Post by niallel on How to change bHiresMode
CODESYS Forge
talk
(Post)
Hi, I'm trying to get Scaling working on my axis. An increment produces 36.6mm of movement, so I want to put the units in application as 36.6. However the docs say that I need to change bHiresMode as it doesn't show me the option for Precision in the User Interface. I'm thinking that I need to change the precision so I can enter decimal places. How can I do this, or is my thinking wrong? Thanks,
Last updated: 2024-03-11
Post by andy-yemm on Assertion Failed
CODESYS Forge
talk
(Post)
I had similar assertion failed error messages today. I am fairly new to Codesys. I tried using SFC for the first time, I usually use ST. Anyway I had errors in some of my transitions. I copied and pasted transition code and forgot to change the target of the code. I started getting lots of the assertion errors but now I have sorted out the problems and it compiles OK the assertion error messages seem to have stopped. There do not seem to be any other responses to your post, did you resolve your problem?
Last updated: 2024-03-19
Post by marcolim on RPC failed 0x16c9a085
CODESYS Forge
talk
(Post)
Hello Matteo, I think the problem is about configuration of firewall (windows firewall usually). You can disable temporary the firewall to check if the communication works. Eventually you can: Go to the control panel -> Windows Defender Firewall -> Allow an app or feature Enable the options to change the settings. Scroll down in the application list to CODESYS and CODESYS ControlService. If you don’t see this application add it to the list. Make sure that all the checkboxes are checked (Domain, Private and public).
Last updated: 2024-04-01
Post by codesysjupiter on Could not be resolved - Library error
CODESYS Forge
talk
(Post)
Hello, everyone. How are you? Please help me with my library error. When I open the CODESyS project, the error message is Could not open library “#loDrvEthernet. (Reason: The placeholder library ToDrvethemet’ could not be resolved.) I tried to find solution to fix this . and the help teach me to run this command "Update placeholder <iodrvethernet> to the newest version:" Is this right ? But I couldn't find where I input this command and how to run it. Or any other solution , please ?</iodrvethernet>
Last updated: 2024-04-12
Post by codesysjupiter on Library Error
CODESYS Forge
talk
(Post)
Hello, everyone. How are you? Please help me with my library error. When I open the CODESyS project, the error message is Could not open library “#loDrvEthernet. (Reason: The placeholder library ToDrvethemet’ could not be resolved.) I tried to find solution to fix this . and the help teach me to run this command "Update placeholder <iodrvethernet> to the newest version:" Is this right ? But I couldn't find where I input this command and how to run it. Or any other solution , please ?</iodrvethernet>
Last updated: 2024-04-12
Post by micik on CAA File, how to check whether file exists or not
CODESYS Forge
talk
(Post)
Hello, what would be the most efficient way to check whether the file exists or not. I don't want to use file.Open function, it seems like rather inefficiet operaton. I considered GetAttribute function, but this function doesn't accept filename (with path) as an input. Basically I need to check first time when program is loaded to the runtime i.e. when application is started for the first time, whether a file exists on the specific location or not.
Last updated: 2024-05-16
Post by engrahman on The current baud rate could not be determined in CR0020 IFM with maintenance tool
CODESYS Forge
talk
(Post)
Hello everyone, im working with IFM CR0020 controller via RS232 protocol where im trying to connect it to my PC but, every time when im using the maintenance tool to identify the device i get the error "The baud rate could not be determined" i have tried to change the cable of RS232 with different types but the error presist, any idea how to fix it
Last updated: 2024-05-21
Post by svdpoint on Raspberry Pi Zero 2W with external Ethernet adapter
CODESYS Forge
talk
(Post)
Hello all, Somebody try to run the CodeSys at RPi Zero 2W with external ETHx device? I need to more information how youi do it, what need to it, ...etc. It is interesting to use it together with EtherCat-interface. For example I had try to connect W5500 over SPI. The eth0 is present, but does not found any EtherCat IO-device. BR
Last updated: 2024-05-25
Post by kris-samoy on Get Alarm status in Codesys
CODESYS Forge
talk
(Post)
I am rather new to Codesys and I'm trying to figure out how to get the status of an alarm. This to interlock the start of a device until the alarm has been acknowledged... I am not sure if IAlarm.GetState (METH) can be used for this purpose. If yes then could someone please briefly explain how to use this? https://content.helpme-codesys.com/en/libs/AlarmManager/4.1.0.0/Interfaces/pou-IAlarm/GetState.html Thx & grtz, Kris
Last updated: 2024-06-03
Post by mozed on Bug Device login
CODESYS Forge
talk
(Post)
Good morning, The problem I encounter is very disturbing, when I try to connect to my project, it asks me to put in my username and password, which I do. However, I cannot connect and it restarts. the window to rewrite my identifiers. However it is the correct identifier and password I do not understand why. When I try to put false identifiers there strangely it tells me that these are not valid identifiers. There is something what can I do? Sincerely
Last updated: 2024-06-11
Post by durallymax on VAR_INFO from inside of a FB to get info on the instance.
