Post by dkugler on User management
CODESYS Forge
talk
(Post)
If the PLC is equieped with a USB socket it's possible to copy the user management file via IEC code to a USB stick and restore it at the new plc. The file is located there: /PlcLogic/visu/app_visuusermgmtdb.csv I use this to reset the user management to default in case of the customer has changed passwords and lost it.
Last updated: 2024-09-04
Post by pietrobalint on Persistent variables are not read after initialization
CODESYS Forge
talk
(Post)
Hi, I realized that if I replug the power supply the persistent variables lost their value with the new software too. Cold reset do not affect the variables value but hardware reboot still reset the values. Application Composer can't be activated. What is the solution?
Last updated: 2024-10-11
Post by gseidel on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
Hi Gustavo, can you reduce the problem to a project that reproduces the issue without the real servo drives? (You could set the servo drives to virtual and strip away as much as possible from the application.) If you can attach a project, we will have a look. Best regards, Georg
Last updated: 2025-01-10
Post by timvh on library is not available
CODESYS Forge
talk
(Post)
1) In the library manager of your project select "Download missing libraries". 2) In the library manager open the "Placeholders" dialog. In here find the Placeholder which is not referenced to a specific library yet. Click in this line on the Library column and select the latest version of this library.
Last updated: 2025-03-24
Post by atone on Set DeviceID of an IO-Link Sensor at Runtime
CODESYS Forge
talk
(Post)
Answering to myself: is not possible according to the IFM support, this possibility has not been taken into account, although the interfaces and FBs in Codesys would apparently support it. So I ended up having to deactivate the sensor validation and the backup & restore functionality in the master and implement it in the PLC myself.
Last updated: 2025-04-28
Post by rajatdas2005 on Codesys Virtual control SL
CODESYS Forge
talk
(Post)
Thanks once again. Right now the codesys virtual control sl docker is using the host ip itself not the docker ip. so the local host edge gateway was able to search the virtual plc. so you are telling me instead of local host edge gateway I should use the edge gateway docker version?
Last updated: 2025-08-08
Post by nilanjan on I want to show the current recipe name in the visualization screen
CODESYS Forge
talk
(Post)
I am having some trouble showing the current recipe name in visualization i am not using the RecipeManCommands i am using the inbuild visualization feature of Saving and Loading recipes. I need it so the user would have a track on which recipe is being used currently.
Last updated: 2025-08-24
How to select the real I/O module terminals/channels in CODESYS V3.5 ? Or better to say, How to specify the real physical terminals of analog and digital I/O modules in the CODESYS programm ?
CODESYS Forge
talk
(Thread)
How to select the real I/O module terminals/channels in CODESYS V3.5 ? Or better to say, How to specify the real physical terminals of analog and digital I/O modules in the CODESYS programm ?
Last updated: 2022-08-13
How to select the real I/O module terminals/channels in CODESYS V3.5 ? Or better to say, How to specify the real physical terminals of analog and digital I/O modules in the CODESYS programm ?
CODESYS Forge
talk
(Thread)
How to select the real I/O module terminals/channels in CODESYS V3.5 ? Or better to say, How to specify the real physical terminals of analog and digital I/O modules in the CODESYS programm ?
Last updated: 2022-07-29
Post by alexgooi on How to protect library project?
CODESYS Forge
talk
(Post)
Hi aniket-b, If you save the library as a compiled library you are not able to see the source code. When the end user tries to view inside the object, CODESYS will give a notification that the source code is missing, see attachment. In short if you don't send the source code, it will not show.
Last updated: 2024-01-25
Post by dhumphries on WAGO PLC 200 750-8216 Ethernet connection to Codesys 3.5
CODESYS Forge
talk
(Post)
make sure the PLC and the programming PC have IP addresses that are on the same subnet, you'll have to know the default address of the PLC or you may need to connect to it with a special cable and use a software tool to set the IP address.
Last updated: 2024-02-06
Post by namwind on Wago 8210
CODESYS Forge
talk
(Post)
Hi guys, I ran into problem with the controller is not saving the project into the internal memory. I was able to download the project to the controller, but as soon as I try to recycle the power it power back up with no project. I have not ran into this problem before. Please help me out thank you.
Last updated: 2024-03-02
Post by schnepper on How to delete main action from SFC Step
CODESYS Forge
talk
(Post)
I added a main action to an SFC step, and then tried to delete it. There is no delete option in the SFC menu nor in the right click menu of the step. I deleted the action from the device tree, but building results in and error saying the action is not defined. Is there a way to delete a main action?
