Post by nz-dave on Ethernet/IP Scanner Exception
CODESYS Forge
talk
(Post)
Hi Trusty-Squire, just seen you post , thanks for the reply. I was out on site the other day as it had done it again and changed a few things like cycle time etc. plc load is only 7% at its highest. I took a few screenshots while i was there to add to this post. its been up for about a week now but seems to happen at random every couple of weeks. fingers crossed!
Last updated: 2025-03-19
Post by wehling-h on PI Input value
CODESYS Forge
talk
(Post)
Hi geoweil, have you tried to save changed values to remanent area or using a VAR RETAIN? After restart you have to initialize Counter with last remanent value. Depending on changes per cycle and the possibilitiy of your control unit to write remanent storage. Otherwise you need a buffering system to ensure save backup of last PI_Counter value. May you could read this Thread to get further help: https://forge.codesys.com/forge/talk/Engineering/thread/31e1c8349e/#bf48
Last updated: 2024-01-12
Post by sturmghost on Visualization using methods and cyclic ST-calls
CODESYS Forge
talk
(Post)
I found a way to do it: You can use, for example, the text variable property of any visualization element and call a function in it. Example: Write a test POU as a function (FUN), like MyTestFun which need a boolean Variable as an input value. Now write into the text variable property: MyTestFun(bBooleanValue) Thats it. The function is called at each visu_task cycle.
Last updated: 2024-01-22
Post by alimans on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hi Manuknecht, Did you manage to solve the problem? I’m facing the same issue with Windows RTE SoftMotion — it works fine as long as nothing else is open in Windows, but as soon as I start another application, the EtherCAT DC time and max jitter values spike, and then all axes stop. I’ve already sent a support request to CODESYS, but haven’t received a response yet.
Last updated: 2025-10-23
Post by risele on dynamic modbus devices
CODESYS Forge
talk
(Post)
Have the same issue: I'm making a test setup for modbus devices testing and calibration. One is run for every possible address, and it starts with minimal request: if the device is found, it continue to work with it, otherwise it's set to Disabled temporary. Those state machines are running under FOR cycle, and disabled are just skipped. Every instance have its own timer for not running too frequently and a start delay, so the actual requests are separate in time. I also check not for a single error, but have some timer to allow one-two timeouts. The small program disables and re-enables devices temporary (manually, since i could not iterate over MB devices). VAR Reset:ARRAY[1..GVL_MB.MD_COUNT] OF R_TRIG; i:INT; END_VAR {IF hasconstantvalue(GVL_MB.MD_COUNT, 1, >= )} i:=1; MD_1.Enable:=GVL_MB.MDPortsEnable[i]; Reset[i](CLK:=GVL_MB.MDPortsEnable[i]); MD_1.xReset:=Reset[i].Q; {END_IF} {IF hasconstantvalue(GVL_MB.MD_COUNT, 2, >= )} i:=2; MD_2.Enable:=GVL_MB.MDPortsEnable[i]; Reset[i](CLK:=GVL_MB.MDPortsEnable[i]); MD_2.xReset:=Reset[i].Q; {END_IF} There is also program to re-enable devices periodically. METHOD ScanBus VAR_INPUT END_VAR VAR j:INT; (*block auto scanning if calibration is running for any device since it's data-reach process that should not be interrupted with modbus timeouts *) CalibrationBusy:BOOL:=FALSE; END_VAR CalibrationBusy:=FALSE; FOR j:=1 TO GVL_MB.MD_COUNT DO CalibrationBusy:=CalibrationBusy OR MD_Calibrate.AutoTesters[j].xBusy; END_FOR; IF CalibrationBusy THEN RETURN; END_IF tBusScanSchedule(IN:=(NOT tBusScanSchedule.Q), PT:=tBusScanPeriod); IF (NOT tBusScanDelayer.Q) AND (tBusScanSchedule.Q OR (NOT xFirstScanPerforemed)) THEN xBusScanBusy:=TRUE; MissingCounter:=0; xFirstScanPerforemed:=TRUE; FOR j:=1 TO GVL_MB.MD_COUNT DO (* MD_Calibrate is main calibration program. Identifiers - is array of State machines mentioned above Phase_Faulted is a state of Identifiers where I'm sure device is missing on the bus *) IF MD_Calibrate.Identifiers[j].state=eStateMDIdentifier.Phase_Faulted THEN MD_Calibrate.Identifiers[j].Rescan(); MissingCounter:=MissingCounter+1; END_IF END_FOR END_IF tBusScanPauser(IN:=tBusScanDelayer.Q AND (MissingCounter>0),PT:=tBusScanDelay*MissingCounter); xBusScanBusy:=tBusScanPauser.Q; xFirstScanPerforemed:=xFirstScanPerforemed OR tBusScanPauser.ET>=tBusScanPauser.PT; Also the GUI have buttons for each address possible that re-enables the device if required.
