Post by ricola on ERROR: CodeMAccess2: Used CmRuntime 2.61.2705.500 is too old
CODESYS Forge
talk
(Post)
hi there , can someone tell me how to deal with this error , please? I use the Linux ARM64SL (4.11) on a bullseye distro and when I want to update or install some package, I have the following reply : pi@NanoPi-R5C:~$ sudo apt upgrade Reading package lists... Done Building dependency tree... Done Reading state information... Done You might want to run 'apt --fix-broken install' to correct these. The following packages have unmet dependencies: ** codesyscontrol : Depends: codemeter but it is not installable or codemeter-lite but it is not installable** E: Unmet dependencies. Try 'apt --fix-broken install' with no packages (or specify a solution). and if I try apt --fix-broken install as suggested, I have a proposal to uninstall codesyscontrol ... :-D so I tried to search if there is some Codesys repo: nothing, then I tried to see if ther was something inside Codesys dev (V3.5.20) and I only found that by reading/requesting my device, i spoted that codemeter was too old . I don't see how to deal with this issue. is there a codemeter.deb somewhere ? thanks in advance for any help.
Last updated: 2024-09-17
Post by imdatatas on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
Hello, I have experienced such situations with some servo drive devices in the past. The home completion information is reported to the upper controller by the slave drive with the states of the relevant bits in the StatusWord (for example; 6041h Bit10, Bit12 in Home mode). If the states of these bits are correct in terms of number and state but the motor does not actually perform the action; You can contact the slave drive manufacturer. There may be a problem with the device firmware. Another area you can play around with is looking at the settings in the "Advanced configuration" for Softmotion axis on the page the link to below, and trying it out and using the one that works for you. https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_cmd_add_softmotion_cia402_axis.html A method I recommended worked for a user as in below message. https://forge.codesys.com/forge/talk/Engineering/thread/40bc82454d/ I hope your problem will be solved as soon as possible and by sharing the result here, you will help others to know and overcome it. Good luck. Best regards, Imdat
Last updated: 2025-01-08
Post by timvh on Device diagnosis ( EtherCAT IO card )
CODESYS Forge
talk
(Post)
You can get the state by just using the name of your node (same name as in device tree): VAR etcState: IoDrvEthercatDriverLib.ETC_SLAVE_STATE; END_VAR etcState := EJ1100.wState; Alternatively, you can iterate through the device tree to get the status of all (Ethercat) nodes. See here an example (no guarantee it works, just give as suggestion): PROGRAM P_IO_State VAR CONSTANT uiMAX_NR_OF_TERMINALS : UINT := 100; END_VAR VAR // general device diagnosis // can only be used when the Device - PLC Settings - Advanced settings - enable diagnosis for devices is enabled // this will add the DED library coupler: DED.INode; terminal: DED.INode; aDeviceState: ARRAY[0..uiMAX_NR_OF_TERMINALS - 1] OF DED.DEVICE_STATE; uiTerminalCount : UINT; uiIndex : UINT; // for each terminal check if it implements device diagnostics xQueryResult: BOOL; itfDevice : DED.IDevice2; xDiagAvailable: BOOL; eError: DED.ERROR; xEverythingOK: BOOL; END_VAR uiTerminalCount := 0; // start at the top of the device tree with the first EtherCAT coupler coupler := EtherCAT_Master.FirstChildNode; WHILE coupler <> 0 DO // for each coupler that is found start at the first terminal terminal := coupler.FirstChildNode; WHILE terminal <> 0 AND uiTerminalCount < uiMAX_NR_OF_TERMINALS - 1 DO // for each terminal that is found get the status through the device diagnosis interface xQueryResult := __QUERYINTERFACE(terminal, itfDevice); IF xQueryResult THEN aDeviceState[uiTerminalCount] := itfDevice.GetDeviceState(xDiagnosisInfoAvailable => xDiagAvailable, eError => eError); uiTerminalCount := uiTerminalCount + 1; END_IF terminal := terminal.NextSiblingNode; END_WHILE coupler := coupler.NextSiblingNode; END_WHILE uiIndex := 0; xEverythingOK := TRUE; WHILE uiIndex < uiTerminalCount DO IF aDeviceState[uiIndex] <> DED.DEVICE_STATE.RUNNING THEN xEverythingOK := FALSE; EXIT; END_IF uiIndex := uiIndex + 1; END_WHILE