Last updated: 2024-05-23
Post by jeffersonhui on SysProcessExecuteCommand2 terminate
CODESYS Forge
talk
(Post)
Hi, I am using the SysProcessExecuteCommand2 function from the SysProcess library to run the candump command in the PLC's Linux environment. However, the candump command stays running indefinitely. If I was running the candump command from a terminal (via PuTTy, etc), that command usually requires Ctrl+C to terminate. Is there a way to terminate a command that is executed with SysProcessExecuteCommand2?
Last updated: 2024-06-24
Post by mg0815 on ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks
CODESYS Forge
talk
(Post)
I use Codesys 3.5.21.1 too I have absolutelly the same fault. Do you know the solution? I get the same massages accept the last one (up to your's from 2025-08-03 04:38) The last messages do not appear. (your's later than 2025-08-03 04:40) Reagards Mg
Last updated: 2025-11-04
Post by osande on Trend/trace data
CODESYS Forge
talk
(Post)
Ok, the problem is that the trend/trace system can't read function block instance data. The variables has to be stored directly under the program calling the FBs. Thus, FB variables to be trended/traced must be connected to variables declared in the program. Seems like a bug to me!
Last updated: 2026-03-13
Post by bdschnapp on OPC-UA ApplicationUri / ProductUri
CODESYS Forge
talk
(Post)
From Codesys support: The format of the URN is always the same. It's always urn:<vendor>:<product>:OPCUA:Server. What I think you can influence the vendor and product (DeviceName) through settings in the runtime cfg file:</product></vendor> [SysTarget] VendorNameUnicode="T\00E\00S\00T\00" DeviceNameUnicode="t\00e\00s\00t\00" Note that these are 16-bit strings, thus the ASCII padded with nulls
Last updated: 2026-03-17
Post by jeroenaero on Problem with CodeSys Control SL Deploy Tool 4.15.0.0
CODESYS Forge
talk
(Post)
Hello, We just installed the new version of CodeSys Control SL Deploy Tool 4.15.0.0 but we get the following error when we try to add a VPLC. Can someone of the CodeSys team fix this issue? the object reference is not set to an instance of the object Zie het einde van dit bericht voor meer informatie over het aanroepen van JIT-foutopsporing (Just In Time) in plaats van dit dialoogvenster. ** Tekst van uitzondering ** System.NullReferenceException: De objectverwijzing is niet op een exemplaar van een object ingesteld. bij _3S.CoDeSys.RuntimeDeployTool.Views.AddNewInstanceForm.ShowAllImages() bij _3S.CoDeSys.RuntimeDeployTool.Views.AddNewInstanceForm..ctor(List1 virtualControls, List1 existingNames) bij _3S.CoDeSys.RuntimeDeployTool.Views.MainEditorTab_Operation.OnAddInstanceClick() bij _3S.CoDeSys.RuntimeDeployTool.Views.MainEditorTab_Operation.bt_add_Click(Object sender, EventArgs e) bij System.Windows.Forms.ToolStripItem.RaiseEvent(Object key, EventArgs e) bij System.Windows.Forms.ToolStripButton.OnClick(EventArgs e) bij System.Windows.Forms.ToolStripItem.HandleClick(EventArgs e) bij System.Windows.Forms.ToolStripItem.HandleMouseUp(MouseEventArgs e) bij System.Windows.Forms.ToolStripItem.FireEventInteractive(EventArgs e, ToolStripItemEventType met) bij System.Windows.Forms.ToolStripItem.FireEvent(EventArgs e, ToolStripItemEventType met) bij System.Windows.Forms.ToolStrip.OnMouseUp(MouseEventArgs mea) bij System.Windows.Forms.Control.WmMouseUp(Message& m, MouseButtons button, Int32 clicks) bij System.Windows.Forms.Control.WndProc(Message& m) bij System.Windows.Forms.ScrollableControl.WndProc(Message& m) bij System.Windows.Forms.ToolStrip.WndProc(Message& m) bij System.Windows.Forms.Control.ControlNativeWindow.OnMessage(Message& m) bij System.Windows.Forms.Control.ControlNativeWindow.WndProc(Message& m) bij System.Windows.Forms.NativeWindow.Callback(IntPtr hWnd, Int32 msg, IntPtr wparam, IntPtr lparam) ** Geladen assembly's ** mscorlib Assembly-versie: 4.0.0.0 Win32-versie: 4.8.9300.0 built by: NET481REL1LAST_C
Last updated: 2025-04-24
Post by marek71 on Ambiguous use of name - CO136
CODESYS Forge
talk
(Post)
