Post by squiggleypuff on Can't Add New Version of Modbus TCP Master
CODESYS Forge
talk
(Post)
I'm having a tough time trying to get Modbus working on a Festo CPX-E PLC; it throws these pre-compiler errors as soon as I add in my Modbus TCP Master 3.5.12.30 to my project: I'm confused about the C0046 error, as I have IODrvModbusTCP 4.3.0.0 Library installed. So I thought maybe I needed to use the newest Modbus TCP Master 4.3.0.0, which is in my device repository: However, whenever I go to add this underneath the Ethernet adapter (which is version 4.2.0.0), the only TCP Master version available is the old 3.5.12.30 one, even if I have Display all versions checked.: I even went so far as to delete the old version, but then there were no options to add a Modbus TCP Master under my Ethernet adapter. What needs to be done to use the newest Modbus TCP Master? Or are these pre-compiler errors unrelated and I'm missing something? Any help greatly appreciated.
Last updated: 2024-04-04
Post by fontrap on cmDongle Raspberry Pi issue
CODESYS Forge
talk
(Post)
Hello mates, I'm working with CODESYS V3.5 SP20 on a Raspberry Pi and I use "Raspberry Pi MC SL" as device on the project. I've installed the Control Standard L (multicore) license on a Wibu System usb-Dongle (cmStick/4.50) that already had another license from another vendor. I follow the online activation procedure from CODESYS documentation. Raspberry Pi has already CodeMeter installed for the other license. When I plugin the dongle on Raspberry and start the Runtime from Raspberry Pi Update in CODESYS I receive the message that I'm on Demo mode because the license is missing. I double checked that the license is activated in the dongle, through the WebAdmin of CodeMeter and the second license runs properly without any issue. I have already try to change the dongle from HID to MSD device and backward but the the Runtime cannot recognize the Dongle. I have also try to stop and start the Runtime through CODESYS without success. Is there anything else I can do to fix this issue?
Last updated: 2024-04-22
Post by jrsantab on Remote connection to ifm PLC & HMI
CODESYS Forge
talk
(Post)
We have finally solved the problem. The version of the Gateway in the computer that worked (3.5.11.0) and the one that didn't (3.5.17.30) was different. We have three different Codesys 3.5 versions installed because we work with different controllers. I believe that, depending on the sequence you follow to install the versions you get a different Gateway version. To solve the problem you first have to disable the "obsolete" services. Open services, serach for (in our case) CODESYS Gateway V3 Version 3.5.11.0 CODESYS ServiceControl Version 3.5.11.0 I stopped the services and changed to Manual Start. Then you have to create the new services. In our case, from a Command Prompt session (cmd): SC CREATE "Codesys GatewayService Rigual" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\GatewayService.exe" and then SC CREATE "CODESYS ServiceControl Version 3.5.17.30" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\CODESYSControlService.exe" remember also to set them as Automatic Start!
Last updated: 2024-04-22
Post by culius on JSON
CODESYS Forge
talk
(Post)
Hey guys, I am trying to write a JSON. First time after login in PLC after download everthing works. But when I want to change values during runtime and try to recreate the JSON nothing happens. When forcing the xStart as an impulse i want to recreate it and see 2 as Key3 instead of 1 from the first run. Any Idea how to make this work? PROGRAM test VAR factory : JSON.JSONDataFactory; eDataFactoryError : JSON.FBF.ERROR; pJsonData : POINTER TO JSON.JSONData := factory.Create(eError => eDataFactoryError); fb_JBuilder : JSON.JSONBuilder; wsValue : WSTRING; diRootIndex, diObject1Index : DINT; iValue : INT; jsonArrayWriter : JSON.JSONByteArrayWriter; wsJsonData : WSTRING(1000); xFirst : BOOL := TRUE; END_VAR IF xFirst THEN fb_JBuilder(pJsonData := pJsonData, diRootObj => diRootIndex); wsValue := "Value1"; fb_JBuilder.SetKeyWithValue("Key1", wsValue, diParentIndex := diRootIndex); diObject1Index := fb_JBuilder.SetKeyWithObject("Key2", diParentIndex := diRootIndex); iValue := iValue + 1 ; // -----------!!! secound run should increment key3!!!!------------ fb_JBuilder.SetKeyWithValue("Key3", iValue, diParentIndex := diObject1Index); xFirst := FALSE; END_IF jsonArrayWriter(xExecute := TRUE, pwData := ADR(wsJsonData), udiSize := SIZEOF(wsJsonData), jsonData := pJsonData^, xAsyncMode := FALSE); Kind Regards
Last updated: 2024-04-30
Post by tama00 on GPIOs not running with Raspberry Pi 4 (and SPI connection)
CODESYS Forge
talk
(Post)
Hello everyone, I have a working SPI connection (with transferExt) between a Raspberry master with Codesys and an ESP32 slave. I would also like to use a few GPIO pins. Is there a problem with using SPI AND GPIOs? Environment: Raspberry Pi 4+ with Raspian from Oct 23 Codesys V3.4 SP19 Patch 5 with Runtime Version 4.10.0.0 Device: GPIOs B+/Pi2 My problem: The status is displayed as “GPIOs : not running”. And also during mapping the message “The bus is not running. The values shown are perhaps not actual”. However, the variable changes that I make in my program are displayed under “Current Value”. In the Logic Analyzer, the pin toggles during transmission with small intervals of +-4us (seems to be a cyclical disorder, but I don't know where exactly it could be coming from). This applies to pins that I actually use (output) but also to the other GPIOs (not used). With GPIO 4, the line remains permanently high. Attached is a screenshot from the Logic Analyzer. Channel 1,3,5 were GPIO pin 26, 22, 17 Would be very grateful for help. Best regards
Last updated: 2024-05-06
Post by tortilla on J1939 connection between two devices
CODESYS Forge
talk
(Post)
Hey, I'm pretty new to CoDeSys so I don't know a lot of things yet. I have to create a connection between two devices (CANbus - J1939 connection). The idea for now is to send a message from one to another (one operates on 3.5 SP11 the other one on 2.3) I watched a few videos, worked with the documentation and worked with chatGPT 4o and was able to build the attached file. This part is about the device on 3.5.11: I'm using the J1939LocalECUDiag, TransmitParameterGroup, TransmissionTrigger Function blocks to send the message but my TransmitPG.xBusy / .xDone never turns to True and therefore my message is not sent while TransmitPG.xExcecute is True. I added the two devices in the CANbus in the J1939Manager and addapted the options like I've seen in the documentation. Can anyone explain what's wrong with my code in this casse or give me advices how to properly create a connection between my two devices? Thanks in advance!
Last updated: 2024-05-23
Post by caprez95 on Deleting the trend recording history
CODESYS Forge
talk
(Post)
Hallo Ich möchte eine laufende Trendaufzeichnung stoppen, den Inhalt löschen und Trend-Diagramm auf 0 zurücksetzen. Laut Codesys soll das mit dem folgenden Code möglich sein: You can insert an input element in the visualization which the operator can use to delete the previous value recording in the trend visualization at runtime. The curve displayed until then is removed and the display starts over. In the application (example: in the program PLC_PRG), implement the following code: itfTrendRecording : ITrendRecording; itfTrendStorageWriter : ITrendStorageWriter; itfTrendStorageWriter3 : ITrendStorageWriter3; sTrendRecordingName : STRING := 'TrendRecording'; itfTrendRecording := GlobalInstances.g_TrendRecordingManager.FindTrendRecording(ADR(sTrendRecordingName)); xClearHistoryTrend: BOOL; IF xClearHistoryTrend THEN itfTrendRecording := GlobalInstances.g_TrendRecordingManager.FindTrendRecording(ADR(sTrendRecordingName)); IF itfTrendRecording <> 0 THEN itfTrendStorageWriter := itfTrendRecording.GetTrendStorageWriter(); IF __QUERYINTERFACE(itfTrendStorageWriter, itfTrendStorageWriter3) THEN itfTrendStorageWriter3.ClearHistory(); END_IF END_IF In the visualization of the trend recording, add a button for deleting the previous curve. Configure its Toggle property with the variable PLC_PRG.xClearHistoryTrend. ⇒ When xClearHistoryTrend is set to TRUE, the previously recorded curve is deleted. The recording immediately starts again. Dies löscht auch die Daten vom Trend, aber das Diagramm wird nicht auf 0 zurückgesetzt, sondern läuft einfach da weiter wo man gestoppt hat. Braucht es für den Diagramm-Reset noch einen zusätzlichen Befehl? Gruss
Last updated: 2024-06-11
Post by brubingh on Download Missing Libraries not working
CODESYS Forge
talk
(Post)
We are working on a project and the customer required 3.5.16 BF4. After working on the project for a few weeks I opened it the next morning and it could not access libraries. IecVarAccess could not be accessed. I checked if windows updated - it did not. So no explanation for why it lost access other than that I shut down the computer for the night. Note that I am using a demo license. I still haven't figured out any reason to purchase a license. So I spent the next hour reinstalling CodeSys. Note that I did NOT uninstall first. After install I waited another 5 minutes for it to open the first time. I clicked File->Open to open the project. Previously I had selected File->Recent Projects - not sure if that makes and difference. But after this process it did open the project and compile it just fine. This is miserable. If this had happened when I went on site to a customer I would have lost hours of work doing the reinstall. Is there a different and quicker fix?
