I am having trouble getting the alarm table filtering to work. I downloaded the alarm filter latch example project and ran it on the local Codesys Control Win and the filters worked fine. I am trying to replicate it in my project and everything seems to be set up the exact same way and every time I turn on the filter, it shows no alarms. I even started a blank project and just copied in elements from the example project so that it is exactly the same and when I attempt to filter, it again shows no alarms. Could there be some project settings I need to adjust to make this work? I have attached my project with elements copied from the example project and filtering is not working.
I actually just found the solution maybe. If anyone else is running into this, go to your Project Settings > Visualization > Advanced (check 'Visible' to see advanced settings) > UNCHECK 'Activate property handling in all element properties.' I am not sure what else unchecking this might affect but it seems to allow the alarm table to be filtered as expected.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I am having trouble getting the alarm table filtering to work. I downloaded the alarm filter latch example project and ran it on the local Codesys Control Win and the filters worked fine. I am trying to replicate it in my project and everything seems to be set up the exact same way and every time I turn on the filter, it shows no alarms. I even started a blank project and just copied in elements from the example project so that it is exactly the same and when I attempt to filter, it again shows no alarms. Could there be some project settings I need to adjust to make this work? I have attached my project with elements copied from the example project and filtering is not working.
I actually just found the solution maybe. If anyone else is running into this, go to your Project Settings > Visualization > Advanced (check 'Visible' to see advanced settings) > UNCHECK 'Activate property handling in all element properties.' I am not sure what else unchecking this might affect but it seems to allow the alarm table to be filtered as expected.