Last updated: 2025-02-06
Post by astutoski on No Motion with SM3_RaspiStepper (GPIO 23/24 Show No Pulses)
CODESYS Forge
talk
(Post)
Hi everyone, I’m completely new to CODESYS and have been teaching myself. And i Want to control an Axis using SM3RaspiStepper. Following the example on the RaspiStepper home page, I set up an axis through a POU and tied the SMC_StartupDrive (Visu) template to my axis instance (sud). Unfortunately, the motor never moves and I don’t see any pulses on the PULSE pin (GPIO 23). Hardware -Raspberry Pi 4 B -Nema 17 stepper motor -A4988 stepper driver (EN pin permanently tied to GND) Software / Runtime -CODESYS 3.5 SP21 Patch 1 – Raspberry Pi runtime (demo) -SoftMotion in demo mode -Package: SM3_RaspiStepper 0.0.0.6 Axis parameters: Pulse pin GPIO 23 Direction pin GPIO 24 Enable pin 0 (unused) Disable pin 0 (unused) Whether I start the axis from the visualization template or through Online Config Mode, the motor never spins. In Online Config Mode I press Power → the state changes from Standstill to Discrete_Motion, but the motor shaft is still locked and no step pulses appear on GPIO 23 (checked with a scope). I can provide screenshots of the Visualization, PLC logs, or wiring pictures if that helps. Any ideas on what I might be missing? Happy to provide screenshots, project files, or scope captures if that helps. Thanks in advance!
Last updated: 2025-06-25
Post by gseidel on AXIS_REF_SM3 Error Codes?
CODESYS Forge
talk
(Post)
Hi SLUCodesys, dwErrorId is a drive specific error number. The drive documentation should be consulted to interpret it. (Note that you should use MC_ReadAxisError to read this error, see https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/POUs/Diagnostics/MC_ReadAxisError.html. Accessing the internal variable will result in outdated values if the acis error is not mapped by PDO and is not recommended in general.) uiDriveInterfaceError holds errors of the SoftMotion driver for the drive. It is also an internal variable, not intended for direct access. It is intended for logging, the PLC log will contain the drive interface error, consisting of this number and an error text. My recommendation for handling axis errors in the CODESYS application: 1) Use MC_ReadStatus on the axis to find out whether it is in state Errorstop 2) If in Errorstop, there are two possibilities: an error reported by the drive (MC_ReadAxisError) or an error of the SoftMotion function blocks (output MC_ReadStatus.FBErrorOccured). 3) If there is no drive error, you can use SMC_ReadFBError https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/POUs/Diagnostics/FBError/SMC_ReadFBError.html Best regards, Georg
Last updated: 2025-09-24
Post by alexgooi on Licensing info not available.
CODESYS Forge
talk
(Post)
Sorry for the question, but I'm not completely getting the idea here, could you be more specific, maybe give an example? I'm now in a state where I don't have a softcontainer on my license server anymore (even after reinstalling from the Codesys-IDE). I tried reaching the webserver of Codemeter but when I do that I get redirected to http://"IP":22352 This is not reachable, afterwards I installed lynx on my Debian machine (command line only). From here I could reach the webserver and toggle the network server setting, but unfortunately this did not help. I also tried to changed the remote read setting to 1 (in the Server.ini file). But after a Codemeter reboot this is overwritten to 0. I have the feeling that it should be much easier to get a license to work, am I missing some checkbox somewhere? Is there a tutorial (or manual) that explains the licensing sequence step by step, because I'm pretty stuck.
