
Objective:
Using the following Phoenix components to built a PLC Rack and run it on Codesys:
Hardware and Software used
1. 2404267, AXC F 2152 - Controller
2. 1088136, AXL F BP SE6 - Module carrier
3. 1088129, AXL SE DO16/1 - Digital module
4. 1337224, AXL SE PD16 GND - Potential distributors
5. 1088127, AXL SE DI16/1 - Digital module
6. 1337223, AXL SE PD16 24V - Potential distributors
7. 1088123, AXL SE AO4 I 4-20 - Analog module
8. 1088134, AXL SE SC-A - Cover
9. Codesys v3.5 SP19 Patch 4
10. Codesys Control for PLCnext V4.10.0.0
Process:
Firstly I built the Rack according to the Phoenix Project+ Software tool. Where I rebuilt it onto my test bench .
I used the PLCnext Engineer IDE from Phoenix and all Communications where up and running and my PLC program executed successfully.
THEN
I tried the same PLC Layout with Codesys and Codesys Control for PLCnext. It was not successful and gave me the "Error: Local Bus not Running".
I searched the web for answers but was unsuccessful in finding a solution.
So I tried to change my configuration and found that the following Modules COULD NOT be recognized by Codesys Control. The result was that the Local Bus Failed to run.
1337224, AXL SE PD16 GND - Potential distributors
1337223, AXL SE PD16 24V - Potential distributors
Example 1, Resulted in "Error: Local Bus Not Running":
Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module
Module carrier slot 2: 1337224, AXL SE PD16 GND - Potential distributors
Module carrier slot 3: 1088127, AXL SE DI16/1 - Digital module
Module carrier slot 4: 1337223, AXL SE PD16 24V - Potential distributors
Module carrier slot 5: 1088123, AXL SE AO4 I 4-20 - Analog module
Module carrier slot 6: 1088134, AXL SE SC-A - Cover
Example 2, Result "Successful":
Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module
Module carrier slot 2: 1088127, AXL SE DI16/1 - Digital module
Module carrier slot 3: 1088123, AXL SE AO4 I 4-20 - Analog module
Module carrier slot 4: 1088134, AXL SE SC-A - Cover
Module carrier slot 5: 1088134, AXL SE SC-A - Cover
Module carrier slot 6: 1088134, AXL SE SC-A - Cover
Result:
Codesys or Codesys Control for PLCnext, has a PROBLEM to identify the following Modules.
1. AXL SE PD16 24V - Potential distributors
2. AXL SE PD16 GND - Potential distributors
Hope that this information could be useful in future.
Best regards
Jaco Pretorius
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I came across your post regarding CodeSys control for PLCnext. Iβm currently working on a similar setup and had a quick question.
Here am using the CODESYS V3.5 SP21 PATCH2 ,VERSION 3.5.21.20 , and Downloaded extension package 4.16.0.0 (old versions are not available in the extension CodeSys installer)
Devices used here are:
BUS COUPLER : 2403869 BK PN TPS
Module carrier slot 1 : 1088127 AXL SE DI16/1
Module carrier slot 2 : 1088062 AXL SE AI4 | 4-20
Module carrier slot 3 : 1088129 AXL SE DO16/1
Module carrier slot 4 : 1088123 AXL SE AO4 | 4-20
-->Start a New Project
Type: Standard Project
Device: CODESYS Control Win V3 x64
Language: Structured Text
-->Install GSDML File
Navigate to: Tools > Device Repository > Install
Select the GSDML file path (downloaded from Phoenix Contact for device coupler Part ID: BK PN TPS 2403869)
Click Renew Device Repository
Close the dialog
-->Add Device to Project
-->Right-click on Devices > Add Device
Issue: Devices from the repository are not available to select or call into the project!
Iβd really appreciate any guidance or suggestions you can offer.
I came across your post regarding CodeSys control for PLCnext. Iβm currently working on a similar setup and had a quick question.
Here am using the CODESYS V3.5 SP21 PATCH2 ,VERSION 3.5.21.20 , and Downloaded extension package 4.16.0.0 (old versions are not available in the extension CodeSys installer)
Devices used here are:
BUS COUPLER : 2403869 BK PN TPS
Module carrier slot 1 : 1088127 AXL SE DI16/1
Module carrier slot 2 : 1088062 AXL SE AI4 | 4-20
Module carrier slot 3 : 1088129 AXL SE DO16/1
Module carrier slot 4 : 1088123 AXL SE AO4 | 4-20
-->Start a New Project
Type: Standard Project
Device: CODESYS Control Win V3 x64
Language: Structured Text
-->Install GSDML File
Navigate to: Tools > Device Repository > Install
Select the GSDML file path (downloaded from Phoenix Contact for device coupler Part ID: BK PN TPS 2403869)
Click Renew Device Repository
Close the dialog
-->Add Device to Project
-->Right-click on Devices > Add Device
Issue: Devices from the repository are not available to select or call into the project!
Iβd really appreciate any guidance or suggestions you can offer.
Do not filter on Phoenix devices.
First add an Ethernet device (from CODESYS). Then add a Profinet Controller (from CODESYS). Then add your Phoenix devices to this CODESYS Profinet Controller.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Good day All
I would like to share some information on this site for the Codesys team as well for the future members using Codesys Control for PLCnext if it is allowed. I hope that i Post it in the correct spot.