My PLC is WAGO PFC200 Firmware Revision 26. target After updating WAGO_Devices_and_Libraries with newer Firmware 27, CODESYS wants to update all libraries to new versions. I will only add that I did not update the Firmware in the PLC. After compiling the program, I received the following errors: ------ Build started: Application: Device.Application ------- Typify code... [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): FbSerialInterface_internal: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): FbSerialInterface_internal: C0136: Ambiguous use of name 'RTS_IEC_RESULT' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0032: Cannot convert type 'Unknown type: 'RTS_INVALID_HANDLE'' to type 'POINTER TO BYTE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0136: Ambiguous use of name 'RTS_INVALID_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0046: Identifier 'RTS_INVALID_HANDLE' not defined [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_is_tx_empty: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_get_line_state: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_is_line_available: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): COMSW_SET_MODE: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_set_line_state: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' Compile complete -- 10 errors, 0 warnings Build complete -- 10 errors, 0 warnings : No download possible The problem was caused by the WagoSysPlainMem(WAGO) library in the original version 1.5.3.0 after updating to 1.5.3.1. After returning to version 1.5.3.0, the problems disappeared. Probably the version number of this library is responsible for supporting the appropriate Firmware Revision. Can anyone confirm or deny my suspicions?
Last updated: 2024-07-06
Post by timvh on STRING conversions to DWORD
CODESYS Forge
talk
(Post)
I guess that the printer expects to receive an array of byte values. So where it is described that it expects to receive: Hercules String : 1B4F513030311B7532626C61636B04 it actually expects to receive an array of bytes with the values 1B,4F,51,30,30, etc. So what you can do is create an array of bytes and assign the byte value to each item in the array: VAR abyToSend : ARRAY[0..99] OF BYTE; END_VAR abyToSend[0] := 16#1B; // ASCII Escape character, hexadecimal representation uses 16# as prefix abyToSend[1] := 16#4F; // ASCII 'O' abyToSend[2] := 16#51; // ASCII 'Q' abyToSend[3] := 16#30; // ASCII '0' // you can do the rest yourself // maybe could be created a lot smarter, but gives you an indication how to handle this. Then with the serial communication (or TCP/IP?) you can send a message with the reference to the array (abyToSend) and the number of bytes to send (15 bytes for the string you gave as example).
Last updated: 2025-02-02
Post by george32 on TCP Server
CODESYS Forge
talk
(Post)
Thank you for your advice Rinie, I have tried to follow this example but found one problem.When I disconnect with Hercules the system does not acknowledge the lost of its connection this could result in critical errors. Because of this error I am trying to implement the Syssocket library. With this library I am having a problem which I could not solve. I have the following code: ip_adres : STRING :='0.0.0.0'; port : WORD := 5000; iStep : INT := 1; // Socket information Socket_handler : SysSocket_Interfaces.RTS_IEC_HANDLE; Socket_handler_result : SysSocket_Interfaces.RTS_IEC_RESULT; Socket_adress : SysSocket_Interfaces.SOCKADDRESS; Addres_Convert : SysSocket_Implementation.RTS_IEC_RESULT; // Bind information Bind_handler : SysSocket_Interfaces.RTS_IEC_RESULT; // Listener Information Listener_handler : SysSocket_Interfaces.RTS_IEC_RESULT; Addres_Convert := SysSocket_Implementation.SysSockInetAddr(szIPAddress:= ip_adres,pInAddr:= ADR(Socket_adress.sin_addr)); Socket_adress.sin_family:= SysSocket_Interfaces.SOCKET_AF_INET; Socket_adress.sin_port := SysSocket_Implementation.SysSockHtons(usHost:= port); CASE iStep OF 1: // Create Socket Socket_handler :=SysSockCreate( iAddressFamily :=SysSocket_Interfaces.SOCKET_AF_INET, diType:=SysSocket_Interfaces.SOCKET_STREAM, diProtocol:=SysSocket_Interfaces.SOCKET_IPPROTO_TCP, pResult:=ADR(Socket_handler_result)); IF Socket_handler = SysSocket_Interfaces.RTS_INVALID_HANDLE THEN iStep := 1; ELSE iStep := 2; END_IF 2: Bind_handler := SysSocket_Implementation.SysSockBind( hSocket:=Socket_handler, pSockAddr :=ADR(Socket_adress), diSockAddrSize:=SIZEOF(Socket_adress) ); 3: Listener_handler := SysSocket_Implementation.SysSockListen( hSocket :=Socket_handler, diMaxConnections :=1); END_CASE When I am trying to get this working, the SysSockBind function gives a value of 16#207 which means adress already in use. I find this weird because of the IP-adress of 0.0.0.0. I think I am converting the Ip-adress in the wrong way, but the code does not give a error arround this. So therefore I cannot find the solution to this problem. I hope someone could help me with this problem. Thanks in advance George
