I am working in Codesys 3.5 SP17 Patch 3. When I try to login to the PLC I get the two errors seen in the screenshot. I have tried changing the version of CMPTLS, CMPTLSImplementation, and SysSocket2 in the placeholders tab of the Library Manager. I have also "Repaired" Codesys via the Codesys installer however have been unsuccessful so far. Has anyone run into this before?
hi,
looks like the library CmpTls implementation is not supported by the runtime on the device. Check with the manufacturer. Maybe there is a newer firmware for the device which supports the CmpTls component.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,
I am working in Codesys 3.5 SP17 Patch 3. When I try to login to the PLC I get the two errors seen in the screenshot. I have tried changing the version of CMPTLS, CMPTLSImplementation, and SysSocket2 in the placeholders tab of the Library Manager. I have also "Repaired" Codesys via the Codesys installer however have been unsuccessful so far. Has anyone run into this before?
Thanks!
hi,
looks like the library CmpTls implementation is not supported by the runtime on the device. Check with the manufacturer. Maybe there is a newer firmware for the device which supports the CmpTls component.
Thanks! I'll give that a go.