Last updated: 2025-10-01
Post by nicetuxedo on Can not activate license on Raspberry pi
CODESYS Forge
talk
(Post)
Hello everyone, I'm hoping for some assistance with a license activation issue: a software crash has left my license in a strange state. Here is the sequence of events: I purchased a new license for the Raspberry PI from the official CODESYS web store. I opened the CODESYS and started the online activation process using the ticket number I received. During the activation, the CODESYS software threw an exception and crashed. I was not able to see if the activation completed. After restarting CODESYS, I attempted to run the activation process again with the same ticket number. The License Manager now gives me an error stating that the ticket has already been activated/used. I am now stuck because my installation is not licensed, but the activation server believes my ticket has been consumed. Has anyone encountered this before? Is there a way to have the ticket status reset?
Last updated: 2025-10-08
Post by mavitia on Application based license problem - Modbus TCP
CODESYS Forge
talk
(Post)
I am running ubuntu on a raspberry pi, and installed an application based license Control Basic M on it, it runs a demo program fine, does not timeout etc. however, when I add a modbus TCP device, I start getting errors: <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="24">Online change denied. Application Application is in exception state!</Entry> <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="68">Download failed: Application=Application</Entry> <Entry severity="exception" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:41 PM" infoId="0">Application app=Application has invalid license metrics!</Entry> the modbus tcp slave runs, and the counter ticks up, however, when I call the variables on the %IX0.0 in my program, and try to upload the changes, I am getting the error messages which stop the program as far as I understand, the application based, M includes 2 fieldbus instances, but on the other side is fairly new, anything obvious I am missing out here?
Last updated: 2023-12-18
Post by vipul on Multicast udp
CODESYS Forge
talk
(Post)
Hi, Good afternoon can anybody help me with UDP Multicast code. I am not able to send or recieve data when code is dumped on linux device. Below is my code. Declaration: PROGRAM udp_multicast VAR oneTimeFlag :UINT :=0; state: INT:=0; driver: UDP.UDPDriver; //port : UDP.Port;//moved to GVL src_ipAddr_ud: UDINT; src_ipAddr_st:STRING := '192.168.127.155';//'192.168.1.155';//ipms ip address dst_ipAddr_ud:UDINT; group_ipAddr_st:STRING := '239.1.5.10'; //group_ipAddr_ud:UDINT; result: SysTypes.RTS_IEC_RESULT; //result of recieve function. bind: UDINT; //result of binding. resultCreate:SysTypes.RTS_IEC_RESULT;//result of port creation. timer:BLINK; temFlag :INT:= 0; post:INT :=0; checksumFunc:checksumXor; localStringBuf:STRING[500]; chksum:BYTE; dataBuffer:POINTER TO BYTE; checksumString:ARRAY[0..5] OF BYTE; recvSize:__XINT; errorCode:UDINT; joinGroupErrorCode:UDINT; END_VAR ************8 Implementation: IF oneTimeFlag <> 1 THEN oneTimeFlag:=1; resultCreate := driver.CreatePort(ADR(GVL.port)); src_ipAddr_ud := UDP.IPSTRING_TO_UDINT(sIPAddress:= src_ipAddr_st); GVL.group_ipAddr_ud := UDP.IPSTRING_TO_UDINT(sIpAddress:= group_ipAddr_st); GVL.port.IPAddress := src_ipAddr_ud; GVl.port.ReceivePort:= GVL.src_port;//port on which messages are expected. GVl.port.SendPort := GVL.dest_port; GVl.port.OperatingSystem := 0; //0- any system GVL.port.Socket :=3; //3- socket type is multicast bind := GVL.port.Bind(udiIPAddress:=src_ipAddr_ud,); GVl.port.JoinGroup(udiGroupAddress:= GVL.group_ipAddr_ud,udiInterfaceAddress:= src_ipAddr_ud,eLogCode=>joinGroupErrorCode); END_IF timer(ENABLE:=TRUE,TIMELOW:=T#100MS,TIMEHIGH:=T#100MS); IF timer.OUT = TRUE THEN GVL.port.Send(udiIPTo:=GVL.group_ipAddr_ud,GVL.dest_port,pbyData:=ADR(GVL.writeData),diDataSize:=SIZEOF(GVL.writeData)); ELSE SysMemSet(ADR(GVL.readData[0]),0,SIZEOF(GVL.readData)); result := GVl.port.Receive(ADR(GVL.readData),diDataSize:=SIZEOF(GVL.readData),udiIPFrom=>dst_ipAddr_ud,diRecvSize=>recvSize,eLogCode=>errorCode); SysMemMove(ADR(GVL.readDataBuf[0]),ADR(GVL.readData[0]),SIZEOF(GVL.readData)); END_IF post:=LEN(GVL.readDataBuf);