Last updated: 2024-06-13
Post by rmaas on Strange Behavior on Raspberry Pi
CODESYS Forge
talk
(Post)
Hello, what you are seeing is not strange behavior. The problem is that everyting is happening in the same program cycle. After the variable Stepnumber is changed from 10 to 20 for example then you want the program to wait with the next EQ until the next program cycle. Else every EQ will be be true because in every line the variable Stepnumber is increased. When the program arrives (still in the same cycle) at the line with the timer, the Stepnumber has been increased to 30 in the meantime and the timer will allway be ON because even though the variable is written to 10 in this line in the next cycle it starts with 10 and will be 30 again before reaching the timer in line 8. Not very good at explaining stuff but i hope you get the problem. See screenshot below for an example of one way you could solve this...
Last updated: 2024-06-18
Post by svenkaro on Codesyscontrol.service stoppt nach 30s
CODESYS Forge
talk
(Post)
Wie Du schon vermutet hast, es meint, die Hardware/Firmware sei nicht kompatibel ... ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-18, 0x00000BB8, 0xFFFFFFFB) Architecture: aarch64 Byte Order: Little Endian CPU(s): 4 On-line CPU(s) list: 0-3 Vendor ID: ARM Model name: Cortex-A72 Model: 3 Thread(s) per core: 1 Core(s) per cluster: 4 Socket(s): - Cluster(s): 1 Stepping: r0p3 CPU(s) scaling MHz: 40% CPU max MHz: 1500.0000 CPU min MHz: 600.0000 BogoMIPS: 108.00 Flags: fp asimd evtstrm crc32 cpuid Caches (sum of all): L1d: 128 KiB (4 instances) L1i: 192 KiB (4 instances) L2: 1 MiB (1 instance) Vulnerabilities: Gather data sampling: Not affected Itlb multihit: Not affected L1tf: Not affected Mds: Not affected Meltdown: Not affected Mmio stale data: Not affected Retbleed: Not affected Spec rstack overflow: Not affected Spec store bypass: Vulnerable Spectre v1: Mitigation; __user pointer sanitization Spectre v2: Vulnerable Srbds: Not affected Tsx async abort: Not affected Allerdings habe ich schon reichlich Firmware versionen getestet.
Last updated: 2024-06-21
Post by timvh on Toradex and CODESYS and licensing
CODESYS Forge
talk
(Post)
For the Virtual Control you need to use a "Network license". The Virtual Control has parameters of which one is the reference to the license server. This can be the device itself, but you need to activate the license on the host system (not in the container). For this, CODESYS has a Network License server with WBM (web based management). See for the Network License configuration: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_license_controller_linux.html If it is only for evaluation, I would advise to use a CODESYS (USB) key and activate the license on the key. Then you still have to install the CODESYS Network License server on the host, but you don't have to activate the license as soft license on the device. The benefit is that you can easily move your license to another device when needed. Off course your device must have a free USB port available to be able to do this.
Last updated: 2025-10-20
Post by valenting on License problem with Raspberry Pi
CODESYS Forge
talk
(Post)
Hello, I have a raspberry pi with a license installed, but Codesys stops after 2 hours, and when I start it manually I have the following message: pszInfo=!!!! no runtime license - running in demo mode(~2 hours) I tried using License Manager, and got the following message: Licensing info not available. There is no dongle attached to the device. I have this message frequently, and usually removing the content of /var/opt/codesys/.cmact_license makes it work. After doing it and restarting Codesys, I have an empty Softcontainer without my License. I tried using "Install license" using the .WibuCmRau file for the corresponding license and got the following message: Licensing info not available. The device does not support this service. I also tried using Additional Functions > Restore Licenses with the Ticket ID and got the following message: This device does not support automatic license backup. How can I reinstall the license to this Raspberry Pi?
Last updated: 2025-11-28
Post by rk-gaw on Unhandled exception and refactoring error
CODESYS Forge
talk
(Post)
Hello everyone. I hope this is the right place to ask for help, this error is causing me a great amount of time loss and I really would like to end this nightmare. I don't know why but at times if I try to Browse -> Display Cross Reference on a variable Codesys just crashes. I'll attach the file with the complete crash report hoping someone can figure why it happend. I think that the unhandled exception comes from the PersisranceManager Module and is connected with the other big problem I'm facing: I cannot refactor in my project, if I'll try to refactor a POU name the whole POU will become "frozen", it's like its desynchronizing from the project and the project cannot find the pointer to the POU once I refactor it. And when I open the project a warning pop-up will show up with the frozen POUs name, but I cannot figure out what the warning is telling me. I'll attach every warning and error pop up the project is showing me, and thanks in advance to anyone who can figure something out.
Last updated: 2025-12-10
Post by baott569 on CODESYS OPC UA Security: HMI Client Not Receiving Server Certificate
CODESYS Forge
talk
(Post)
Hello everyone, I am currently using OPC UA in CODESYS with the security mode BASIC256SHA256 – Signed and Encrypted. The OPC UA Server is running on an RTE CX device, and the HMI is running on another computer. I have reviewed many CODESYS documents and successfully established communication when the security mode is set to None with Anonymous login. However, when security is enabled, the server does not provide its certificate for the CODESYS HMI client to trust. Interestingly, the client can send its certificate to the server, and UAExpert works normally, but the CODESYS HMI client does not receive the server certificate. Can anyone help clarify what I might be missing? I have been stuck on this issue for three days. If I missed or misconfigured any step, please let me know. I believe I am stuck at step 15 in the following CODESYS guide: Encrypting the Communication of a Data Source OPC UA Client https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_encrypt_communication_data_sources_opc_ua_client.html Thank you very much.
Last updated: 2026-01-06
Post by baott569 on CODESYS OPC UA Security: HMI Client Not Receiving Server Certificate
CODESYS Forge
talk
(Post)
Hello everyone, I am currently using OPC UA in CODESYS with the security mode BASIC256SHA256 – Signed and Encrypted. The OPC UA Server is running on an RTE CX device, and the HMI is running on another computer. I have reviewed many CODESYS documents and successfully established communication when the security mode is set to None with Anonymous login. However, when security is enabled, the server does not provide its certificate for the CODESYS HMI client to trust. Interestingly, the client can send its certificate to the server, and UAExpert works normally, but the CODESYS HMI client does not receive the server certificate. Can anyone help clarify what I might be missing? I have been stuck on this issue for three days. If I missed or misconfigured any step, please let me know. I believe I am stuck at step 15 in the following CODESYS guide: Encrypting the Communication of a Data Source OPC UA Client https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_encrypt_communication_data_sources_opc_ua_client.html Thank you very much.