CODESYS Forge
talk
(Post)
The help link appears to be broken. When I implemented something similar I had to add {attribute 'reflection} above the declaration of the FB with {attribute 'instance-path'} above the string VAR that would contain the path. Then wrote a function to trim off however much I wanted removed by searching for periods, then formatting it with spaces at the periods and removing brackets on arrays while also breaking up the PascalCase to present it a bit nicer for the end-users.
Last updated: 2025-12-12
Post by tommyk-mar on Smooth path is not working with SMC_NCInterpreter
CODESYS Forge
talk
(Post)
Hello, Im using SMC_NCInterpreter and SMC_NCReadFile2 to read gcode program for CNC machine and what I have observed is that G51 and G52 is not smoothing the path. Machine stops in every point, what could I do to make machine pass through the points without stopping or what could allow me to use smooth path corretly if I use NCInterpreter. Im using it because I want to add variables to my gcode and its not possible directly from the CNC editor thats why I do use external file. Any ideas?
Last updated: 2026-03-26
Post by confre on Combo box drop-down invisible
CODESYS Forge
talk
(Post)
Hi, I created a combo box and I need to know when the drop‑down menu is open, in order to avoid hiding the combo box while the drop‑down is visible. Alternatively, if it’s not possible to detect whether the drop‑down is open, I would like to know how to close or hide the drop‑down programmatically when the combo box is made invisible. I'm using Codesys 3.5 SP19 on IFM CR1074 without touch screen (with standard keyboard handling) Thanks.
Last updated: 2026-04-09
Post by mondinmr on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
In reality, other vendors are already moving towards integration with VS Code. B&R, for example, is likely the only one that could truly challenge Codesys in the market: they’ve overhauled their once-archaic environment (previously lacking ST OOP) and are now catching up significantly with Automation Studio Code, offering modern programming capabilities and native support for tools like Git and GitHub Copilot. The other big names in the market, frankly, are still light years behind. For smaller projects, typically handled by “wire strippers” (with all due respect!), a classic environment might be just fine. But once you’re dealing with thousands or even millions of lines of code—possibly organized in an OOP paradigm, spanning large teams, integrating third-party libraries, requiring version control, and performing comprehensive tests—a lightweight, responsive editor supercharged with AI-based features becomes essential. The real strength of something like VS Code lies in its vast ecosystem of extensions and integrations: from advanced Git support to automated build/test pipelines, and even AI-assisted autocompletion that already makes software development much more agile and productive. I understand that a PLC project involves more than just ST code (task setup, fieldbus configuration, libraries, etc.). However, there’s no technical reason not to at least provide ST files in a pure text format, making version control and collaboration far easier. B&R has clearly adopted this approach; I hope Codesys will accelerate its own efforts to offer a native, text-based integration and modern development tooling. Once you go beyond a certain level of complexity—dozens of configurations, OOP hierarchies, and distributed teams—you really do need “engineer-level” software tools, not just solutions targeting “wire strippers.” For large-scale automation projects, a more open and flexible approach is the only way to avoid chronic frustration. Let me emphasize that I truly love Codesys and consider the work done so far to be brilliant—I’d be sorry to see it overshadowed by others moving faster in this direction.