Last updated: 2024-01-14
Post by umdee on Error when monitoring LAD programs
CODESYS Forge
talk
(Post)
System Information from the computer being used: OS Name Microsoft Windows 11 Pro Version 10.0.22631 Build 22631 Other OS Description Not Available OS Manufacturer Microsoft Corporation System Manufacturer Dell Inc. System Model Latitude 5500 System Type x64-based PC System SKU 08B9 Processor Intel(R) Core(TM) i7-8665U CPU @ 1.90GHz, 2112 Mhz, 4 Core(s), 8 Logical Processor(s) BIOS Version/Date Dell Inc. 1.3.11, 6/11/2019 SMBIOS Version 3.2 Embedded Controller Version 255.255 BIOS Mode UEFI BaseBoard Manufacturer Dell Inc. BaseBoard Product 0M14W7 BaseBoard Version A00 Platform Role Mobile Secure Boot State On PCR7 Configuration Elevation Required to View Windows Directory C:\WINDOWS System Directory C:\WINDOWS\system32 Boot Device \Device\HarddiskVolume1 Locale United States Hardware Abstraction Layer Version = "10.0.22621.2506" User Name CARDASSIA-IX\Engineer Time Zone Eastern Daylight Time Installed Physical Memory (RAM) 16.0 GB Total Physical Memory 15.8 GB Available Physical Memory 4.67 GB Total Virtual Memory 18.5 GB Available Virtual Memory 2.52 GB Page File Space 2.63 GB Page File C:\pagefile.sys Kernel DMA Protection Off Virtualization-based security Not enabled Windows Defender Application Control policy Enforced Windows Defender Application Control user mode policy Off Device Encryption Support Elevation Required to View Hyper-V - VM Monitor Mode Extensions Yes Hyper-V - Second Level Address Translation Extensions Yes Hyper-V - Virtualization Enabled in Firmware Yes Hyper-V - Data Execution Protection Yes
Last updated: 2024-03-19
Post by salvadegianluca on How to use TON inside an FB that is instanced within a Visu page
CODESYS Forge
talk
(Post)
Hi everyone; I'm building a project in which the drag of the mouse over some controls (or the click event) changes the background color of the control items; this change of color is made with an FB that assignes a color code to the background with MUX command based on the value of an enumerator, this part is perfectly working but, when I'm using a touchpanel instead of a web visu (controlled by a mouse) I get into some issues as it seems that the touch operations are not triggering the MouseEnter and MouseLeave properties as it's done with the mouse.... For this reason I'm trying to add a TON to my FB and, if the enum that changes color remains at the same state for more then 3s I'm automatically resetting it to it's "0" so the item gets back the not selected color. Anyhow it looks like the TON function from library is not working in these FB that are instanced in the various visualizations, as instead they do if I create some instances within the POUS. Anyone has ideas of how to make them work?
Last updated: 2024-04-15
Post by salvadegianluca on How to use TON inside an FB that is instanced within a Visu page
CODESYS Forge
talk
(Post)
Hi everyone; I'm building a project in which the drag of the mouse over some controls (or the click event) changes the background color of the control items; this change of color is made with an FB that assignes a color code to the background with MUX command based on the value of an enumerator, this part is perfectly working but, when I'm using a touchpanel instead of a web visu (controlled by a mouse) I get into some issues as it seems that the touch operations are not triggering the MouseEnter and MouseLeave properties as it's done with the mouse.... For this reason I'm trying to add a TON to my FB and, if the enum that changes color remains at the same state for more then 3s I'm automatically resetting it to it's "0" so the item gets back the not selected color. Anyhow it looks like the TON function from library is not working in these FB that are instanced in the various visualizations, as instead they do if I create some instances within the POUS. Anyone has ideas of how to make them work?