Last updated: 2026-01-06
Post by mrkm-dic on CODESYS: Combining Master Redundancy with EtherCAT Ring Topology – Is it Supported?
CODESYS Forge
talk
(Post)
Hello, I would like to ask whether it is technically supported (and practically achievable) to combine CODESYS Master Redundancy with EtherCAT ring (loop) redundancy in the same system. System setup CODESYS version: CODESYS 3.5.21.40 CODESYS Control SL for Weidmuller u-OS-4.12.2.0 Controllers (Masters): Weidmuller UC20-M4000 ×2, configured as Active / Standby using CODESYS redundancy EtherCAT Slaves: Weidmuller UR20-FBC-EC ×3, supporting EtherCAT ring / line break detection Topology: EtherCAT ring (loop) Main question Is it officially supported to use: ・CODESYS PLC/Master redundancy (Active/Standby) and ・EtherCAT ring topology (for cable redundancy) at the same time? Expected behavior Our expectation is: ・When the Active PLC fails, the Standby PLC becomes Active ・The Standby PLC then takes over the role of EtherCAT Master ・EtherCAT communication is re-established ・I/O control continues after reinitialization (a short interruption is acceptable; no strict bumpless requirement) We do not expect completely seamless / zero-cycle switchover, but we want to understand: ・Whether this combination is supported by design ・Or whether there are known limitations or restrictions when EtherCAT ring mode is used together with Master redundancy Clarification At this stage, the question is mainly about feasibility and support, not about a specific error message yet. Any official guidance, limitations, or real-world experience would be greatly appreciated. Thank you in advance.
Last updated: 2026-02-05
Post by risele on Modbus connection via Qronox PCD3 M6893
CODESYS Forge
talk
(Post)
First, if you don't need to change conversion rules in runtime, take a look at "Unit conversion" module (Application -> add object -> UnitConversion). You can specify there biderectional conversion with different units, limits and so on. Second, since MODBUS don't have "real" types but only general 16-bit registers and Real is 32-bit, generally you need a byte-was conversion Real <> two Words. Note, that depending on the devices on both sides, there are two options: Real-> Word1, Word2 or Real-> Word2, Word1, where Word1 is minor register in Modbus register pair and Word2 is major. You can use simple union: TYPE u_Real : UNION rVal:REAL; wVal:ARRAY[0..1] OF WORD; dwVAL:DWORD; //same as previous, may be easier to specify the MB register END_UNION END_TYPE and convert it as following: VAR myUnion:u_Real; rValue_TO_SEND:REAL; rValue_TO_GET:REAL; END_VAR myUnion.rVal:=rValue_TO_SEND; rValue_TO_GET:=myUnion.rVal; Note, that WORD-order should be properly set in MODBUS registers, otherwise you will get strange values. This tool is helpful: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/ Alternative, you can use functions as REAL_TO_DW and DW_TO_REAL from OSCAT_BASIC, for example.
Last updated: 2026-02-19
Post by kunal-pinetics on USB Communication for IP Configuration & Application Update – STM32H Series PLC
CODESYS Forge
talk
(Post)
Hello everyone, I am currently working on a PLC device based on the STM32H series MCU, running CODESYS. At the moment, I can: Change the Ethernet IP address Update/download the PLC application via Ethernet without any issues. However, I would like to implement the same functionality over USB (or Serial via USB) instead of Ethernet. My goals are: Change the device’s Ethernet IP address via USB Download/update the PLC application via USB communication Possibly use USB as a service/programming interface The hardware platform is based on STM32H series, and I am looking for guidance on: Whether CODESYS supports USB device communication for runtime download If a custom USB CDC (Virtual COM Port) implementation is required Whether a specific CODESYS runtime configuration is needed If a bootloader approach is recommended for application updates via USB If anyone has experience implementing USB communication for runtime download or device configuration on an STM32-based PLC, I would really appreciate your guidance. Thank you in advance for your help.
Last updated: 2026-02-26
Post by taywinkel on Virtual Keyboard Support on Login Page
CODESYS Forge
talk
(Post)
I am in the process of getting a visualization to work with the codesys keyboard. I created a custom keyboard which works fantastic for all input fields in the main visualization. I created a user management for my runtime, which gave me the standard blue login page. The codesys keyboard does not show up when trying to enter the usernam or password. I have tried every setting: changing the keyboard back to the standard codesys keyboard, and changing various settings on the visualization manager with no success. I can only use a physical keyboard connected to the device to enter the password. I did try removing the keyboard to no success either. I even tried creating my own login page so I could guarantee the keyboard showed up. This ended in disaster as I could not figure out the very complicated VisuUserManagement and VisuUserManagementDialog library, and documentation is contradictory or lacking. I imagine that an on screen keyboard is essential for many people's projects when using touchscreen panels, so I am wondering what others are doing. I would rather not use an external virtual keyboard (external to codesys) because this causes its own complications (I am working on a linux build with high securities).
Last updated: 2026-03-22
Post by lukasz on Unresolved reference when trying to upload to Codesys Runtime V3
CODESYS Forge
talk
(Post)
Hello! I'm working with Codesys SP21 Patch 4. The project builds without any errors. When trying to upload my project to Codesys Runtime V3 x64 I get a lot of Unresolved Reference errors, all with FU- at the start and then -CLOSELAYER2, -GETBUSINFO, -GETFRAME etc. I also get a error pop-up that I should 'update device' in the project but it's not specified to which version or anything useful really.There's also not much to choose from. When I check Runtime version in the systray I get 3.5.21.40 and it's the same as I have set up in the project as the device. All information I get is that it should be clear from the errors but no useful information is provided in the errors. Do I need to install some library? I checked other posts and for different reference error and this was the answer. Thanks in advance!