Subject:
Codesys, Codesys Control for PLCnext
Objective:
Using the following Phoenix components to built a PLC Rack and run it on Codesys:
Hardware and Software used
1. 2404267, AXC F 2152 - Controller
2. 1088136, AXL F BP SE6 - Module carrier
3. 1088129, AXL SE DO16/1 - Digital module
4. 1337224, AXL SE PD16 GND - Potential distributors
5. 1088127, AXL SE DI16/1 - Digital module
6. 1337223, AXL SE PD16 24V - Potential distributors
7. 1088123, AXL SE AO4 I 4-20 - Analog module
8. 1088134, AXL SE SC-A - Cover
9. Codesys v3.5 SP19 Patch 4
10. Codesys Control for PLCnext V4.10.0.0
Process:
Firstly I built the Rack according to the Phoenix Project+ Software tool. Where I rebuilt it onto my test bench .
I used the PLCnext Engineer IDE from Phoenix and all Communications where up and running and my PLC program executed successfully.
THEN
I tried the same PLC Layout with Codesys and Codesys Control for PLCnext. It was not successful and gave me the "Error: Local Bus not Running".
I searched the web for answers but was unsuccessful in finding a solution.
So I tried to change my configuration and found that the following Modules COULD NOT be recognized by Codesys Control. The result was that the Local Bus Failed to run.
1337224, AXL SE PD16 GND - Potential distributors
1337223, AXL SE PD16 24V - Potential distributors
Example 1, Resulted in "Error: Local Bus Not Running":
Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module
Module carrier slot 2: 1337224, AXL SE PD16 GND - Potential distributors
Module carrier slot 3: 1088127, AXL SE DI16/1 - Digital module
Module carrier slot 4: 1337223, AXL SE PD16 24V - Potential distributors
Module carrier slot 5: 1088123, AXL SE AO4 I 4-20 - Analog module
Module carrier slot 6: 1088134, AXL SE SC-A - Cover
Example 2, Result "Successful":
Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module
Module carrier slot 2: 1088127, AXL SE DI16/1 - Digital module
Module carrier slot 3: 1088123, AXL SE AO4 I 4-20 - Analog module
Module carrier slot 4: 1088134, AXL SE SC-A - Cover
Module carrier slot 5: 1088134, AXL SE SC-A - Cover
Module carrier slot 6: 1088134, AXL SE SC-A - Cover
Result:
Codesys or Codesys Control for PLCnext, has a PROBLEM to identify the following Modules.
1. AXL SE PD16 24V - Potential distributors
2. AXL SE PD16 GND - Potential distributors
Hope that this information could be useful in future.
Best regards
Jaco Pretorius
Hello Jaco Pretorius,
I came across your post regarding CodeSys control for PLCnext. Iβm currently working on a similar setup and had a quick question.
Here am using the CODESYS V3.5 SP21 PATCH2 ,VERSION 3.5.21.20 , and Downloaded extension package 4.16.0.0 (old versions are not available in the extension CodeSys installer)
Devices used here are:
BUS COUPLER : 2403869 BK PN TPS
Module carrier slot 1 : 1088127 AXL SE DI16/1
Module carrier slot 2 : 1088062 AXL SE AI4 | 4-20
Module carrier slot 3 : 1088129 AXL SE DO16/1
Module carrier slot 4 : 1088123 AXL SE AO4 | 4-20
-->Start a New Project
Type: Standard Project
Device: CODESYS Control Win V3 x64
Language: Structured Text
-->Install GSDML File
Navigate to: Tools > Device Repository > Install
Select the GSDML file path (downloaded from Phoenix Contact for device coupler Part ID: BK PN TPS 2403869)
Click Renew Device Repository
Close the dialog
-->Add Device to Project
-->Right-click on Devices > Add Device
Issue: Devices from the repository are not available to select or call into the project!
Iβd really appreciate any guidance or suggestions you can offer.
Best Regards
Ranadheer Reddy
Hello Jaco Pretorius,
I came across your post regarding CodeSys control for PLCnext. Iβm currently working on a similar setup and had a quick question.
Here am using the CODESYS V3.5 SP21 PATCH2 ,VERSION 3.5.21.20 , and Downloaded extension package 4.16.0.0 (old versions are not available in the extension CodeSys installer)
Devices used here are:
BUS COUPLER : 2403869 BK PN TPS
Module carrier slot 1 : 1088127 AXL SE DI16/1
Module carrier slot 2 : 1088062 AXL SE AI4 | 4-20
Module carrier slot 3 : 1088129 AXL SE DO16/1
Module carrier slot 4 : 1088123 AXL SE AO4 | 4-20
-->Start a New Project
Type: Standard Project
Device: CODESYS Control Win V3 x64
Language: Structured Text
-->Install GSDML File
Navigate to: Tools > Device Repository > Install
Select the GSDML file path (downloaded from Phoenix Contact for device coupler Part ID: BK PN TPS 2403869)
Click Renew Device Repository
Close the dialog
-->Add Device to Project
-->Right-click on Devices > Add Device
Issue: Devices from the repository are not available to select or call into the project!
Iβd really appreciate any guidance or suggestions you can offer.
Best Regards
Ranadheer Reddy
Do not filter on Phoenix devices.
First add an Ethernet device (from CODESYS). Then add a Profinet Controller (from CODESYS). Then add your Phoenix devices to this CODESYS Profinet Controller.