Last updated: 2025-02-20
Post by nz-dave on MC_HOMING
CODESYS Forge
talk
(Post)
Hi Just new to motion and i am building my own 3axis cnc cutter using servo drives. i have every thing working quite well apart from mc_home. when executed (r_trig) it stops immediately and i get fb_wasnt_called_during_motion. if i execute the mc_home fb with a toggle it just runs and runs for a while then errors out. what im unsure of is the way mc_home works. from what i understand it changes the drive mode to 6 (homing) and should then run of the drive homing settings. once origin sensor is made then homing would stop and mc_home.done is true. and the position on the fb is where i what the new home position (zero) to be? or do i feed mc_readposition to that input? so i would think its the settings in the drive that aren't quite right. but i believe they are all correct. has any one got any info to steer me in the right direction? Cheers
Last updated: 2025-04-04
Post by alexgooi on Licensing info not available.
CODESYS Forge
talk
(Post)
Sorry for the question, but I'm not completely getting the idea here, could you be more specific, maybe give an example? I'm now in a state where I don't have a softcontainer on my license server anymore (even after reinstalling from the Codesys-IDE). I tried reaching the webserver of Codemeter but when I do that I get redirected to http://"IP":22352 This is not reachable, afterwards I installed lynx on my Debian machine (command line only). From here I could reach the webserver and toggle the network server setting, but unfortunately this did not help. I also tried to changed the remote read setting to 1 (in the Server.ini file). But after a Codemeter reboot this is overwritten to 0. I have the feeling that it should be much easier to get a license to work, am I missing some checkbox somewhere? Is there a tutorial (or manual) that explains the licensing sequence step by step, because I'm pretty stuck.
Last updated: 2025-10-01
Post by mp9876 on Problem using MeasureFrequence FB
CODESYS Forge
talk
(Post)
Hi everyone, new at Codesys and PLC programming in general. I am using Codesys Win V3.5 SP20 I would like to measure an encoder's frequency output (obtaining that pulse train from Factory IO) and intended to use the MeasureFrequence FB (Intern/CAA/Utilities/CAA Mathematics/3.5.19.0). As mentioned in the title what I need to measure is low frequency, such as lower than 40hz (a cycle every 25mS) or so; I could even go lower frequency if required as this is for test purposes) therefore I am not expecting problem measuring a low frequency with that FB The library in question appears to be installed as I can retrieve it from the Library Repository. I can also see it from the Device's Library Manager. Problem arises when I am trying to instantiate this particular FB. I go like this: VAR MeasF:MeasureFrequence; END_VAR Please note that as soon as I start typing the "MeasureFrequence", the MeasureFrequence comes out as a viable option in auto-typing; seems to indicate that the FB is recognized somehow. But there is no way I can compile this as it comes back with the following: C0046: Identifier 'MeasureFrequence' not defined. Tried to rename that to ABC instead of MeasF; same issue. Possibly that the library is not properly installed ? Placeholder ? I would greatly appreciate a bit of guidance if possible. Thank you and regards, Mike
Last updated: 2024-06-24
Post by lukasz on Unresolved reference when trying to upload to Codesys Runtime V3
CODESYS Forge
talk
(Post)
Hello! I'm working with Codesys SP21 Patch 4. The project builds without any errors. When trying to upload my project to Codesys Runtime V3 x64 I get a lot of Unresolved Reference errors, all with FU- at the start and then -CLOSELAYER2, -GETBUSINFO, -GETFRAME etc. I also get a error pop-up that I should 'update device' in the project but it's not specified to which version or anything useful really.There's also not much to choose from. When I check Runtime version in the systray I get 3.5.21.40 and it's the same as I have set up in the project as the device. All information I get is that it should be clear from the errors but no useful information is provided in the errors. Do I need to install some library? I checked other posts and for different reference error and this was the answer. Thanks in advance!
Last updated: 2026-03-25