Last updated: 2024-04-15
Post by bertus on Can't get SMC_SmoothPath to work
CODESYS Forge
talk
(Post)
Hi Georg, thanks for your time. What is the value of D_ANGLE_TOL? It is set to 0.01. Do you need the assignment bAbort := NOT bDecoder? Does it help to leave it out? This seems to make no difference. Any errors (e.g. SMC_SmoothPath.Error/ErrorID) or PLC log messages? No errors or log messages. What if you comment out SMC_SmoothMerge and SMC_LimtiDynamics, is corner smoothing still not working? Indeed. Is bDecode written from a different task (e.g. visu)? Then I would recommend to assign to a local variable (bDecodeLocal := bDecode) and use that for all FBs. Otherwise, FBs might see different values of bDecode in a single cycle, which will cause problems. It is a local variable, written from a state machine inside this program. But there is new information: During some trial and error, I tried skipping "stage 2: merge short linear segments" (SMC_SmoothMerge). And suddenly it rounds the corners, see attached image. Looking a bit closer, I noticed that (with the original program) after a download (cold start?), it in fact did round the corners, but only once. Ever next cycle in which the NC program was executed, the corners where not rounded. Not sure if there is any relation, but SMC_SmoothMerge is also the only FB which has no bAbort input. Perhaps I need to reset it (or any buffers) by other means?
Last updated: 7 days ago
Post by ryandmg on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
Thanks So Much for the reply! Were using the Weidmuller UV66-ADV-10-CAP-W The HMI is pointed to the URL which is assigned through u-OS. Basically when you log into the controller's webserver via browser you can view the installed apps. One of which is the Codesys runtime. When you click on that it takes you to the visualization. That corresponding url is what the HMI is looking for. I apologize I don't have that on hand as I'm in the office right now. I don't think I tried connecting using the port you mentioned and https in lieu of the u_OS URL. I can certainly try. Out of the box the u-OS is set for HTTP. Since we're isolated I havent changed that yet. When this has happened while logged on via chrome on my laptop, simply refreshing brings the visualization right back. In the case of the HMI in kiosk mode, we power cycle the HMI to force a reconnect, log back in u-OS and the visualization is back.
Last updated: 2023-09-06
Post by ryusoup on JSONByteArrayWriter problem?
CODESYS Forge
talk
(Post)
Hello, I am trying to implement a FB to make JSON formatted WSTRING type message using JSON Utilities 1.9.0.0 included in the IIoT library. In my case, I want to set some objects or arrays and set values to them later. But when I wrote as the sample below, // init builder builder(pJsonData:=pJsonData, diRootObj=>diRootObj); // set the 1st key to root diKey1 := builder.SetKeyWithArray(wsKey:="key1", diParentIndex:=diRootObj, eError=>eError); // set a value to the 1st key wsValue:="value01"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey1, eError=>eError); // set the 2nd key to root diKey2 := builder.SetKeyWithArray(wsKey:="key2", diParentIndex:=diRootObj, eError=>eError); // set a value to the 2nd key wsValue:="value02"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey2, eError=>eError); // set a value to the 1st key again wsValue:="value03"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey1, eError=>eError); // set a value to the 2nd key again wsValue:="value04"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey2, eError=>eError); // write build result writer(xExecute:=TRUE, pwData:=ADR(wsResult), udiSize:=SIZEOF(wsResult), xAsyncMode:=FALSE, jsonData:=pJsonData^); the result was: { "key1": ["value01"], "key2": ["value02", "value03", "value04"] } while my expection was: { "key1": ["value01", "value03"], "key2": ["value02", "value04"] } Inspecting pJsonData^, JSONData itself seems to be ok, so I believe the issue is something caused by the writer FB. Does anyone know how to fix it? Thanks,
Last updated: 2023-10-04
Post by mondinmr on Jitter problems on imx8
CODESYS Forge
talk
(Post)
We are experiencing serious jitter issues on an ARM64 imx8. Until now, on rpi and beaglebone derivatives, and on Intel, we never encountered jitter issues unless they were already present on the device. In this case, as can be seen from the attached graph, we have excellent maximum latency. The cyclictest on the isolated core dedicated to IEC CODESYS tasks shows a latency of 37µs, with an average of 14µs. Usually, on all other devices, with an RT kernel, with the appropriate parameters to avoid frequency throttling, with properly managed IRQs, and with the disabling of large page sizes, the jitter measured by CODESYS is very close to the cyclictest latency. However, on this imx8, we are noticing a fluctuating value of +/- 300µs that seems to be added to this latency, as if something occasionally miscalculates the sleep times by exactly +/- 300µs. Two screenshoot attached. - Result of cyclictest - Jitter on CODESYS Tasks are assigned to isolated core!