Last updated: 2026-02-13
Post by jonasz on Deploy LicenseServer for Linux SL
CODESYS Forge
talk
(Post)
So here's how: I manually installed the following packages: codemeter-lite_8.30.6885.501_amd64.deb codesyslicenseserver_licenseserver_4.18.0.0_all.deb codesyswbmbase_wbmbase_4.18.0.0_all.deb codesyswbmlicensing_wbmlicensing_4.18.0.0_all.deb Of course, the license server appeared immediately. Trying to install it again using Install in the Deploy tab, the same error appears. Of course, the information that such a server is already installed is also there. Configuring PLC, S_PLC, EDGE, and SAFE_TIMER_PROVIDER went smoothly, and basically everything works. I wrote a simple program for S_PLC. I'm loading the programs into PLC and S_PLC. When loading the program into S_PLC, a message appears stating that there is no connection to the S_PLC controller. Timeout error. Restart the controller, attempt to load, and see the above. After changing the cycle time for S_PLC to 50ms, the problem no longer occurs. My question, besides the difficulty of installation for a new user, is what causes the cycle time for S_PLC to be so long, and how can I fix it?
Last updated: 2025-11-14
Post by janderson on Ethercat scan for devices not picking up EL7041 as a softmotion axis
CODESYS Forge
talk
(Post)
it appears that the different revisions have different PDOs. I am currently trying to use the rev25. I have tried to use the rev24 (the device repository entry not from 'scan for devices') and i keep getting 'invalid output mapping' or 'invalid input mapping' in the ethercat log. I cant even get the bus to run from the device description that comes from 'scan for devices'...
Last updated: 2023-09-18
Post by janderson on Ethercat scan for devices not picking up EL7041 as a softmotion axis
CODESYS Forge
talk
(Post)
it appears that the different revisions have different PDOs. I am currently trying to use the rev25. I have tried to use the rev24 (the device repository entry not from 'scan for devices') and i keep getting 'invalid output mapping' or 'invalid input mapping' in the ethercat log. I cant even get the bus to run from the device description that comes from 'scan for devices'...
Last updated: 2023-09-18
Post by albertisa on GPIO Konfiguration auf SK-AM64B
CODESYS Forge
talk
(Post)
Hallo, seit einigen Tagen versuche ich erfolglos eine Ansteuerung der GPIOs des SK-AM64B Entwicklungsboards (Texas Instruments) über Codesys zu bewerkstelligen. Bei dem Versuch GPIOs anzusteuern, ohne die devdesc.xml bzw. den iodriver anzupassen, wird mir von Codesys die Fehlermeldung "Bus läuft nicht" (siehe Screenshot) angezeigt. Welche Vorgehensweise wird zur Konfiguration der IO empfohlen? Ist eine Anpassung der devdesc.xml und des IOdrivers notwendig? Wie wird am besten bei der Anpassung der genannten Dateien vorgegangen? Folgende Dokumentation ist mir bekannt, hat mir aber noch nicht weitergeholfen: https://forge.codesys.com/drv/io-drivers/doc/Generic/
Last updated: 2023-09-19
Post by vincentger on using ADS1115
CODESYS Forge
talk
(Post)
Any reason the ADS1115 wouldnt work with SP20.1 and Runtime 10.0.0.0 on the Raspberry Pi . Using Bullseye or Buster i run into the same issue: Libary and integration works in general as described above BUT i am seeing "bleeding" between the analog inputs . Specifically consecutive ones: So sometimes the raw from AI1 shows on AI2, AI2 on AI3, .. AI4 on AI1. Even with filtering i cant smoothen that out properly and i feel like something is wrong. Almost like the bus is stumbling over itself, or the request from Codesys to the device.