Last updated: 2025-02-18
Post by sahin6033 on DSE M840-001-02: DSEServiceTool transfers CodesysApp.pkg successfully, but device shows “No application loaded
CODESYS Forge
talk
(Post)
Hi, I am trying to load a test application into a DSE M840-001-02 display, but after reboot the device still shows: “No application loaded” I would like to understand whether the problem is in my project, the package creation process, or firmware/runtime compatibility. Hardware Device: DSE M840-001-02 Firmware used: M840 MKII Firmware File v4.1.2 Software CODESYS V3.5 SP12 (32-bit) DSE CODESYS Package v1.5.44 DSEServiceTool What I did Created a new empty Standard Project Selected target/template: M840-02 V4.1 Used a minimal ST program only: PROGRAM PLC_PRG VAR xAlive : BOOL := TRUE; END_VAR Confirmed: project builds PLC_PRG is assigned to MainTask created Boot Application Generated CodesysApp.pkg Put the M840 into bootloader mode Sent the package using DSEServiceTool DSEServiceTool result Transfer completes successfully and I get: connection accepted 100% download package ACK <status>OK</status> ** Example log:** Searching for controllers.... sendPackageToController: waiting for incoming data connection... sendPackageToController: connection accepted... <status>Downloading</status> <percent>20</percent> <percent>40</percent> <percent>90</percent> <percent>100</percent> sendPackageToController: sent 112cb8 bytes OK Package ...\CodesysApp.pkg transferred to controller c0a80101 OK sendPackageToController: package ACK <status>OK</status> Actual result After reboot, the display still shows: “No application loaded” Additional issue I also saw earlier At one stage I also had these fatal errors in CODESYS: [FATAL ERROR] Unresolved reference: 'IOMGRLOCKENTER' [FATAL ERROR] Unresolved reference: 'IOMGRLOCKLEAVE' I checked library versions and adjusted them to: IoDrvBase = 3.5.5.0 IoStandard = 3.5.10.0 Also, I am using CODESYS SP12, which I understand is the correct version for DSE M840. My questions If DSEServiceTool shows Status OK and package ACK, but the device still says “No application loaded”, does that mean: the .pkg was transferred but not accepted as a valid application? the package was built incorrectly? the boot application / runtime / firmware versions are still mismatched? What is the correct procedure to generate CodesysApp.pkg for M840-02 V4.1? Is there any known compatibility issue between: DSE CODESYS Package 1.5.44 M840 MKII Firmware 4.1.2 CODESYS 3.5 SP12 Has anyone successfully loaded even a minimal empty test project into M840-001-02, and if so, what exact versions/process did you use? Any help would be appreciated.
Last updated: 2026-03-17
Post by grant32 on RAMP_REAL FB is retaining my output value when i try to re use the FB
CODESYS Forge
talk
(Post)
Hello, I'm relatively new to PLC programming. I am trying to creat a ramp down function, I have an example here of what I am using. I can get the function to work, the issue is that the OUT (variable3) value is being held by the FB so after I use it once it no longer works. In this example i set variable3 to 100 and the rest is as seen, over the course of a minute it ramped down to 10 (as desired). But when I deenergize TEST_START, set variable3 back to 100, and then re-energize TEST_START it immediately jumps back to the previously held value 10. The reset on this block just pauses the function and holds the last OUT. In my case I will need the function to start OUT at a set value, ramp down to the IN (variable2) value, and then accept a new OUT value to ramp down next time the block is energized. Hopefully this made sense, if anyone has any advice that would be awesome!
Last updated: 2024-07-29
Post by yannickasselin on Connect to remote PLC via local pc and teamviewer
CODESYS Forge
talk
(Post)
Yes it is possible. I did it a lot of times using TeamViewer VPN. Unfortunately, TeamViewer VPN only works on Windows. If the remote PLC is a Codesys runtime running on Windows, you should be able to login directly using TeamViewer VPN if it is installed on the PC/PLC. If it is not Windows based, you can still do it but you need to have a Windows based PC acting as a gateway in the middle. In this case you need to enable IP Forwarding on the Windows remote PC (the gateway) and you need to setup the gateway IP address on the PLC to be the address of the Windows PC. Then you need to add a route on your local PC to point to the gateway PC for Codesys communication. I know it may not be detailed enough but I did not want to make a whole tutorial on how to do it. Bottom line, it is possible. I do it all the time.