Last updated: 2023-10-18
Post by janber0206 on Gateway doesn't come online, regarding a working internet connection
CODESYS Forge
talk
(Post)
Solved EN: The Problem is that the Codesys Edge-Gateways have a License with a runtime of an half year, as long the Gateways are online they will self renew themselfs. In my Case the RevPi was more than a year offline and so the Edge-Gateway was not working anymore. The solution: I accessed a laptop that was directly connected to the RevPi. I installed the Codesys service tool and renewed the certificate manual. DE: Das Propblem ist das die Codesys Edge-Gatways eine Lizenz haben die nur ein halbes Jahr gültig ist. Solange das Gateway eine Internet verbindung hat aktualisiert sich das Zertifikat von alleine. In meinem Fall war das Gateway aber über ein Jahr offline und hat somit nicht mehr funktioniert. Die Lösung: Ich hab auf einen Laptop von Kunden mit TeamViewer zugegriffen, der Laptop wurde mit Kabel direkt mit RevPi verbunden. Codesys Service Tool installiert und dann das Gatewayzertifikat aktualisiert.
Last updated: 2023-10-26
Post by riccardo on VisuElems.CurrentUserGroupId is not stable
CODESYS Forge
talk
(Post)
GoodMorning everyone. I have a system that, in case of alarm, have to block. When the operator logs in must have to acknoledge the alarm and should operate in the system freely. To perform this I detect the logged User by (VisuElems.CurrentUserGroupID <> 0) with a similar code to the the following: PROGRAM AlarmMngt VAR alarm : BOOL:= FALSE; Ack : BOOL:= TRUE; PushBottonOpening : BOOL:= FALSE; Valve : BOOL := FALSE; Flag: BOOL := FALSE; END_VAR IF alarm AND Ack AND (NOT Flag) THEN valve := FALSE; PushBottonOpening := FALSE; Ack := FALSE flag := TRUE; ELSIF (NOT alarm) AND Ack THEN flag := FALSE; END_IF (* if the system is in alarm but there is a logged operator that acknowledge the alarm the system allows the valve opening.*) IF (VisuElems.CurrentUserGroupID <> 0) AND Ack AND Alarm AND PushBottonOpening THEN Valve := TRUE; ELSIF (VisuElems.CurrentUserGroupID = 0) AND Alarm THEN valve := FALSE; END_IF The problem I have is in the last 5 lines of the code: Even if there is a logged in user, the GroupID variable is subjected to a refresh that cyclically set for an instant it to 0 and this close the valve making difficult to the user to work Now I solved it creating a time hysteresys cycle but it is not a good solution. Someone is able to explane me why the GroupID variable is sobjected to this refresh and how to stabilize to avoiding it? Thank you in advance, Riccardo
Last updated: 2023-11-10
Post by grant32 on RAMP_REAL FB is retaining my output value when i try to re use the FB
CODESYS Forge
talk
(Post)
Hello, I'm relatively new to PLC programming. I am trying to creat a ramp down function, I have an example here of what I am using. I can get the function to work, the issue is that the OUT (variable3) value is being held by the FB so after I use it once it no longer works. In this example i set variable3 to 100 and the rest is as seen, over the course of a minute it ramped down to 10 (as desired). But when I deenergize TEST_START, set variable3 back to 100, and then re-energize TEST_START it immediately jumps back to the previously held value 10. The reset on this block just pauses the function and holds the last OUT. In my case I will need the function to start OUT at a set value, ramp down to the IN (variable2) value, and then accept a new OUT value to ramp down next time the block is energized. Hopefully this made sense, if anyone has any advice that would be awesome!