Last updated: 2026-03-25
Post by derpaul on Official MQTT-Client: MAX_RECEIVE_BUFFER_SIZE_EXCEEDED
CODESYS Forge
talk
(Post)
Here is the output Codesyscontrol.log ;**************************************************************** ;<loggername>/tmp/codesyscontrol.log</loggername> ;<logoptions> ; <enable>1</enable> ; <type>normal</type> ; <timestamp>rtc</timestamp> ; <deactivatable>0</deactivatable> ; <dump>always</dump> ; <filter>0x0000000f<filter> ; <maxentries>1000</maxentries> ; <maxfiles>1</maxfiles> ; <maxfilesize>1000000</maxfilesize> ;</logoptions> ;<entries> ;Timestamp, CmpId, ClassId, ErrorId, InfoId, InfoText ;ClassId: LOG_INFO =1 ;ClassId: LOG_WARNING =2 ;ClassId: LOG_ERROR =4 ;ClassId: LOG_EXCEPTION =8 ;ClassId: LOG_DEBUG =16 ;ClassId: LOG_PRINTF =32 ;ClassId: LOG_COM =64 ;</entries> ;**************************************************************** 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <logoptions> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <bEnable>1</bEnable> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <type>normal</type> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <timestamp>rtc</timestamp> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <disableable>0</disableable> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <Filter>0x0000000f</Filter> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <MaxEntries>1000</MaxEntries> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <MaxFiles>1</MaxFiles> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, <MaxFileSize>1000000</MaxFileSize> 2023-09-12T21:11:41Z, 0x00000013, 1, 0, 0, </logoptions> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 4, CODESYS Control for PFC200 SL 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 4, OS=Linux, CPU=ARM, Arch=32Bit, Coding=C 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 6, <version>3.5.16.40</version> <builddate>Mar 2 2021</builddate> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 5, Copyright (c) 3S - Smart Software Solutions GmbH 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>CM</cmp>, <id>0x00000001</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>CmpMemPool</cmp>, <id>0x0000001e</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>CmpLog</cmp>, <id>0x00000013</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>CmpSettings</cmp>, <id>0x0000001a</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysFile</cmp>, <id>0x00000104</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysCom</cmp>, <id>0x00000100</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysCpuHandling</cmp>, <id>0x00000101</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysDir</cmp>, <id>0x0000011b</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysEthernet</cmp>, <id>0x0000011c</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysEvent</cmp>, <id>0x00000102</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysExcept</cmp>, <id>0x00000103</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysInternalLib</cmp>, <id>0x00000107</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysMem</cmp>, <id>0x00000108</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysModule</cmp>, <id>0x00000109</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysMsgQ</cmp>, <id>0x0000010a</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysMutex</cmp>, <id>0x0000013a</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysOut</cmp>, <id>0x0000010b</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysProcess</cmp>, <id>0x0000010e</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysSem</cmp>, <id>0x0000010f</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysSemCount</cmp>, <id>0x00000139</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysSemProcess</cmp>, <id>0x00000119</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysShm</cmp>, <id>0x00000110</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysSocket</cmp>, <id>0x00000111</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysTarget</cmp>, <id>0x00000112</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysTask</cmp>, <id>0x00000114</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysTime</cmp>, <id>0x00000115</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysTimeRtc</cmp>, <id>0x00000127</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, System: <cmp>SysTimer</cmp>, <id>0x00000116</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpAlarmManager</cmp>, <id>0x0000007c</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpApp</cmp>, <id>0x00000002</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpAppBP</cmp>, <id>0x00000073</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpAppForce</cmp>, <id>0x00000074</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpAsyncMgr</cmp>, <id>0x0000005f</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpBinTagUtil</cmp>, <id>0x00000004</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpBinTagUtilIec</cmp>, <id>0x0000005c</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpBitmapPool</cmp>, <id>0x00000050</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpBlkDrvTcp</cmp>, <id>0x00000030</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpBlkDrvUdp</cmp>, <id>0x00000007</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAAAsyncMan</cmp>, <id>0x00004007</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAABehaviourModel</cmp>, <id>0x00004015</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAACallback</cmp>, <id>0x00004001</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAACanL2</cmp>, <id>0x00004004</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAADTUtil</cmp>, <id>0x00004013</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAAFile</cmp>, <id>0x00004008</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAAMemBlockMan</cmp>, <id>0x00004003</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAANetBaseServices</cmp>, <id>0x00004018</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAARealTimeClock</cmp>, <id>0x00004014</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAASdoClient</cmp>, <id>0x00004011</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAASdoServer</cmp>, <id>0x00004017</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAASegBufferMan</cmp>, <id>0x00004019</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAASerialCom</cmp>, <id>0x00004012</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAAStorage</cmp>, <id>0x0000007e</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAATick</cmp>, <id>0x00004009</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAATickUtil</cmp>, <id>0x00004010</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAATimer</cmp>, <id>0x00004016</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCAATypes</cmp>, <id>0x00004006</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpChannelClient</cmp>, <id>0x00000008</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpChannelClientIec</cmp>, <id>0x0000005d</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpChannelMgr</cmp>, <id>0x00000009</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpChannelServer</cmp>, <id>0x0000000a</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCharDevice</cmp>, <id>0x00000300</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpChecksum</cmp>, <id>0x0000000b</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCodeMeter</cmp>, <id>0x0000007a</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCommunicationLib</cmp>, <id>0x0000000c</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCoreDump</cmp>, <id>0x00000083</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpCryptMD5</cmp>, <id>0x0000006a</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpDevice</cmp>, <id>0x0000000e</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpDynamicText</cmp>, <id>0x00000051</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpEL6751CanDrv</cmp>, <id>0x00005f0b</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpEventMgr</cmp>, <id>0x0000005b</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpFileTransfer</cmp>, <id>0x0000005e</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpIecStringUtils</cmp>, <id>0x0000007f</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpIecTask</cmp>, <id>0x00000011</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpIecVarAccess</cmp>, <id>0x00000060</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpIoDrvIec</cmp>, <id>0x0000005a</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpIoMgr</cmp>, <id>0x00000012</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpKbus</cmp>, <id>0x0000008a</id> <ver>4.0.1.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpKnxStack</cmp>, <id>0x0000004d</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpMonitor2</cmp>, <id>0x00000032</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceClient</cmp>, <id>0x00000015</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceClientIec</cmp>, <id>0x0000011d</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceServer</cmp>, <id>0x00000016</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAClient</cmp>, <id>0x00000096</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAProviderIecVarAccess</cmp>, <id>0x00000126</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAServer</cmp>, <id>0x00000124</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAStack</cmp>, <id>0x0000008d</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpOpenSSL</cmp>, <id>0x00000033</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpPfcx00</cmp>, <id>0x00000088</id> <ver>4.0.1.