Last updated: 2024-02-02
Post by tomast on Codesys and Siemens SINAMICS 20 modbus RTU "Response CRC Fail"
CODESYS Forge
talk
(Post)
Hi everyone, I'm currently working on a project involving the control of 5 VFDs via Modbus RTU, this time using the WAGO 750-8212 CPU. So far, I've managed to make progress, but I've encountered an issue. While I can successfully read and write to all the registers I need, I consistently encounter a "Response CRC Fail" error when attempting to write the value 1151 to the STW register at address 40100. I'm able to set the frequency via register 40101 and adjust all other parameters using different registers. Setting STW to 1150 results in the drive ready boolean from the ZSW-bit being received instantly. However, the moment I attempt to send 1151 to register 40100, I immediately receive the "Response CRC Fail" error for all channels. I've also attempted to use combined control, employing Modbus for frequency control and starting from a digital input. Everything seems to function properly until I send the start command to the VFD. Interestingly, I consistently encounter the same error the moment I send the start command, regardless of whether I use register 40006 (high) or 40100 (1151). Could someone please assist me in resolving this issue?
Last updated: 2024-03-21
Post by xnoop on MBTCP Slave configuration
CODESYS Forge
talk
(Post)
Hello, I use Codesys 3.5 SP18 Patch 4 (64 bit) My Codesys project is composed of several dozen of Modbus TCP Slaves. I want to configure each of them by define : - Modbus TCP Slave Configuration : Name, IPAddress, port - Channels - Mapping I can't afford to configure manually and I need to find automatic way What possibilities does the Codesys offer? 1. I know it possible to use python script to create Modbus TCP Master and Slave. But I don't find anyway to create Channels and Mapping through the API 2. I 've tested to set mapping with file.csv on a Modbus Tcp Slave, but no way to import channels definition from file 3. I 've tried to use PLCOpenXml file. For example I 've create a project with an Ethernet device. I've exported it in PlcOpenXml file. After delete the Ethernet device, I've imported the PlcOpenXml file without success. I've tried the same by creating Modbus TCP Slave. Could you help me to find to good way ? Thanks
Last updated: 2024-06-19
Post by andrea199403 on Assigning Modbus addresses to a structure in a dynamic way
CODESYS Forge
talk
(Post)
Hello everyone, I am new to this forum and I am also new to Codesys programming. My problem is this: I have a STRUCT of 64 bool and 30 real, this STRUCT is assigned in the programme 9 times. Now I need to communicate with an HMI via Modbus and I have defined the slave device and created the holding registers for communication. I would like to declare the first call of the STRUCT on the Modbus registers %QX2000.0 to %QX2007.7 for the booleans and on the registers %QW1004 to %QW1034 for the real registers. That said, I would like to change an index and set an offset of 100 bytes for the calls of the other 8 assignments, so that the result is: %QX2100.0 to %QX2107.7 for the booleans and on the %QW1104 to %QW1134 registers for the Real registers, etc. Is there a way to declare this? Thank you very much.
Last updated: 2025-10-21
Post by thommy54 on Raspi-Cam: CameraStream.project nicht zum Laufen zu bringen
CODESYS Forge
talk
(Post)
Hallo, Ich bringe das CameraStream.project nicht zum Laufen. Ich sehe die Ursache darin, das das Beispielprogramm sehr sparsam mit Programm-Kommentaren umgeht (von der Hilfe gar nicht zu reden). Ich habe beide Varianten bei der zu ändernden Zielvariable getestet: //copy video.htm to the webserver; //the location of the webserver depends on the used Apache version as mentioned in online help hDirHtmlTest:=SysDirOpen( szDir:='/var/www', pDirInfo:= ADR(dirInfo), diMaxDirEntry:=iMaxDirEntry, szDirEntry:=szDirEntry, pResult:=ADR(iDirHtmlError)); IF (iDirHtmlError = 0) THEN SysDirClose(hDir:=hDirHtmlTest); SysFileCopy('/var/www/video.htm', '$$PlcLogic$$/Application/video.htm', ADR(dwCopySize)); ELSE .... als auch hDirHtmlTest:=SysDirOpen( szDir:='/var/www/html', pDirInfo:= ADR(dirInfo), diMaxDirEntry:=iMaxDirEntry, szDirEntry:=szDirEntry, pResult:=ADR(iDirHtmlError)); IF (iDirHtmlError = 0) THEN SysDirClose(hDir:=hDirHtmlTest); SysFileCopy('/var/www/html/video.htm', '$$PlcLogic$$/Application/video.htm', ADR(dwCopySize)); ELSE .... Die Url-Streams habe ich gelassen wie sie vorgegeben waren: urlStream := CONCAT('http://', CONCAT(sIPAddress, '/video.htm')); urlPicture := CONCAT('http://', CONCAT(sIPAddress, '/cam_pic.php')); In der Webvisu im Browser komme ich maximal dahin wie im Screeshot Video_Visu_1 zu sehen. Also scheint der Link zu video.htm zu klappen. Das der zu cam_pic.php nicht klappt, wundert mich nicht, denn es existiert nicht und wird auch nicht evtl. am rechten Ort angelegt. Ich bin mir vollkommen im Unklaren: muss da was auf dem Raspberry Pi im Hintergrund laufen , z.B. raspivid . Welcher Programmteil bedient die Cam ? Ich erkenne auch nicht, wo ein einzelnes picture entstehen soll. Wäre dankbar, wenn ich hier etwas Hilfe bekommen könnte. Evtl. gibt es Probleme mit der von mir verwendeten Codesys-Version 3.5.20.1 ? Ich benutze einen Raspberry 4 Rev.1.2. Grüße Thomas
Last updated: 2024-07-04
Post by rossanoparis on How to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server
CODESYS Forge
talk
(Post)
Hello at all I'd like to know how to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server. In the past, I tried to ask in "Forge" about this topic, but I could find neither help nor document informations about it. Reading the file "codesyscontrol.log" I see these logs OPC UA Server Started: Hostname: NTLRPICTRL01, Port: 4840 URL: opc.tcp://NTLRPICTRL01:4840 Loopbackadapter activated. **All available networkadapters are used.** Multithreading activated. 3 workers used. My controller, which is a Linux PC, has got two network cards eth0 and eth1 I whant to use the card with name "eth0" as a server for OPCUA and keep the "eth1" free for other stuffs. Is it possible ? Best regards Rossano
Last updated: 2023-08-25
Post by muhq on Profinet connection to Siemens CP343-1 Lean (IO-Device/Slave)
CODESYS Forge
talk
(Post)
Hi, I am quite new to Codesys and I try to do a Profinet connection to an Siemens PLC (315-2DP) with CP343-1 Lean Modul. I already configured the Siemens PLC, exported the GSDML. Then I added a new project in Codesys, added following moduls: - Ethernet - PN_Controller - Imported Profinet Device via GSDML importer When I start the programm everything looks fine but I always get the message "Stopped Profinet" and no data is available This is only for a small test. Therefore I start to do that on a Windows 10 with Development System. Later I will try to realize this on Raspberry. Ethernet Adapter is configured (192.168.1.1 / 24) Firewall deactivated WinPCap is installed S7-Station seems to be found ('fuadazenzitest') Can please somebody help me?
Last updated: 2023-08-26
Post by andre-luis on Check if Codesys runtime is on 'Running' or 'Stopped' state?
CODESYS Forge
talk
(Post)
Hi there, I'm running the Codesys runtime on Windows 64 and I need to know if it is on "Running" or "Stopped" state just after a system crash. The following commands works perfectly well to (re)start it... net stop “CODESYS Control Win V3 - x64" net start “CODESYS Control Win V3 - x64" ...however I'm unable to determine when it is required to be call; I mean, by checking the System Tray icon, it is possible to know if it is on "Stopped" state, but I wanted to run a .BAT command to retrieve it. How can we do that?
Last updated: 2024-07-02
Post by vamsi on How to configure gateway for programming RPi 2B using Codesys
CODESYS Forge
talk
(Post)
I am using a Raspberry Pi 2B. Installed Codesys V3.5.20.1 64-bit and installed 'CODESYS Control for Raspberry PI 4.12.0.0' I am able to install the packages using the 'Update Raspberry Pi' option, but when I try to log into the RPi, in the Device tab it says 'Sacn fail. Please checl that the gateway is running and that its settings are correct'. My setup looks like this. I connected my RPi to my company LAN and also my laptop to company LAN (using HP Docking station). This setup worked when I installed 'CODESYS Control for Raspberry PI', but now I donot know how to configure the gateway. Could anyone please help me in finding what I have to enter in the gateway configuration? Thanks, Vamsi.
Last updated: 2024-07-10