Last updated: 2024-10-28
Post by dkugler on Beckhoff EL6652-0010 with Codesys
CODESYS Forge
talk
(Post)
we use successful for many years the KEB MFI terminal for Profinet, EtherCAT, Ethernet/IP,... You'll need a EtherCAT Coupler as "head" from KEB, Kendrion or Berghof. It's all the same board inside: https://www.kebamerica.com/products/ethercat-bus-coupler/ Or the coupler with 16Di/Do integrated: https://www.kebamerica.com/products/ethercat-digital-io-module/ last year I got a EK1100 with EL6731 Profibus treminal runnig. But it was a lot of reverse engineering and thinkering in Codesys and TwinCAT to be done, to get it up, fulfilling my needs. Good luck!
Last updated: 2025-03-25
Post by gseidel on Scara3 kinematic robot error
CODESYS Forge
talk
(Post)
Hi aniket-b, this error has nothing to do with the scara3 kinematics, or robotics, or SoftMotion. It means that the EtherCAT bus is not synchronized. The usual cause is that the realtime of the PLC is not sufficient. See https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_basic_common_errors.html for details and ways to solve the problem. You can also check the PLC log for additional information about the error. Best regards, Georg
Last updated: 2025-12-23
Post by fleaplc on CPU + EtherCAT redundancy
CODESYS Forge
talk
(Post)
Hi all, for a new project I'm looking for a redundant controller with EtherCAT fieldbus I/O. Actually I'm using Beckhoff and it works great! but there's not a solid redundancy yet... Does someone get experience for industrial application (not raspberry) for a redundant Codesys system? If yes please share some info (CPU / OS type, bus, number of managed I/O,... and especially feeling feedback (stability, bugs, performance)... Every suggestion is kindly appreciated!! Fabrizio
Last updated: 2026-01-27
Post by mandeepahujaifm on Ethernet/IP 4.6.0 causing exceptions?
CODESYS Forge
talk
(Post)
I have experienced the same with one of our customers after updating EIP Scanner to 4.6.0.0 and really baffled by it. The core dump simply shows error with ENIPScanner I/O task and on analyzing it says no source code available for 4.6.0.0. Contemplating to go back to 4.5.1 but 4.6.0.0 has some really nice fixes. I guess it don't matter if it crashes anways. Please keep us posted if you find anything.
Last updated: 2024-07-11
Post by totorovic on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
However, if faulty EtherCAT cables were the issue, why wouldn't the error occur during normal operation? Why would bad cables only cause problems during a hard shutdown? I don't have the answer to this question. One last question: When you encountered this behavior, did you see a similar error in your logs? i.e, an "AccessViolation" exception in the EtherCAT Task Yes. It was the exeption you can see in attached file.
Last updated: 2024-10-03
Post by sturmghost on Find visualization elements that require a lot of computing time
CODESYS Forge
talk
(Post)
I found out that the Codesys simulation mode is not good to measure performance. As soon as I upload the code onto the hardware PLC I can see that my visu-task needs around 60 ms to complete. I'm wondering if there is a possibility to find out which visualization/visualization element takes a lot of computing time? Then I would look for ways to decrease the long computing time.
Last updated: 2024-01-22
Post by yofi on Raspberry Pi 4 POU not running
CODESYS Forge
talk
(Post)
I have this error where the pou doesn't run even for simple programs like contact and a coil if i remove the pou from the task and put another one it works for one run then it stops working again in the photo we can see a contact is on but the coil connected to it is still not on and the device is in run mode I had this issue again and again any help
Last updated: 2024-06-02
Post by yofi on Raspberry Pi 4 POU not running
CODESYS Forge
talk
(Post)
I have this error where the pou doesn't run even for simple programs like contact and a coil if i remove the pou from the task and put another one it works for one run then it stops working again in the photo we can see a contact is on but the coil connected to it is still not on and the device is in run mode I had this issue again and again any help
Last updated: 2024-06-02
Post by swe-hob on call of a method of a function block in another program
CODESYS Forge
talk
(Post)
Hi, Let's assume following: PRG_1 fb_1 : fbExample1; fb_1.method_1 do something... PRG_2 fb_2 : fbExample2; fb_2.method_2 if xTest then PRG_1.fb_1.method_1(); end_if; Is there a reason why runtime hangs when I call the method_1 in PRG_1 from a method in PRG_2? Both programs run in the same task. No chance that any other program calls the method. What I practically do there is that in the program PRG_2 I add a structed object into a buffer. In PRG_1 I just process the items in the buffer.