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpPlcShell</cmp>, <id>0x00000128</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpRedundancy</cmp>, <id>0x00000129</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpRedundancyConnectionIP</cmp>, <id>0x0000ff03</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpRetain</cmp>, <id>0x00000017</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpRouter</cmp>, <id>0x00000018</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpSchedule</cmp>, <id>0x00000019</id> <ver>3.5.16.30</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpSecureChannel</cmp>, <id>0x00000090</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpSecurityManager</cmp>, <id>0x0000008e</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpSessionInformation</cmp>, <id>0x00000097</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpSocketCanDrv</cmp>, <id>0x00005f0d</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpSrv</cmp>, <id>0x0000001c</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpTraceMgr</cmp>, <id>0x00000070</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpUserDBFile</cmp>, <id>0x00000098</id> <ver>3.5.16.20</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpUserGroupsDBFile</cmp>, <id>0x00000099</id> <ver>3.5.16.20</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpUserMgr</cmp>, <id>0x00000061</id> <ver>3.5.16.40</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpUserObjectsDBFile</cmp>, <id>0x0000009c</id> <ver>3.5.16.20</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpVisuHandler</cmp>, <id>0x00000054</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpVisuServer</cmp>, <id>0x00000057</id> <ver>3.5.16.10</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpWebServer</cmp>, <id>0x00000071</id> <ver>3.5.16.0</ver> 2023-09-12T21:11:41Z, 0x00000001, 1, 0, 10, <cmp>CmpWebServerHandlerV3</cmp>, <id>0x00000072</id> <ver>3.5.16.0</ver> 2023-09-12T21:12:16Z, 0x00000007, 1, 0, 6, Network interface: <ipaddress>192.168.1.17</ipaddress>, subnetmask <subnetmask>255.255.255.0</subnetmask> 2023-09-12T21:12:16Z, 0x00000018, 1, 0, 4, Network interface <interface>ether 4</interface> at router <instance>0</instance> registered 2023-09-12T21:12:16Z, 0x00000009, 1, 0, 2, Running as network server 2023-09-12T21:12:16Z, 0x00000009, 1, 0, 1, Running as network client 2023-09-12T21:12:16Z, 0x0000000a, 1, 0, 0, <NumOfChannels>4</NumOfChannels> channels available, each of the size <BufferSize>100000</BufferSize> Bytes 2023-09-12T21:12:16Z, 0x00000129, 1, 0, 0, Debug Messages not activated 2023-09-12T21:12:16Z, 0x0000ff03, 1, 0, 0, Read connection settings... 2023-09-12T21:12:16Z, 0x00000030, 1, 0, 6, Local network address: <ipaddress>192.168.1.17</ipaddress> 2023-09-12T21:12:16Z, 0x00000018, 1, 0, 4, Network interface <interface>BlkDrvTcp</interface> at router <instance>2</instance> registered 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, No certificate for the OPC UA server available. 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, Security policy allows plain text communication. Secure communication is deactivated. 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, ************************************************************** 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, OPC UA Server Started: 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, Hostname: PFC200, Port: 4840 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, URL: opc.tcp://PFC200:4840 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, Loopbackadapter activated. 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, All available networkadapters are used. 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, ************************************************************** 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, Provider CODESYS_DefaultProvider with Version 0x3051028 registerd at the OPC UA server. 2023-09-12T21:12:16Z, 0x00000124, 1, 0, 0, Provider CmpOPCUAProviderIecVarAccess with Version 0x3051028 registerd at the OPC UA server. 2023-09-12T21:12:17Z, 0x00000126, 1, 0, 0, Valid license found for OPC UA IecVarAccess provider. 2023-09-12T21:12:17Z, 0x00000002, 1, 0, 7, Retains matched to bootproject of application [<app>Application</app>] 2023-09-12T21:12:17Z, 0x00000002, 1, 0, 6, Bootproject of application [<app>Application</app>] loaded 2023-09-12T21:12:17Z, 0x00000018, 1, 0, 1, Setting router <instance>0</instance> address to <address>(0011)</address> 2023-09-12T21:12:17Z, 0x00000018, 1, 16, 8, Network interface for mainnet=<mainnet>ether 5</mainnet> not found 2023-09-12T21:12:17Z, 0x00000018, 1, 0, 1, Setting router <instance>1</instance> address to <address>(0000)</address> 2023-09-12T21:12:17Z, 0x00000018, 1, 0, 1, Setting router <instance>2</instance> address to <address>(2ddc:c0a8:0111)</address> 2023-09-12T21:12:17Z, 0x00000002, 1, 0, 10, Application [<app>Application</app>] started 2023-09-12T21:12:17Z, 0x00000001, 1, 0, 34, CODESYS Control ready 2023-09-12T21:13:37Z, 0x00000001, 1, 0, 0, runtime licensed 2023-09-12T21:17:17Z, 0x00000002, 1, 0, 2, Application [<app>Application</app>] loaded via [OnlineChange] 2023-09-13T01:38:17Z, 0x00000009, 1, 418, 0, Channel timeout (<curtime>16012264</curtime>, <lasttime>15982259</lasttime>) 2023-09-13T01:38:17Z, 0x00000009, 1, 418, 0, Closing connection to <address>0329:032e</address> 2023-09-23T14:46:00Z, 0x00000002, 1, 0, 2, Application [<app>Application</app>] loaded via [OnlineChange] 2023-09-23T14:48:57Z, 0x00000002, 1, 0, 2, Application [<app>Application</app>] loaded via [OnlineChange]
Last updated: 2023-09-27
Post by frank1001 on Codesys läuft nicht hoch
CODESYS Forge
talk
(Post)
Bin Neuling bei Codesys. Habe Codesys 64 Bit installiert (3.5.1) Nach dem Starten geht nur ein EIngabefenster auf mit folgenden Inhalt. Weiter passiert nichts. Was kann ich machen ? //////////////////////////////////////////////////////////// //////////////////////////////////////////////////////////// _/_/_/_/ _/_/_/_/ _/_/_/_/_/ _/_/_/_/_/_/ _/_/_/_/_/ _/_/ _/_/ _/_/_/_/_/ _/ _/_/_/_/_/_/ _/_/_/_/_/_/ _/_/_/_/_/_/ _/_/_/_/_/_/ _/_/_/_/_/_/ _/_/ _/_/ _/_/_/_/_/_/ _/_/_/ _/_/ _/_/ _/_/ _/_/ _/_/ _/_/ _/_/ _/_/ _/_/ _/_/ _/_/ _/_/_/_/_/ // // // // // //// //// //// //// /////// // // // // // // // // // // ///// ////// ////// ////// ////// ////// // ////// /// //// //// ///// ////// ///// // ///// _/ //////////////////////////////////////////////////////////// //////////////////////////////////////////////////////////// 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CM</cmp>, <id>0x00000001</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CmpMemPool</cmp>, <id>0x0000001e</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CmpLog</cmp>, <id>0x00000013</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CmpSettings</cmp>, <id>0x0000001a</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysFile</cmp>, <id>0x00000104</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CmpMemGC</cmp>, <id>0x0000001f</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysCom</cmp>, <id>0x00000100</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysCpuBreakpoints</cmp>, <id>0x00000305</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysCpuHandling</cmp>, <id>0x00000101</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysCrypto</cmp>, <id>0x00000141</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysDir</cmp>, <id>0x0000011b</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysEthernet</cmp>, <id>0x0000011c</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysEvent</cmp>, <id>0x00000102</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysExcept</cmp>, <id>0x00000103</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysFileStream</cmp>, <id>0x00000120</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysGraphicGDIPlus</cmp>, <id>0x0000012a</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysInt</cmp>, <id>0x00000106</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysInternalLib</cmp>, <id>0x00000107</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysMem</cmp>, <id>0x00000108</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysModule</cmp>, <id>0x00000109</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysMsgQ</cmp>, <id>0x0000010a</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysMutex</cmp>, <id>0x0000013a</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysNativeCommonControls</cmp>, <id>0x00000138</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysNativeControl</cmp>, <id>0x0000012f</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysOut</cmp>, <id>0x0000010b</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysPci</cmp>, <id>0x0000010c</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysPort</cmp>, <id>0x0000010d</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysProcess</cmp>, <id>0x0000010e</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysSem</cmp>, <id>0x0000010f</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysSemCount</cmp>, <id>0x00000139</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysSemProcess</cmp>, <id>0x00000119</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysShm</cmp>, <id>0x00000110</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysSocket</cmp>, <id>0x00000111</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTarget</cmp>, <id>0x00000112</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTask</cmp>, <id>0x00000114</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTime</cmp>, <id>0x00000115</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTimeRtc</cmp>, <id>0x00000127</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTimer</cmp>, <id>0x00000116</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysWindow</cmp>, <id>0x00000117</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysWindowFileDialog</cmp>, <id>0x0000011a</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System|Dynamic: <cmp>SysTargetSoftMotion</cmp>, <id>0x00000112</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System|Dynamic: <cmp>SysCpuMultiCore</cmp>, <id>0x0000013d</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System|Dynamic: <cmp>SysReadWriteLock</cmp>, <id>0x0000013e</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAlarmManager</cmp>, <id>0x0000007c</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpApp</cmp>, <id>0x00000002</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAppBP</cmp>, <id>0x00000073</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAppForce</cmp>, <id>0x00000074</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAsyncMgr</cmp>, <id>0x0000005f</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAuditLog</cmp>, <id>0x000000a1</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBinTagUtil</cmp>, <id>0x00000004</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBinTagUtilIec</cmp>, <id>0x0000005c</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBitmapPool</cmp>, <id>0x00000050</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBlkDrvCom</cmp>, <id>0x00000006</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBlkDrvShm</cmp>, <id>0x00000068</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBlkDrvTcp</cmp>, <id>0x00000030</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBlkDrvUdp</cmp>, <id>0x00000007</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAAAsyncMan</cmp>, <id>0x00004007</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAABehaviourModel</cmp>, <id>0x00004015</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAACallback</cmp>, <id>0x00004001</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAACanL2</cmp>, <id>0x00004004</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAADTUtil</cmp>, <id>0x00004013</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAAFile</cmp>, <id>0x00004008</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAAMemBlockMan</cmp>, <id>0x00004003</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAANetBaseServices</cmp>, <id>0x00004018</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAARealTimeClock</cmp>, <id>0x00004014</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAASdoClient</cmp>, <id>0x00004011</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAASdoServer</cmp>, <id>0x00004017</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAASegBufferMan</cmp>, <id>0x00004019</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAASerialCom</cmp>, <id>0x00004012</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAAStorage</cmp>, <id>0x0000007e</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAATick</cmp>, <id>0x00004009</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAATickUtil</cmp>, <id>0x00004010</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAATimer</cmp>, <id>0x00004016</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAATypes</cmp>, <id>0x00004006</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChannelClient</cmp>, <id>0x00000008</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChannelClientIec</cmp>, <id>0x0000005d</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChannelMgr</cmp>, <id>0x00000009</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChannelServer</cmp>, <id>0x0000000a</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChecksum</cmp>, <id>0x0000000b</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCodeMeter</cmp>, <id>0x0000007a</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCommunicationLib</cmp>, <id>0x0000000c</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCoreDump</cmp>, <id>0x00000083</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCryptMD5</cmp>, <id>0x0000006a</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpDevice</cmp>, <id>0x0000000e</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpDynamicText</cmp>, <id>0x00000051</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpEventMgr</cmp>, <id>0x0000005b</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpFileTransfer</cmp>, <id>0x0000005e</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIecStringUtils</cmp>, <id>0x0000007f</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIecTask</cmp>, <id>0x00000011</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIecVarAccess</cmp>, <id>0x00000060</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIoDrvC</cmp>, <id>0x00000066</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIoDrvIec</cmp>, <id>0x0000005a</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIoMgr</cmp>, <id>0x00000012</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIpc</cmp>, <id>0x0000001d</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpMonitor</cmp>, <id>0x00000014</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpMonitor2</cmp>, <id>0x00000032</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpNameServiceClient</cmp>, <id>0x00000015</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpNameServiceClientIec</cmp>, <id>0x0000011d</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpNameServiceServer</cmp>, <id>0x00000016</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpOPCUAClient</cmp>, <id>0x00000096</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpOPCUAProviderIecVarAccess</cmp>, <id>0x00000126</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpOPCUAServer</cmp>, <id>0x00000124</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpOPCUAStack</cmp>, <id>0x0000008d</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpObjectMgr</cmp>, <id>0x00000080</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpOpenSSL</cmp>, <id>0x00000033</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpPlcShell</cmp>, <id>0x00000128</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpRedundancy</cmp>, <id>0x00000129</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpRedundancyConnectionIP</cmp>, <id>0x0000ff03</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpRetain</cmp>, <id>0x00000017</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpRouter</cmp>, <id>0x00000018</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSchedule</cmp>, <id>0x00000019</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSecureChannel</cmp>, <id>0x00000090</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSecurityManager</cmp>, <id>0x0000008e</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSercos3Master</cmp>, <id>0x0000004c</id> <ver>3.1.2.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSessionInformation</cmp>, <id>0x00000097</id> <ver>3.5.19.20</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSrv</cmp>, <id>0x0000001c</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSupervisor</cmp>, <id>0x0000008f</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpTraceMgr</cmp>, <id>0x00000070</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpUserDBFile</cmp>, <id>0x00000098</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpUserGroupsDBFile</cmp>, <id>0x00000099</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpUserMgr</cmp>, <id>0x00000061</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpUserObjectsDBFile</cmp>, <id>0x0000009c</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpVisuClientControllerHost</cmp>, <id>0x00000132</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpVisuHandler</cmp>, <id>0x00000054</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpVisuServer</cmp>, <id>0x00000057</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpXMLParser</cmp>, <id>0x00000058</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= Dynamic: <cmp>CmpTargetVisuStub</cmp>, <id>0x00000053</id> <ver>3.5.19.0</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= Dynamic: <cmp>CmpWebServer</cmp>, <id>0x00000071</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.025Z: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= Dynamic: <cmp>CmpWebServerHandlerV3</cmp>, <id>0x00000072</id> <ver>3.5.19.10</ver> 2023-09-19T08:02:04.045Z: Cmp=SysCpuMultiCore, Class=1, Error=0, Info=4, pszInfo= MultiCore support: [activated], all cores are used 2023-09-19T08:02:04.045Z: Cmp=SysCpuMultiCore, Class=1, Error=0, Info=4, pszInfo= Number of available cores: 8 2023-09-19T08:02:04.076Z: Cmp=CmpBlkDrvUdp, Class=1, Error=0, Info=6, pszInfo= Network interface: <ipaddress>192.168.1.167</ipaddress>, subnetmask <subnetmask>255.255.255.0</subnetmask> 2023-09-19T08:02:04.076Z: Cmp=CmpRouter, Class=1, Error=0, Info=4, pszInfo= Network interface <interface>ether 0</interface> at router <instance>0</instance> registered 2023-09-19T08:02:04.076Z: Cmp=CmpBlkDrvUdp, Class=1, Error=0, Info=6, pszInfo= Network interface: <ipaddress>192.168.56.1</ipaddress>, subnetmask <subnetmask>255.255.255.0</subnetmask> 2023-09-19T08:02:04.076Z: Cmp=CmpRouter, Class=1, Error=0, Info=4, pszInfo= Network interface <interface>ether 3</interface> at router <instance>1</instance> registered 2023-09-19T08:02:04.076Z: Cmp=CmpChannelMgr, Class=1, Error=0, Info=2, pszInfo= Running as network server 2023-09-19T08:02:04.076Z: Cmp=CmpChannelMgr, Class=1, Error=0, Info=1, pszInfo= Running as network client 2023-09-19T08:02:04.077Z: Cmp=CmpChannelServer, Class=1, Error=0, Info=0, pszInfo= <numofchannels>4</numofchannels> channels available, each of the size <buffersize>100000</buffersize> Bytes 2023-09-19T08:02:04.265Z: Cmp=CmpRedundancy, Class=1, Error=0, Info=0, pszInfo= Debug Messages not activated 2023-09-19T08:02:04.266Z: Cmp=CmpRedundancyConnectionIP, Class=1, Error=0, Info=0, pszInfo= Read connection settings... 