I have the Raspberry Pi 2 Model B with the latest CoDeSys 3.5.8.10.
The Ethernet/IP Scanner is not able to receive the data on cyclic connection, but data are available via GET_Attribute_Single.
With the same EDS file insert into CompactLogix, I'm able to read the value.
Did I miss anything in the CoDeSys setting?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I have the Raspberry Pi 2 Model B with the latest CoDeSys 3.5.8.10.
The Ethernet/IP Scanner is not able to receive the data on cyclic connection, but data are available via GET_Attribute_Single.
With the same EDS file insert into CompactLogix, I'm able to read the value.
Did I miss anything in the CoDeSys setting?
Found the solution, need to set the box "Always update variables" to Enable 2 (always in bus cycle task) or Enable 1.