Last updated: 2024-06-03
Post by swe-hob on call of a method of a function block in another program
CODESYS Forge
talk
(Post)
Hi, Let's assume following: PRG_1 fb_1 : fbExample1; fb_1.method_1 do something... PRG_2 fb_2 : fbExample2; fb_2.method_2 if xTest then PRG_1.fb_1.method_1(); end_if; Is there a reason why runtime hangs when I call the method_1 in PRG_1 from a method in PRG_2? Both programs run in the same task. No chance that any other program calls the method. What I practically do there is that in the program PRG_2 I add a structed object into a buffer. In PRG_1 I just process the items in the buffer.
Last updated: 2024-06-03
Post by ben1 on How to stay in a method until something is finished.
CODESYS Forge
talk
(Post)
Why must you use a method? Top of my head can't you just use the button to turn on a bit and use it in a normal task? Just turn a bit on with the button, and run a TON from it in code, and turn it back off with the ton. And then just log the pressure on both the rising & falling edge?
Last updated: 2025-11-03
Post by sheberle on ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks
CODESYS Forge
talk
(Post)
Do you have any additional information about when the error occurs? I am trying to recreate this issue to find a workaround... Maybe you could also make the project available. You could add the following logfilter to the CODESYS configuration file: [CmpLog] Logger.0.Filter=0xFFFFFFFF Logger.0.Enable=1 Logger.0.MaxEntries=10000 Logger.0.MaxFileSize=1000000 SysSem.Filter=0xFFFFFFFF SysTask.Filter=0xFFFFFFFF I hope that the log filter will show us which task is responsible for this, so we can narrow it down a bit more.
Last updated: 2026-03-31
Post by jegerjon on Testing of Codesys program
CODESYS Forge
talk
(Post)
I have a simulation function that toggle xSimActive. I map all IO variables to "IO GVLs" when xSimActive=0. I map IO corresponding SimIO GVL to "IO GVLs" when xSimActive=1. Then I write code for the simulation program that runs when xSimActive=1. Typically increase flow corresponding to pump speed, simulate tankfilling corresponding to flow and so on. I made a FC that require a correct code to activate simulation to avoid unintended activation by service dept. When comissioned remove any possibility to activate simulation. Super when officetesting and supporting service dept. + cheap as it requires no additional equipment, and it is easier to support customer later on in the life cycle as you can test proposed changes without setting up a testlab.
Last updated: 2023-12-07
Post by jegerjon on Testing of Codesys program
CODESYS Forge
talk
(Post)
I have a simulation function that toggle xSimActive. I map all IO variables to "IO GVLs" when xSimActive=0. I map IO corresponding SimIO GVL to "IO GVLs" when xSimActive=1. Then I write code for the simulation program that runs when xSimActive=1. Typically increase flow corresponding to pump speed, simulate tankfilling corresponding to flow and so on. I made a FC that require a correct code to activate simulation to avoid unintended activation by service dept. When comissioned remove any possibility to activate simulation. Super when officetesting and supporting service dept. + cheap as it requires no additional equipment, and it is easier to support customer later on in the life cycle as you can test proposed changes without setting up a testlab.
Last updated: 2023-12-07
Post by mikek10 on HTTP Client TCP Init Error
CODESYS Forge
talk
(Post)
Hi, I tried posting in the discussion for the HTTP Client example but perhaps that is not monitored? I have been using http client successfully for approximately 12 months, however in recent weeks I have begun to get TCP_INIT_ERROR when attempting to communicate. The only resolution seems to be power cycling and then the connection begins to work again for a time. I am not aware of any changes to code or libraries between working ok and now. Cold reset does not resolve, only power cycle. It seems the error from NBS.TCP_Client is 6002 which I think is invalid_addr However the address is the same when working and not working?