2023-09-19T08:02:05.456Z: Cmp=CmpRouter, Class=1, Error=0, Info=4, pszInfo= Network interface <interface>BlkDrvShm</interface> at router <instance>2</instance> registered 2023-09-19T08:02:05.456Z: Cmp=CmpBlkDrvShm, Class=1, Error=0, Info=9, pszInfo= Local address (BlkDrvShm) set to 1 2023-09-19T08:02:05.463Z: Cmp=CmpBlkDrvTcp, Class=1, Error=0, Info=6, pszInfo= Local network address: <ipaddress>192.168.56.1</ipaddress> 2023-09-19T08:02:05.464Z: Cmp=CmpRouter, Class=1, Error=0, Info=4, pszInfo= Network interface <interface>BlkDrvTcp</interface> at router <instance>3</instance> registered 2023-09-19T08:02:05.507Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= No certificate for the OPC UA server available. 2023-09-19T08:02:05.507Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= Security policy allows plain text communication. Secure communication is deactivated. 2023-09-19T08:02:05.508Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= ********** 2023-09-19T08:02:05.508Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= OPC UA Server Started: 2023-09-19T08:02:05.508Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= Hostname: SIEMENS, Port: 4840 2023-09-19T08:02:05.508Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= URL: opc.tcp://SIEMENS:4840 2023-09-19T08:02:05.508Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= Loopbackadapter activated. 2023-09-19T08:02:05.508Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= All available networkadapters are used. 2023-09-19T08:02:05.508Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= Multithreading activated. 7 workers used. 2023-09-19T08:02:05.508Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= ************ 2023-09-19T08:02:05.513Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= Provider 'CODESYS_DefaultProvider' (version 0x3051300) registered at the OPC UA server. 2023-09-19T08:02:05.522Z: Cmp=CM, Class=1, Error=0, Info=0, pszInfo= ========================================================================= 2023-09-19T08:02:05.522Z: Cmp=CM, Class=1, Error=0, Info=4, pszInfo= CODESYS SoftMotion Win V3 x64 2023-09-19T08:02:05.522Z: Cmp=CM, Class=1, Error=0, Info=4, pszInfo= OS=Windows, CPU=x86, Arch=64Bit, Coding=C 2023-09-19T08:02:05.522Z: Cmp=CM, Class=1, Error=0, Info=6, pszInfo= <version>3.5.19.20</version> <builddate>Aug 1 2023</builddate> 2023-09-19T08:02:05.522Z: Cmp=CM, Class=1, Error=0, Info=5, pszInfo= Copyright CODESYS Development GmbH 2023-09-19T08:02:05.522Z: Cmp=CM, Class=1, Error=0, Info=0, pszInfo= ========================================================================= 2023-09-19T08:02:05.529Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= Provider 'AddressSpaceFragment Provider' (version 0x3051314) registered at the OPC UA server. 2023-09-19T08:02:05.530Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= Provider 'OPC UA for IEC-61131-3' (version 0x3051314) registered at the OPC UA server. 2023-09-19T08:02:05.530Z: Cmp=CmpOPCUAServer, Class=1, Error=0, Info=0, pszInfo= Provider 'AlarmManager' (version 0x3051314) registered at the OPC UA server. 2023-09-19T08:02:05.606Z: Cmp=CmpRouter, Class=1, Error=0, Info=1, pszInfo= Setting router <instance>0</instance> address to (00a7) 2023-09-19T08:02:05.606Z: Cmp=CmpRouter, Class=1, Error=0, Info=1, pszInfo= Setting router <instance>1</instance> address to (0001) 2023-09-19T08:02:05.606Z: Cmp=CmpRouter, Class=1, Error=0, Info=1, pszInfo= Setting router <instance>2</instance> address to (0001) 2023-09-19T08:02:05.606Z: Cmp=CmpRouter, Class=1, Error=0, Info=1, pszInfo= Setting router <instance>3</instance> address to (2ddc:c0a8:3801) 2023-09-19T08:02:05.611Z: Cmp=CM, Class=1, Error=0, Info=34, pszInfo= CODESYS Control ready 2023-09-19T08:02:05.796Z: Cmp=CM, Class=2, Error=0, Info=0, pszInfo=!!!! no runtime license - running in demo mode(~2 hours)
Last updated: 2023-09-19
Post by darko7417 on When running as a service, CodesysControl doesn't write log files to the disk (and other CmpLog related issuess)
CODESYS Forge
talk
(Post)
I run CODESYS runtime as a service and use CmpLog (the LogAdd2 function) to log different events to a file. I have done this many times before on various projects and hardware, and it works fine. On this particular system, I have CODESYS 3.5.20.40 running on a Windows 11 PC. The CODESYSControlService autostarts (with Local System credentials, the default), and the application runs fine. However, the configuration file is not read (or at least not the one that should be, or not the CmpLog section), and log files are not written to the disk. I would be thankful if anyone knew why this is happening and how to fix it. A note to CODESYS people: you must provide more information on the codesys configuration file, CODESYSControlService.exe and other major components and system behaviour. You created the service and various features (i.e. logging), but haven't explained how they work, which, in my opinion, is below standard for industrial automation software. These are my observations: - When running as a service, the config file is not read (none of them), or at least the CmpLog section is not read. I checked the log using Codesys IDE, and the CmpLog parameters are not the ones I have set in any of the config files. Which CmpLog config values does the service use, and where does it read them from? I have no idea, but it's not the config files. Here are the codesys config files I located on the PC's disk: o C:\Program Files (x86)\CODESYS 3.5.20.40\GatewayPLC\CODESYSControl.cfg (only 2 lines in this config) o C:\Program Files (x86)\CODESYS 3.5.20.40\GatewayPLC\AppDataFiles\CODESYSControlWinV3\CODESYSControl.cfg o C:\Users\SRV\AppData\Roaming\CODESYS\CODESYSControlWinV3\C4DBB537\CODESYSControl.cfg o C:\Program Files (x86)\CODESYS 3.5.20.40\GatewayPLC\tempCFG\CODESYSControl.cfg - When I run codesys as an app (e.g. by clicking the icon), this config file is read C:\Users\SRV\AppData\Roaming\CODESYS\CODESYSControlWinV3\C4DBB537\CODESYSControl.cfg and log files are written ok. The icon target is "C:\Program Files (x86)\CODESYS 3.5.20.40\GatewayPLC\CODESYSControlService.exe" -d o the -d option, I think, starts a cmd-like window showing service debug output (the output shown in log in the IDE) o the -i option, again I think, means install the service - I tried adding -d to service start parameters in the registry, but it started only once and after that it refused to start. Knowing what -d does and which other options are available would be great (e.g. can I make the service read a different config file). - Syslog UDP logging works fine in any case. - These are my CmpLog parameters ~~~ [CmpLog] Logger.0.Name=PlcLog3 Logger.0.Filter=0xFFFFFFFF Logger.0.Enable=1 Logger.0.MaxEntries=10003 Logger.0.MaxFileSize=50003 Logger.0.MaxFiles=33 Logger.0.Backend.0.ClassId=0x0000010B ;sends logger messages to SysOut Logger.0.Backend.1.ClassId=0x00000104 ;writes logger messages in a file Logger.0.Backend.2.ClassId=0x00000135 ;sends logger messages as UDP syslog Logger.0.Type=0x314 ;Set the timestamp to RTC ~~~
Last updated: 2025-02-27
Post by francesco86 on Script python for write in a file Project information
CODESYS Forge
talk
(Post)
