    Hello,

    I have configured and tested the ADS1115 by looking at the forums below.
    https://forge.codesys.com/forge/talk/Runtime/thread/f1400b71b6/?limit=25#9623

    As a result, I was able to get a full scale 2048 count with the FSR_2048mV setting, however, due to the low resolution, we would like to change this full scale to 32767. How can I get the raw AD count value as it is?

     
  • mark0328 - 2021-04-01

    Hi Ian,
    Thank you for your advice.
    We could change the resolution to 32000 from 2000 on our environment.
    This version is 1.0.0.1, please refer attach library and device profile.

     