Last updated: 2024-07-29
Post by mondinmr on First IO address of a CAADiagDeviceDefault.
CODESYS Forge
talk
(Post)
I have a device CAADiagDeviceDefault: IoConfig_Globals.Axis_A In our library, we perform introspection of the Etc_SlaveDiag. In that case, we have connectors, and by searching for them by address, I can find them in the IO mapping using the offset and size provided by EtherCAT. However, a Lenze i700 drive, instead of placing the IO mapping in the Etc_SlaveDiag device, places it in a sub-device CAADiagDeviceDefault. So, when I perform introspection, I cannot find the IO correspondences. Yet, in the CAADiagDeviceDefault, I do not find the connectors and cannot do the matching. Is there a way with a pointer or reference to a CAADiagDeviceDefault to obtain the address of the first input and the address of the first output? This is because we have our own motion library with many EtherCAT devices that automatically configure the mappings, but I can't manage to do so with the Lenze i700.
Last updated: 2024-08-22
Post by rossanoparis on Clarifications regarding the appropriate runtime system to use
CODESYS Forge
talk
(Post)
Thank you @TimvH It is clear that licences are application based and now thanks to your reply I could understand the meaning of RT systems. The RT called "CODESYS Control for Linux ARM SL" can be deployed on a generic debian based ARM system. The RT called "CODESYS Control for Raspberry Pi MC SL" is more specific for Rasberry HW. Did I understand correctly? Regarding the RT called "CODESYS Virtual Control SL" despite its description it is not clear to me when to use it. It seems that a project created using such RT system can be deployed on any HW. It sound good obviously, as it means that it is possible to realize a completely abstract project from its hardware. The only limit could be represented by the need of using a specific HW or OS feature, in that case a more specific RT system should be chosen. Is my last consideration correct? Regards Rossano
Last updated: 2024-09-26
Post by andrax on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
Hi, Communication with the ADS1115 is actually simple. 1. write config 2. write address pointer 3. read conversation register The ADS1115 works like a multiplexer. This means that you do this individually for each channel that you want to read. e.g: Channel 1: write config > write address pointer > read conversation register Channel 2: write config > write address pointer > read conversation register Channel 3: write config > write address pointer > read conversation register Channel 4: write config > write address pointer > read conversation register then you start again from the beginning You can also omit individual channels or read only one. It doesn't matter. I have written the driver so that I can also use it on the TCA9548. The driver is from Stefan Dreyer. In your case, the driver works and communication with the ADS1115 is running. As you can see, the cfgWrong:=FALSE If you could not write or read data, cfgWrong:=TRUE; This means that either something is wrong with your ADS1115 or you have connected something incorrectly. Question: what voltage do you want to measure?
Last updated: 2024-11-08
Post by struccc on Bibliothek: floatingpointutils
CODESYS Forge
talk
(Post)
The issue s the byte order typically in this case. Can be especially problematic with floating point numbers - even more tricky if transferred with a word based protocol. It is a peasant way to try out the alternatives, dword order can be a-b-c-d, b-a-d-c, c-d-a-b, d-c-b-a where a is the most significant, d is the least significant byte. So all you need is to swap the bytes in your dword, until you get the expected result. If you don't want to mess writing code for this, I'd recommend CAA_Memory library for that: MEM.ReverseBYTEsInDWORD and MEM.ReverseWORDsInDWORD functions would definitively do the trick. Otherwise, can do like this: VAR dwIn : DWORD := 16#11223344; dwOut : DWORD; rOut : REAL; pIN : POINTER TO BYTE; pOUT : POINTER TO BYTE; END_VAR pIN := ADR(dwIn); //pOUt := ADR(dwOut); pOUt := ADR(rOut); pOut[0] := pIN[3]; pOut[1] := pIN[2]; pOut[2] := pIN[1]; pOut[3] := pIN[0]; Ugly, but does the job...