Dear all, My python script can read a Codesys project and save in file the different POU, but the problem is that I don't able to read the project info from the obj list. Following of this message there is my python script. Can you help my? Best regards Francesco # encoding:utf-8 # We enable the new python 3 print syntax from __future__ import print_function import os import shutil import time import sys from datetime import datetime print("--- Saving files in the project: ---") print("sys.argv: ", len(sys.argv), " elements:") for arg in sys.argv: print(" - ", arg) if (len(sys.argv)>1): folderExportName = sys.argv[1] print(" folderExportName: ", folderExportName) exportPath = sys.argv[2]+ sys.argv[3]+ "\\"+ sys.argv[1] print(" File path: ", exportPath) # git has_repo=False #save_folder=r'E:\Tmp\ControlPlugins\ControlPlugins\Export' save_folder = exportPath if not os.path.exists(save_folder): os.makedirs(save_folder) else: a=os.listdir(save_folder) for f in a: if not f.startswith("."): sub_path= os.path.join(save_folder,f) if os.path.isdir(sub_path): shutil.rmtree(sub_path) else: os.remove(sub_path) elif f==".git": has_repo=True info={} type_dist={ '792f2eb6-721e-4e64-ba20-bc98351056db':'pm', #property method '2db5746d-d284-4425-9f7f-2663a34b0ebc':'dut', #dut 'adb5cb65-8e1d-4a00-b70a-375ea27582f3':'lib', #lib manager 'f89f7675-27f1-46b3-8abb-b7da8e774ffd':'m', #method no ret '8ac092e5-3128-4e26-9e7e-11016c6684f2':'act', #action '6f9dac99-8de1-4efc-8465-68ac443b7d08':'pou', #pou '6654496c-404d-479a-aad2-8551054e5f1e':'itf', #interface '738bea1e-99bb-4f04-90bb-a7a567e74e3a':'', #folder 'ffbfa93a-b94d-45fc-a329-229860183b1d':'gvl', #global var '5a3b8626-d3e9-4f37-98b5-66420063d91e':'prop', #property '2bef0454-1bd3-412a-ac2c-af0f31dbc40f':'tl', #textlist '63784cbb-9ba0-45e6-9d69-babf3f040511':'gtl', #global textlist '225bfe47-7336-4dbc-9419-4105a7c831fa':'dev', #device 'ae1de277-a207-4a28-9efb-456c06bd52f3':'tc', #task configuration 'f8a58466-d7f6-439f-bbb8-d4600e41d099':'m', #method with ret '261bd6e6-249c-4232-bb6f-84c2fbeef430':'gvl', #gvl_Persistent '98a2708a-9b18-4f31-82ed-a1465b24fa2d':'task', #task '085afe48-c5d8-4ea5-ab0d-b35701fa6009':'progInfo'#project information }; def save(text,path,name,tp): if not tp: tp='' else: tp='.'+tp+'.txt' with open(os.path.join(path,name+tp),'w') as f: f.write(text.encode('utf-8')) def print_tree(treeobj, depth, path): global info #record current Path curpath=path isfolder=False t='' #text tp='' #type # get object name name = treeobj.get_name(False) id = treeobj.type.ToString() if id in type_dist: tp = type_dist[treeobj.type.ToString()] #Print all type of objects #print("--Name: ", tp) else: info[id]=name if treeobj.is_device: deviceid = treeobj.get_device_identification() t = 'type='+str(deviceid.type) +'\nid=' +str(deviceid.id) + '\nver='+ str(deviceid.version) if tp == "progInfo": print("-- There is prog info, ", tp) print("-- It has textual declaration: , ", treeobj.has_textual_declaration) print("-- It has textual implementation: , ", treeobj.has_textual_implementation) print("-- It is folder: , ", treeobj.is_folder) print("-- It is children: , ", treeobj.get_children(False)) print("-- It is children len: , ", len(treeobj.get_children(False))) print("-- It is progInfo type: , ", type(treeobj.ScriptProject)) #for child in treeobj.get_children(False): # print_tree(child, depth+1,curpath) try: if treeobj.is_folder : #system.ui.prompt('folder:'+u, PromptChoice.YesNo, PromptResult.Yes) isfolder=true pass except: pass if treeobj.has_textual_declaration : t=t+'(*#-#-#-#-#-#-#-#-#-#---Declaration---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' a=treeobj.textual_declaration t=t+a.text if treeobj.has_textual_implementation: t=t+'(*#-#-#-#-#-#-#-#-#-#---Implementation---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' a=treeobj.textual_implementation t=t+a.text if treeobj.has_textual_declaration and not treeobj.has_textual_implementation: t=t+'(*#-#-#-#-#-#-#-#-#-#---NOT Implementation visible---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' if treeobj.is_task : exports=[treeobj] projects.primary.export_native(exports,os.path.join(curpath,name+'.task')) if treeobj.is_libman: exports=[treeobj] projects.primary.export_native(exports,os.path.join(curpath,name+'.lib')) if treeobj.is_textlist: treeobj.export(os.path.join(curpath,name+'.tl')) children = treeobj.get_children(False) if children or isfolder: if tp: curpath=os.path.join(curpath,name+'.'+tp) else: curpath=os.path.join(curpath,name) if not os.path.exists(curpath): os.makedirs(curpath) if t: save(t,curpath,name,tp) for child in treeobj.get_children(False): print_tree(child, depth+1,curpath) for obj in projects.primary.get_children(): print_tree(obj,0,save_folder) with open(os.path.join(save_folder,'ExportInfo.txt'),'w') as f: now = datetime.now() infTimeExecution = now.strftime("%Y-%m-%d %H:%M:%S") f.write("Export date and time: "+infTimeExecution + "\r\n" + str(info)) print("--- Script finished. ---") #system.ui.info('save ok') projects.primary.close()
Last updated: 2024-04-30
Post by francesco86 on Script python for write in a file Project information
CODESYS Forge
talk
(Post)
Dear all, My python script can read a Codesys project and save in file the different POU, but the problem is that I don't able to read the project info from the obj list. Following of this message there is my python script. Can you help my? Best regards Francesco # encoding:utf-8 # We enable the new python 3 print syntax from __future__ import print_function import os import shutil import time import sys from datetime import datetime print("--- Saving files in the project: ---") print("sys.argv: ", len(sys.argv), " elements:") for arg in sys.argv: print(" - ", arg) if (len(sys.argv)>1): folderExportName = sys.argv[1] print(" folderExportName: ", folderExportName) exportPath = sys.argv[2]+ sys.argv[3]+ "\\"+ sys.argv[1] print(" File path: ", exportPath) # git has_repo=False #save_folder=r'E:\Tmp\ControlPlugins\ControlPlugins\Export' save_folder = exportPath if not os.path.exists(save_folder): os.makedirs(save_folder) else: a=os.listdir(save_folder) for f in a: if not f.startswith("."): sub_path= os.path.join(save_folder,f) if os.path.isdir(sub_path): shutil.rmtree(sub_path) else: os.remove(sub_path) elif f==".git": has_repo=True info={} type_dist={ '792f2eb6-721e-4e64-ba20-bc98351056db':'pm', #property method '2db5746d-d284-4425-9f7f-2663a34b0ebc':'dut', #dut 'adb5cb65-8e1d-4a00-b70a-375ea27582f3':'lib', #lib manager 'f89f7675-27f1-46b3-8abb-b7da8e774ffd':'m', #method no ret '8ac092e5-3128-4e26-9e7e-11016c6684f2':'act', #action '6f9dac99-8de1-4efc-8465-68ac443b7d08':'pou', #pou '6654496c-404d-479a-aad2-8551054e5f1e':'itf', #interface '738bea1e-99bb-4f04-90bb-a7a567e74e3a':'', #folder 'ffbfa93a-b94d-45fc-a329-229860183b1d':'gvl', #global var '5a3b8626-d3e9-4f37-98b5-66420063d91e':'prop', #property '2bef0454-1bd3-412a-ac2c-af0f31dbc40f':'tl', #textlist '63784cbb-9ba0-45e6-9d69-babf3f040511':'gtl', #global textlist '225bfe47-7336-4dbc-9419-4105a7c831fa':'dev', #device 'ae1de277-a207-4a28-9efb-456c06bd52f3':'tc', #task configuration 'f8a58466-d7f6-439f-bbb8-d4600e41d099':'m', #method with ret '261bd6e6-249c-4232-bb6f-84c2fbeef430':'gvl', #gvl_Persistent '98a2708a-9b18-4f31-82ed-a1465b24fa2d':'task', #task '085afe48-c5d8-4ea5-ab0d-b35701fa6009':'progInfo'#project information }; def save(text,path,name,tp): if not tp: tp='' else: tp='.'+tp+'.txt' with open(os.path.join(path,name+tp),'w') as f: f.write(text.encode('utf-8')) def print_tree(treeobj, depth, path): global info #record current Path curpath=path isfolder=False t='' #text tp='' #type # get object name name = treeobj.get_name(False) id = treeobj.type.ToString() if id in type_dist: tp = type_dist[treeobj.type.ToString()] #Print all type of objects #print("--Name: ", tp) else: info[id]=name if treeobj.is_device: deviceid = treeobj.get_device_identification() t = 'type='+str(deviceid.type) +'\nid=' +str(deviceid.id) + '\nver='+ str(deviceid.version) if tp == "progInfo": print("-- There is prog info, ", tp) print("-- It has textual declaration: , ", treeobj.has_textual_declaration) print("-- It has textual implementation: , ", treeobj.has_textual_implementation) print("-- It is folder: , ", treeobj.is_folder) print("-- It is children: , ", treeobj.get_children(False)) print("-- It is children len: , ", len(treeobj.get_children(False))) print("-- It is progInfo type: , ", type(treeobj.ScriptProject)) #for child in treeobj.get_children(False): # print_tree(child, depth+1,curpath) try: if treeobj.is_folder : #system.ui.prompt('folder:'+u, PromptChoice.YesNo, PromptResult.Yes) isfolder=true pass except: pass if treeobj.has_textual_declaration : t=t+'(*#-#-#-#-#-#-#-#-#-#---Declaration---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' a=treeobj.textual_declaration t=t+a.text if treeobj.has_textual_implementation: t=t+'(*#-#-#-#-#-#-#-#-#-#---Implementation---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' a=treeobj.textual_implementation t=t+a.text if treeobj.has_textual_declaration and not treeobj.has_textual_implementation: t=t+'(*#-#-#-#-#-#-#-#-#-#---NOT Implementation visible---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' if treeobj.is_task : exports=[treeobj] projects.primary.export_native(exports,os.path.join(curpath,name+'.task')) if treeobj.is_libman: exports=[treeobj] projects.primary.export_native(exports,os.path.join(curpath,name+'.lib')) if treeobj.is_textlist: treeobj.export(os.path.join(curpath,name+'.tl')) children = treeobj.get_children(False) if children or isfolder: if tp: curpath=os.path.join(curpath,name+'.'+tp) else: curpath=os.path.join(curpath,name) if not os.path.exists(curpath): os.makedirs(curpath) if t: save(t,curpath,name,tp) for child in treeobj.get_children(False): print_tree(child, depth+1,curpath) for obj in projects.primary.get_children(): print_tree(obj,0,save_folder) with open(os.path.join(save_folder,'ExportInfo.txt'),'w') as f: now = datetime.now() infTimeExecution = now.strftime("%Y-%m-%d %H:%M:%S") f.write("Export date and time: "+infTimeExecution + "\r\n" + str(info)) print("--- Script finished. ---") #system.ui.info('save ok') projects.primary.close()
Last updated: 2024-04-30