Last updated: 2024-11-19
Post by dom4u on Using PEAK CAN PCIe card (IPEH-004040) with Codesys Control RTE V3
CODESYS Forge
talk
(Post)
Some findings on this issue: PEAK CAN Driver is the same as in every PCI card from PEAK. I updated the inf file. Here are my steps: 1. Include right VendorID into the *.inf file 2. Disable Windows driver check (Disable WHQL check). This you need because 3S driver is not certified. You will find steps via google or ask chatgpt :) 3. Select: Select driver from a list and navigate to the folder. Say yes to install an uncertified driver. 4. Driver installed and device without errors I did the same with CAN Card from ESD, but here you dont need to include the vendor ID. In ANY CASE it was not successful. The RTIOwdmgeneric is not available in Codesys or anyhow accassable :( I wonder that it fails in two cases, two suppliers, two driver in the same way. How can RTIOwdmgeneric implemented into the project?
Last updated: 2024-12-20
Post by george32 on TCP Server
CODESYS Forge
talk
(Post)
Thank you for your advice Rinie, I have tried to follow this example but found one problem.When I disconnect with Hercules the system does not acknowledge the lost of its connection this could result in critical errors. Because of this error I am trying to implement the Syssocket library. With this library I am having a problem which I could not solve. I have the following code: ip_adres : STRING :='0.0.0.0'; port : WORD := 5000; iStep : INT := 1; // Socket information Socket_handler : SysSocket_Interfaces.RTS_IEC_HANDLE; Socket_handler_result : SysSocket_Interfaces.RTS_IEC_RESULT; Socket_adress : SysSocket_Interfaces.SOCKADDRESS; Addres_Convert : SysSocket_Implementation.RTS_IEC_RESULT; // Bind information Bind_handler : SysSocket_Interfaces.RTS_IEC_RESULT; // Listener Information Listener_handler : SysSocket_Interfaces.RTS_IEC_RESULT; Addres_Convert := SysSocket_Implementation.SysSockInetAddr(szIPAddress:= ip_adres,pInAddr:= ADR(Socket_adress.sin_addr)); Socket_adress.sin_family:= SysSocket_Interfaces.SOCKET_AF_INET; Socket_adress.sin_port := SysSocket_Implementation.SysSockHtons(usHost:= port); CASE iStep OF 1: // Create Socket Socket_handler :=SysSockCreate( iAddressFamily :=SysSocket_Interfaces.SOCKET_AF_INET, diType:=SysSocket_Interfaces.SOCKET_STREAM, diProtocol:=SysSocket_Interfaces.SOCKET_IPPROTO_TCP, pResult:=ADR(Socket_handler_result)); IF Socket_handler = SysSocket_Interfaces.RTS_INVALID_HANDLE THEN iStep := 1; ELSE iStep := 2; END_IF 2: Bind_handler := SysSocket_Implementation.SysSockBind( hSocket:=Socket_handler, pSockAddr :=ADR(Socket_adress), diSockAddrSize:=SIZEOF(Socket_adress) ); 3: Listener_handler := SysSocket_Implementation.SysSockListen( hSocket :=Socket_handler, diMaxConnections :=1); END_CASE When I am trying to get this working, the SysSockBind function gives a value of 16#207 which means adress already in use. I find this weird because of the IP-adress of 0.0.0.0. I think I am converting the Ip-adress in the wrong way, but the code does not give a error arround this. So therefore I cannot find the solution to this problem. I hope someone could help me with this problem. Thanks in advance George
Last updated: 2025-02-20